GFCI's: Upstream protection Also ?

Hello,

Concerning the normal GFCI protectors/modules:

Obviously they protect "downstream" like they are designed to.

But does this protection also extend "upstream" ? If so, to where ?

Thanks, Bob

Reply to
Bob
Loading thread data ...

No

Reply to
gfretwell

???? 13/8/2017 12:43 ??, ? Bob ??????:

nope, but if you "cascade" many GFCIs, you have to pick up them correctly, so that a downstream trip doesn't trip the upstream one. So, if for instance in a factory in the main panel you put one with a 30 mA trip current, and downstream another with also 30 mA, you have to pick an upstream "specially" rated so the downstream trip won't affect the upstream breaker.