What does Class 1, 2, 3 mean??

I've been reading through the NEC for a test and want to make sure that I understand.

Class 1 = 30 v & 1000 VA ?? powered circuits Class 2 Class 3

and then there is a completely different set of classes I, II, III for hazardous stuff??

NEC has too much info

Reply to
fre
Loading thread data ...

You are right. Hazardous locations have "classes" too but you are referring to article 725 here. It is generally called "low voltage" but that is not really true. Class 1 can be line voltage, class 2 is low voltage and class 3 is just a bigger class 2.

This is the commentary from the handbook.

GENERAL DISCUSSION OF REMOTE-CONTROL, SIGNALING, AND POWER-LIMITED CIRCUITS The wiring methods required by Chapters 1 through 4 of the Code apply to remote-control, signaling, and power-limited circuits, except as amended by Article 725 for specified conditions. A remote-control, signaling, or power-limited circuit is the portion of the wiring system between the load side of the overcurrent device or the power-limited supply and all connected equipment. The circuit is categorized as Class 1, Class 2, or Class 3. Class 1 circuits are not permitted to exceed 600 volts. In many cases, Class 1 circuits are extensions of power systems and are subject to the requirements of the power systems, except under the following conditions: (1) Conductors sized 16 AWG and 18 AWG may be used if properly protected against overcurrent (see 725.23). (2) Where damage to the circuit would introduce a hazard, the circuit must be mechanically protected by a suitable means [see 725.8(B)]. (3) The adjustment factors of 310.15(B)(2) apply only if such conductors carry a continuous load (see 725.28 for the exact requirements for adjustment factors affecting ampacity). Class 1 remote-control circuits are commonly used to operate motor controllers in conjunction with moving equipment or mechanical processes, elevators, conveyors, and other such equipment. Class 1 remote-control circuits may also be used as shunt trip circuits for circuit breakers. Class 1 signaling circuits often operate at 120 volts but are not limited to this value. Conductors and equipment on the supply side of overcurrent protection, transformers, or current-limiting devices of Class 2 and Class 3 circuits must be installed according to the applicable requirements of Chapter 3. Load-side conductors and equipment must comply with Article 725. Class 2 and Class 3 conductors are required to be separated from, and not occupy, the same raceways, cable trays, cables, or enclosures as electric light, power, and Class 1 conductors. Exceptions are noted in 725.55. Dry-cell batteries are considered Class 2 power supplies, provided the voltage is 30 volts or less and the capacity is equal to or less than that available from series-connected No. 6 carbon-zinc cells. (A No. 6 dry-cell battery is cylindrically shaped with nominal dimensions of 2.5 in. in diameter by 6 in. tall and weighing just over 2 lb. A No. 6 dry-cell battery is about 10 times the volume of the standard D-cell battery commonly used in flashlights.) Circuits originating from thermocouples are classified Class 2 circuits also. Neither dry-cell batteries nor thermocouples are required to be listed.

Reply to
Greg

If you are talking about Class 1, 2 and 3 Circuits as covered in Article 725 in the NEC I have an online course on this at:

formatting link
There is some background on the man who found most of the data for the Tables for Class 2 and 3 circuits at:
formatting link
If you are talking about Class 1, Class 2, and Class 3 Hazardous Locations see Articles 500, 501, 502, and 503 in the National Electrical Code