Fast and simple: VD = 2 *K*L *I / CMA for single phase Multiply this by .866 for three phase and multiply by .5 for 4 wire, 3 phase.

K = 12.9 for copper and 21.2 for Aluminum (for 75 degrees C. maximum insulation temperature) L = one way circuit length in feet I = amperes CMA = circular mil area from Table 8 in Chapter 9 of the NEC VD = volts for voltage drop

Or just go to

formatting link
and place your mouse over calculators. The voltage drop calculator near the bottom of the menu does it for you. The advanced voltage drop calculator will give even better results for contract work where you really are nit picking to downsize your wire or arguing with the inspector.

Reply to
Mr. Smith

Presidant of the company and you cant calc VD ?

How bizarre.

sQuick..

Reply to
sQuick

He must be the "Son" part...

Reply to
indago

He could have an accouting/finance/business background.

Sincerely,

Donald L. Phillips, Jr., P.E. Worthington Engineering, Inc.

145 Greenglade Avenue Worthington, OH 43085-2264

snipped-for-privacy@worthingtonNSengineering.com (remove NS to use the address)

614.937.0463 voice 208.975.1011 fax

formatting link

Reply to
Don Phillips

What he really needs is a chart that gives the voltage drop for one amp in 1000 feet of the various wire sizes. Then it is a simple process that you can virtually do in your head if you just want a "go/nogo" answer.

Reply to
Greg

I would recommend a copy of Ugly's Reference Book

formatting link
should answer most of your electrical questions....

Reply to
Ross Mac

Same thing I thought when reading this one. I thought all those guys had an NEC handbook and an Ugly's reference at least!

Reply to
Ross Mac

formatting link
It should answer most of your electrical questions....

Not quite. The application of heat transfer to voltage drop allows the calculation of the conductor temperature that gives a more accurate voltage drop. Ugly's does not have a single line about calculating amperes using heat transfer.

Reply to
Mr. Smith

formatting link
> It should answer most of your electrical questions....

I figured if he didn't have a grasp on things, Ugly's would be a good reference....You already left the equation.....

Reply to
Ross Mac

I*R for DC

Reply to
William Wallace

Works equally well for AC, since resistance doesn't discrimate.

Harry C.

Reply to
Harry Conover

True, while 'I' says a lot, the 'R' gets a little more complicated with AC. Indeed, Zee issue can get quite complex.