Hi All i need to calculate the wire gauge for 3 phase system ( 3 x 220 power,

1 neutral and 1 ground) and 150 Amp balanced load ( 50 Amp on each phase). what should be wire guage for 3 phase wire and specially for neutral and ground. can any body tell me about calculations. looking forward towards positive response Regards Rooh
Reply to
Rooh
Loading thread data ...

The short answer to your question is 6 ga copper (50a per phase) but I am not sure the question is right.

Reply to
gfretwell

Reply to
Rooh

Reply to
Rooh

Hello i need to calculate the wire gauge for 3 phase 4 wire system ( 3 phase

  • 1 neutral). total load is 150 Amp and load is not balanced .Different devices are connected in single phase confgiuration ( phase to neutral using each phase wires), no device is connected in phase to phase configuration. what wire gauge will be used for power lines for a balanced power system. also what wire gauge will used for neutral wire. will it carry total 150 Amp current or only 50 Amp current. waiting for postive response.
Reply to
Imran

If this is still max 50A per phase the phase wires are still 6 ga.

3 phase simple loads the phase currents cancel each other on the neutral. With equal loads on all 3 phases the neutral current will be zero. With 50 A on one phase or 50 A on 2 phases the neutral will be 50 A.

With high harmonic current on the neuutral, some of the harmonic currents add. That could result in more than 50 A on the neutral. Harmonics are produced by rectification to DC as in computer power supplies and variable frequency drives.

bud--

Reply to
Bud--

If it is only 50amp per phase, that would be a 50amp 3 phase circuit. If you are using a 60 amp breaker the wire would be: Feeders - 6 gauge Neutal - 6 gauge Ground - 8 gauge

However thare are exceptions depending on what this circuit is for. Is it feeding a motor, a dist. panel, or what? The above is feeding a dist panel. If a motor why a neutal? We just need more info here.

The Voltmaster

Reply to
Voltmaster

The correct answer is "Hire a good electrician or maybe an electrical engineer " - the nature of this question gives me great doubt that an answer gotten off a newsgroup will provide a safe solution.

Bill

Reply to
Bill Shymanski

And doesn't this apply to so many questions in this NG For example-- How do I parallel 2 1000kva alternators? The real answer is much like the answer to -- How do hedgehogs make love? Answer.. Very carefully.

But the devious ill-informed and irrelevant rubbish sometimes supplied to this type of question leave a lot to be desired.

Reply to
John G

When the load is perfectly balanced on the three phases there will be no current flowingf on the neutral wire. When the load is not balanced, there will be current floating on the neutral. With pure linear loads the neutral current can be up to the current of one phase (the current of phase carryign the highest current, think situation where power is taken only fron one phase). If the load is non-linear then the the neutral current can in extreme case be the sum of all phase currents (all load third harmonic). Dimmers and switch mode power supplies without power factor correction do generate a large number of odd-order harmonics (worst is third). For example with large dimmer loads the usual practice is to specify the neutral conductors at 130% of phase conductors (rated for 130% of nominal phase current).

Reply to
Tomi Holger Engdahl

Then if you are running the cable for more than fifty feet or so, you need to consider voltage drop, and might have to increase your conductor size.

--Dale

Reply to
Dale Farmer