GE WavePro circuit breaker problems?

Jul 26, 2004 3 Replies

A client has recently had problem with this breaker; it's 3 pole, 480 volts, 4000A frame, 4000A trip, electrically operated, drawount mounted. The trip unit is a MVT with LSIG trips. The breaker has been in service less than 6 months.



The breaker is installed in an UPS switchgear and opened without any instruction from the UPS system. A long time trip flag was indicated, with a LT setpoint of 5100A. Tripping on LT is dubious because the UPS cannot produce this amount of current for long enough to reach the LT range. The UPS would have to transfer to bypass to provide 5100A, but the UPS history log indicates nothing about such a transfer.



Anybody encountered anything similar?



Regards, Chris Johnston


The older version of that device, RMS-9, with the dials instead of digital programmer, is great for tripping early. Out of an installed base of 70, I have had 4 so bad that they failed with less than 25% load. Although these units are LSI.

The short versi>A client has recently had problem with this breaker; it's 3 pole, 480

make sure that the electricity is not going backwards through the breaker. Happens a lot especially in UPS and paralleling gear. Example top stabs are line in and the bottom ones are line out. If this is not the case then reverse the ct's and all should be better. Which may mean getting someone that built it out so you do not loose warranty.

I assume you HAVE tested the breaker and the settings with secondary injection. I have seen bad trip units out of the box. You have looked at the TIME setting for the LT, right?

Hope this helps

Thanks for responding. CT polarities are correct. Checked breaker with primary injection. Checked time setting for LT as well. Any other thoughts?

Cheers, Chris