Pressure Testing HV cables

Could somebody please explain the difference between pressure testing and insulation resistance testing of HV cables.

And how is the pressure testing actually done and what do the results actually mean ?

i.e Leakage in mA

Thank You

Reply to
toby jug
Loading thread data ...

IEEE Std 400-2001, Guide for Field Testing and Evaluation of the Insulation of Shielded Power Cable Systems is avaialalbe in PDFat shop.ieee.org, but not for free.

--s falke

"toby jug" wrote...

Reply to
s falke

You do not say where you are in the world and this sometimes effects the answers to this type of question, but in the UK Pressure Testing implies applying a voltage to a cable for a short time which exceeds working voltage. This is usually done with dc even on ac cables, and the result of the test is either success or failure depending on whether the cable survives or fails. There will usually be a measured leakage current, but it is not regarded as important. It is usually done once only as a test when commissioning a cable.

Insulation Resistance testing usually involves testing an HV cable at a lower voltage, and measures the insulation resistance of the cable at this voltagae. If done regularly and carefully with guard electrodes the readings can give some indication of how a cable is detiorating with age. Personally I would not use it because of the difficulties of ensuring all readings were done under the same conditions, and the data management needed to keep meaningful records, but it some places it may be a legal requirement.

John

Reply to
Eur Ing John Rye