How many amps is my service?

Hello, all,

I'm getting ready to have an electrician put some 220V circuits in my detached barn workshop. (I only have 110V right now.) I'm hoping I have enough power running from the main panel in the house out to the sub-panel in the barn to do what I want.

When my electrician came out to check and make sure I won't need another/heavier wire between the house and the barn, he opened up the sub-panel in the barn and said it looked like I have 100A service at the subpanel in the barn.

(He said that he wanted to check at the main breaker panel in the house to make sure 100A service was going to the barn, but he forgot to do so.)

I just took a look in the main panel in the house, and it looks like there is a dual pole breaker feeding the barn (I think that's the proper term -- it's like two breakers side-by-side with the switches connected) and each switch of this double-pole breaker is labeled 50A.

It's a Square-D panel, if that helps.

Can anyone tell me from the information I've provided what the amperage going to the barn likely is? (Right now I have only 110V at the barn, I believe, so please express the amperage with that in mind.) I'm hoping I have enough capacity to have a 220V 30A circuit for a compressor and a 220V 20A circuit for a saw (though they would never both be used simultaneously).

Thanks for any replies.

Jones.

Reply to
Jones
Loading thread data ...

That's only 50 amp service, not 100 amps.

Reply to
Esther & Fester Bestertester

The real limiting factor is the wire size going to the barn. If it is

2ga copper. The other issue is the main breaker size. If you have the capacity in the main panel and big enough wire he can swap out the 50a breaker.
Reply to
gfretwell

On Mon, 11 Feb 2008 21:00:09 GMT Esther & Fester Bestertester wrote: |> I just took a look in the main panel in the house, and it looks like |> there is a dual pole breaker feeding the barn (I think that's the |> proper term -- it's like two breakers side-by-side with the switches |> connected) and each switch of this double-pole breaker is labeled 50A. | | That's only 50 amp service, not 100 amps.

However, for 120 volt loads only, it can aggregate as much as 100 amps. Half of them would be on one pole, and half on the other. This assumes the feed to the barn is 3-wire plus ground. It is possibly it is only a 2-wire feed, and only providing one of the poles the breaker can do.

Reply to
phil-news-nospam

OK, thanks for the replies.

I'm assuming (and hoping) that since he seemed to think I already had

100A service to the barn, that the wire from the house to the barn is heavy enough.

Here's hoping he can just swap out the 50A dual-pole breaker for a 100A dual pole (or whatever is needed)...

Reply to
Jones

It looks like you have 50 amperes for the barn at 220 volts. You said nothing about distance to the barn, other loads in the barn, or the wire size. These are factors for determining if the 50 ampere subfeed is adeqaute.

Reply to
Gerald Newton

You will probably be fine with 50a at 240v unless you have several people working at one time. It is hard for one person to use more than

30 amps at a time.
Reply to
gfretwell

Yeah, but at what voltage? As I said in the original post, I'm using

110V as the reference point...
Reply to
Jones

| You will probably be fine with 50a at 240v unless you have several | people working at one time. It is hard for one person to use more than | 30 amps at a time.

Imagine running a 9600 watt heater in the barn. Now imagine running equipment that produces that much heat just from operation.

Sometimes I wonder why we need 200 amp services to a home. Well, maybe we need 100 amps to run air conditioners to remove the heat produced by using 100 amps for other things.

Reply to
phil-news-nospam

The protective device determines the rating. It is a 50A service, regardless of whether it is 240V 3-wire or 120V 2-wire. The difference is the maximum wattage available, not the maximum amps.

Reply to
Ben Miller

Ben, the only reason I believe he really has 240 out there is the 2 pole breaker. He probably just has 120v receptacles at this point.

Reply to
gfretwell

I agree that is probably what he has. Phil seemed to be adding 50+50 to get to 100A, however. I was just making the point that 50A is all he has, assuming the conductors are properly sized of course!

Reply to
Ben Miller

On Tue, 12 Feb 2008 08:59:42 -0600 Ben Miller wrote: | snipped-for-privacy@aol.com wrote: |> On Tue, 12 Feb 2008 00:00:17 -0600, "Ben Miller" |> wrote: |>> The protective device determines the rating. It is a 50A service, |>> regardless of whether it is 240V 3-wire or 120V 2-wire. |>> The difference is the maximum wattage available, not the maximum |>> amps. |>

|> Ben, the only reason I believe he really has 240 out there is the 2 |> pole breaker. He probably just has 120v receptacles at this point. | | I agree that is probably what he has. Phil seemed to be adding 50+50 to get | to 100A, however. I was just making the point that 50A is all he has, | assuming the conductors are properly sized of course!

Right, I was adding 50+50. If his loads are all 120 volt, and can be split loaded well enough, then he has 100 amps worth of 120 volts, assuming he has both poles fed in. Now that he wants 240 volt stuff, he does have to look at it as 50 amps and needs to be sure he has both poles fed.

Reply to
phil-news-nospam

That is a very confusing way to look at it. While what you are saying is true, it bears no relationship to the the rating. Service or feeder sizes reflect the maximum amps that any individual line can carry. Nowhere on that system will you ever measure 100A. The breaker will open when any line exceeds 50A. In the electrical world, that is a 50A service.

120V 2-wire with 50A 1-pole breaker = 50A feeder 240/120V 3-wire with 50A 2-pole breaker= 50A feeder 208/120 three-phase, 4-wire with 50A 3-pole breaker=50A feeder

Of course, the available kVA from those three systems is not the same, which is what you are really talking about, but that is different from the rating of the feeder.

Reply to
Ben Miller

Your 100A subpanel does not mean you have 100A service at the barn unless you have wire sized for 100A and is protected by a 100A breaker at the main panel.

Looks like you have 50A, 120/240V, single phase service to the barn assuming the conductors are correctly sized. You should have 2 hot, a neutral and a ground to the subpanel.

50A, 120/240V service, but your electrician need to verify the conductor size. If your compressor is not interlocked with the table saw, how would you insure it won't run at the same time? Do you turn the compressor off before you run the saw? In any case, for a 50A service, its ok to have it run at the same time since typically neither of those loads are continuous. However, watch out for inrush current as it might trip the breaker when both starts at the same time. (Hard to say if it trips without doing a coordination study.) Presuming your electrician is correct regarding the 100A service at the barn, you could than replace the 50A with a 100A breaker at the main panel. I would just leave it at 50A for now if your not adding addition loads, as it offers better protection than 100A.

Your electrician should be able to tell you if the main panel is able to take the additional load (and some future loads, whatever that may be) without tripping the main panel, bringing down you house as well as your barn. He should also be able to perform a voltage drop calculation from the main to the subpanel to assure you that neither the compressor or table saw motors would burn out. The voltage drop should include future loads just to be on the safe side.

Reply to
Frank

100A is confusing, current not scalar:

50A on line 1 + 50A on line 2 = 0 amps for the subject 120/240V, single phase system

Reply to
Frank

The op simply wanted to know "How many amps is my service?", refering to a sub-feed to a second building. With the existing 50A breaker feeding the building, it is 50A. If the wiring is adequate and he increases the breaker size to 100A, then it will be 100A. It is not "0 amps". That is the neutral current if both lines are carrying equal current at equal pf, but it bears no relationship to the circuit rating.

Reply to
Ben Miller

Frank (any all other repliers),

Thank you very much for all of your thought, debate and replies.

I didn't mean to stir the pot, but I do appreciate all the information!

I'm hoping my electrician will come to install the circuits on Saturday, and if he does, I will try to supply an after-action report to fill you all in on what the final disposition was.

Again, many thanks.

Jones.