On Wed, 15 Sep 2004 20:58:45 -0700 Joe wrote: | I was replacing a receptacle on what I'll call circuit 1, which is a 20-amp | appliance circuit in the kitchen. The breaker was off, confirmed with outlet | tester. The wire nut came off of the neutral bundle, I went to put it back | on, touched two of the NEUTRAL (white) wires, and got a shock. I got my | multimeter and found 120 volts across two neutral wires. I found this VERY | strange. | | But the plot thickens: my wife then asked when the microwave would be back | on. She was right...the microwave was off, but the microwave is on a | different circuit (also a 20 amp appliance circuit), which I'l call circuit | 2. I tested an outlet on circuit 2, and the outlet tester indicated that hot | & ground were switched. | | So, I turned off circuit two, and the hot neutral in circuit one went away. | Turned both circuits back on, and everything works fine.
Turn circuit 2 back on, but unplug the microwave oven. See if the voltage is still present in the neutrals.
| This seems very strange to me...can anyone shed some light on this?
Sounds more like a case of neutral crossover. Someone could have wired the neutral of circuit 2 into circuit 1.
It is unlikely that ground was switched with hot (things would get really nasty if it were). The indication you are getting is probably because there is voltage between neutral and ground (you'd get this if ground was really hot), and no voltage between hot and neutral (you'd get this if hot was really ground. Hence the reading says hot and ground are switched. But that's not the only thing that can cause this. If hot is hot, and ground is ground, and neutral is hot (same phase as the other hot), you'd get the same reading. You may even get a false reading due to capacitive voltages when there is no load. If you were doing this reading with the neutral bundle all taken apart, I would not be surprised by it.
The big question is where does the wiring for circuit 2 go? If it passes through the box for the receptacle on circuit 1, that could have been why the neutrals were cross connected.
Are circuit 1 and circuit 2 on opposite phases? There would be 240 volts between hots of the 2 circuits, when live, if so. You can tell by checking their position in the breaker box. Phases alternate vertically, but are the same horizontally. If they are on opposite phase, and especially if they go through the same receptacle box, this could be a case of shared neutral. Such a circuit SHOULD be wired via a single 2-pole common trip breaker to avoid the shocking experience you had. But they are very often not wired that way.
So let us know more about the circuits you have.