SETUP: 200 AMP Main Panel connected to a 100 AMP sub-panel via metallic ...
D
Don Kelly
------------- What is the code in your location? Follow it.
E
ehsjr
You don't need a separate ground rod. The ground bus in the sub must be bonded to the existing grounding electrode system. This can be done with a short nipple between the panels - but check with the local inspector for the accepted practice in your location.
Ed
D
daestrom
IIRC, it is also important to *separate* the grounding bus from the neutral bus in the sub-panel. That is, you need *four* electrical connections to the main service panel. Two hots, a neutral and a ground. As you said, the ground *can* be via a short nipple between cases, but it must be separate from the neutral.
daestrom
R
Randell Tarin
Local code has the GROUND bonded to the NEUTRAL at the MAIN. This was accomplished with a built-in bonding strap.
Since the the ground in the MAIN box is bonded to the ground, then a nipple wouldn't work because it would bond the sub ground to the neutral as well.
It seems that I would have to isolate the grounding bar in the sub-panel and run a separate grounding wire to the existing grounding bar.
B
Ben Miller
That is correct.
The nipple bonds the sub-panel enclosure to the grounding system, which is necessary for safety and code compliance. However, the only place the neutral should be bonded to the grounding conductor is at the service entrance. Therefore, you need two separate bars in the sub-panel. The neutral bar that all of the grounded conductors (white) connect to must be isolated. This means remove or do not install the bonding screw or strap. On the other hand, the ground bar that all of the equipment grounding conductors (green) connect to should be bonded to the metal enclosure, and not isolated.
Ben Miller
D
daestrom
True.
Not true. You want the enclosure and the *grounding bus* inside the enclosure to be bonded to the main panel frame and grounding bus in the main panel. The fact that the grounding bus and neutral bus are bonded in the main panel is not an issue.
And, you want the neutral bus in the sub-panel to *not* be bonded to the sub-panel frame or the sub-panel grounding bus. The neutral bus and grounding bus must *only* be connected at the main/service-entrance panel.
So, to power the sub-panel requires: 1) firm electrical contact on the panel (such as the pipe-nipple arrangement, or a bare wire between the main-panel grounding bus and the sub-panel grounding bus). 2) An electrical connection from the neutral bus in the main panel and the neutral bus in the sub-panel with an *insulated* wire. 3) The neutral bus in the sub-panel must *not* be bonded to the sub-panel frame or grounding bus (as Ben said, remove/do-not-install the bonding jumper). 4) One or two 'hot' conductors from the main panel to the 'hot' busbar(s) of the sub-panel.
No, isolate the *neutral* bar in the sub-panel. Running a fourth wire between the grounding bus in the main and the grounding bus in the sub-panel
*is* an option. Especially if they are some distance apart.
daestrom
*
**THE-RFI-EMI-GUY**
Is it permissable under NEC to drive another ground rod near the subpanel and bond the ground of the subpanel to it as well as (via 4 conductor) to the Main box? The two panels are on opposite sides of my residence.
Joe
Ben Miller wrote:
R
Randell Tarin
Thanks, I've got it now.
The sub will be right next to the main. I can easily run a fourth wire.
G
gfretwell
B
Ben Miller
You can connect as many grounded objects as you want, such as water lines, structural steel, ground rods, etc. to the equipment grounding system anywhere. In fact, this will happen whenever you mount boxes or conduit to buried steel structure, or connect to any buried conduit. If your sub-panel feeder runs underground in steel conduit, then you already have it connected to a grounding electrode!
Just remember that it all must be bonded ultimately to the grounding electrode at the service entrance. It is not acceptable for the earth to provide the sole return path for fault current from the sub-panel to the main panel. As long as you have the fourth wire or a metal raceway between the panels you are fine.
The neutral is only bonded to a grounded object at the service entrance. It is isolated from the grounding system everywhere else in the facility to prevent a parallel return path for current through conduit and equipment enclosures.
Ben Miller
*
**THE-RFI-EMI-GUY**
Thanks Ben;
Joe
Ben Miller wrote:
E
ehsjr
Make sure you understand *how* to add grounds to your system. Quoting Ben, for emphasis: "It is not acceptable for the earth to provide the sole return path for fault current from the sub-panel to the main panel." Any ground you add must be properly bonded to the grounding electrode system. Ed
B
Ben Miller
Now if we could only get the IT industry and some automation vendors to understand that simple concept, and abandon the idea of "isolated" ground rods!
R
Randell Tarin
You guys are basically answering my original question:
My MAIN is grounded to an 8' copper electrode via a #4 bare wire. My subpanel will be only inches from this installation. I can bond to the electrode OR to the MAIN grounding bar. As long as the NEUTRAL is isolated in the sub-panel, is there any difference?
D
DaveC
Thus spake Ben Miller:
Thanks, Ben, for an explanation of the technical reason for ground/neutral isolation in subpanels.
What are the dangers and symptoms of having parallel return paths between the the SE panel and a subpanel?
Thanks,
B
Ben Miller
The danger is the possibility of raising the touch potential on the exposed metal to levels that could be fatal. It might only be a few volts normally, but deterioration of the grounding conductor (which might be accelerated if it carries current continuously) or abnormally high current could raise it. By code, equipment grounding conductors should not carry any current under normal operating conditions.
BEn Miller
*
**THE-RFI-EMI-GUY**
E
ehsjr
Your sub and main are side by side, connected by a nipple. (Don't forget the 4 locknuts) This is what you want your installation to look like:
Installing a subpanel does not automatically mean you must add a supplementary grounding electrode. In your case, since the sub will be nippled off the main, and want to add a second ground rod, you want it to look like the diagram.
The physical connection of the "grounding electrode conductor" which is the single, continuous unspliced wire from rod 1 to rod 2 to the main panel is important, and must be up to code.
Right or wrong, there are inspectors who will reject your installation if it is physically arranged like this:
Ground Ground Rod 1 --------- --------- Rod 2 ||==============|MainPanel|=|Sub Panel|====|| || --------- --------- || || || || || || ||
Check with the local inspector & do it the way he/she recommends. There's a bunch of rules in the code concerning the grounding electrode system, and they must be followed.
Ed
B
Bud--
Also bushings
bud--
*
**THE-RFI-EMI-GUY**
Join the Discussion
Have something to add? Share your thoughts — no account required.
Didn't find your answer?
Ask the community — no account required
Report Content
You are reporting this content to the moderators. They will look at it
ASAP.