Power mains question: wire gauge

Air compressor 1/2 hp motor rated 220v (2-wire, not 3-phase) @ 15A. Distance from load panel ~100 ft (as the conduit runs).

15A can be handled by 14 gauge, but I'd normally go with 12 gauge due to start current.

With such a distance, is it recommend to up-scale the wire to 10 ga?

Thanks.

Reply to
DaveC
Loading thread data ...

I would, since the starting current is much higher.

Reply to
Michael A. Terrell

"DaveC"

** Giant HUH ??

Such a motor normally draws around 3 amps.

... Phil

Reply to
Phil Allison

#12 is 1.6 mohms/foot. That's 0.32 ohms total. The short-circuit current from 220 volts is almost 700 amps. A half horse is only around

400 watts, about 2 amps. I'd use #14.
Reply to
John Larkin

Up to 4.9 Amps, according to the 2011 NEC (Table 430.248). And that's all you have to provide in terms of feeder/branch circuit ampacity.

Reply to
Paul Hovnanian P.E.

Hmmmm, did the OP leave off a 1 or has he a very inefficient 1/2 hp motor ??

Rheilly P

Reply to
Rheilly Phoull

As another poster stated, 220V @ 15A is like 4.5 HP (Or VERY lossy)

Something is amiss somewhere.

Reply to
SoothSayer

Hmm, now that you mention it...

Lemme check my notes.

[OP]
Reply to
DaveC

Maybe OP dropped a leading '1'. A 1.5 HP 230V 1ph motor still only draws up to 10 Amps per the NEC.

Reply to
Paul Hovnanian P.E.

There is s thing called "voltage drop". Voltage will drop in a wire running a long distance, sometimes so much, the device at the end will not operate!

The amount of voltage drop depends on the voltage, the type of metal used for the wire (copper / aluminum), the wire size, and the load in amperage at the end of that wire.

The internet has made this easy for you. Just search google.com for the words...

Voltage Drop Calculator

Reply to
Bill

200' of 14AWG solid copper wire has a resistance of about 0.5 ohms, so if your locked rotor current is 15A, then the drop across the cable will be 7.5V when the motor first starts up, leaving 212.5V for the motor. No problem.

If your motor is about 80% efficient, then at full load it'll be taking about 466 watts from the mains, which is about 2.1A.

2.1A through 200' of 14AWG ohm will drop about 1.1V across the run, leaving about 219 for the motor. Absolutely no problem with 14AWG, so don't waste your money on what you don't need.
Reply to
John Fields

3.1 horsepower.

Thanks.

Reply to
DaveC

The rating plate on the compressor says 3.1 hp, 15A, 230V.

Yet I see that 3 hp @ 230v is 18A:

Won't the 14 ga. wire and 15A breaker be taxed?

Should I reconsider the 14 ga (upscale it to at least 12?) wire for this compressor?

Thanks.

Reply to
DaveC

Until the motor or compressor is replaced with a larger unit. Then all bets are off. It's cheaper to do it right the first time. You could even put a small breaker box by the compressor & run AWG 6 to it, to power other tools, as needed without starting from scratch.

Reply to
Michael A. Terrell

That's a good idea. I'll talk it over with the owner.

But for now I want to settle on what size conductor to use if it's just to supply this one compressor.

Thanks.

Reply to
DaveC

If it's 1/2HP, now, it's unlikely to grow to >5HP.

Run several #12s, instead, when needed. It's cheaper.

Reply to
krw

Pull additional #12s in the future? I've had bad experience pulling additional conductors in a conduit with existing conductors.

If I misunderstand your statement, please try again. ;-)

Thanks.

Reply to
notme

Yet your original post said 1/2HP. Make up your mind.

That's high. 3HP is about 2.2kW, or 7A at 240V. Double it (motors aren't 100% efficient) and it's in the 15A area.

Yes. Use a 20A breaker and 12GA.

Go figure that you'd expect a different answer with a different question.

Reply to
krw

No. A bundle of a few 12s will make a nice oversized #10. The finished 'wire' will be stronger and more flexible too.

Of course, the return has to match. So you pull all 7 at once.

Two sets of 3 #12s and one #12 fault return. Seven wires.

Reply to
MrTallyman

Conduit?

Reply to
krw