Not an expert in 3-phase stuff, but familiar with motor starters and contactors. Have a need to work on a Dough Mixer, which is 3-phase but the motor is two speed. One motor for the rotating bowl, and a larger motor for the dough hook. The dough hook motor is two speed. This is an older Italian machine (no info on it), but after cleaning the contact tips on the main contactor, got the motor so it will run on low speed and shut off when it is supposed to. However, this machine is designed to run for a preset time (owner selected) on low speed, then kick into high speed for another preselected time. Problem: Runs on low speed but when it kicks into high speed, starts to single phase, and trips out. I'm not sure how the motor is made, and how the wiring through the contactors would be done to accomplish this. Any links to show a crude schematic? I've been looking without much luck. Any help appreciated. Thanks. Ken.
3-phase 2-speed question
Apr 09, 2008
6 Replies
Ken,
I can't help with a diagram but my advice is to check the motor thoroughly when disocnnected from the control box. When you are sure the motor is good on both speeds, then trouble shoot the control box.
Bob Swinney
Check Wiki-answers:
formatting link
I didn't study it, this may be how your motor is wired.
Paul
Another possibility - there's a wire swapped, or most likely the shorting contacts aren't shorting.
formatting link
give clues on wiring - you have to swap the feed point to U2-V2-W2 AND short U1-V1-W1 together to shift into high speed. If the shunt contacts leave one lead open, that will cause problems.
Tear down all the contactors (again) and inspect the contact points first. That's often where the trouble lies, one of the contacts has burned to the point it is going open. And unless it's one of the European DIN-rail miniature units that you just toss and replace, almost all motor starters and power contactors have field replaceable contact kits.
Sometimes you can repair a bad contactor TEMPORARILY by filing off the contacts flat and smooth, then swapping one half of the contacts during reassembly - the filed-off bad base contacts now mate with a good moving shoe, and a bad moving shoe with good base contacts.
The contact swap will only buy you a few days before the trouble reappears, but it proves where the fault is and gets the gear running. And that's usually enough time to find and ship the needed parts.
And always check your phasing carefully when you are done, jog it in each speed before allowing automatic operation - if there's a wire swapped and the motor tries reversing as it shifts from Low to High while it is running, this is not good at ALL.
-->--
Thanks for the reply Bruce. I tore down the contactor which was preventing any operation at all.... it was pretty bad inside (the machine uses Siemens Minicont contactors) not necessarily fun to get apart, but do-able. Pretty poor shape inside, but I got it dressed up and back together good enough to get the machine to fire up. I have ordered a replacement contactor to get that particular one out of the pile that's in there, and the machine will run on low without problems. When the new contactor comes in, I will swap it into the stack and then try to figure out which one(s) are causing the high-speed problem. The problem with the Siemens contactors that were use in this machine is that the only way you can see if they are pulled in is by looking at a little tiny red tip inside the contactor face to see if it moves. I'm thinking I may rig up several 120v small bulbs on leads to connect across the coil terminals to see which contactors are energized when switching into high gear. There are probably 7 or 8 contactors in this mess, and no paperwork to help. Thanks again for the link - I'll check it out, but I'm unfamiliar with the terminology of U,V,W (1 & 2) as I'm used to working with T1,2,3. Ken.
This is a European convention that's become common in the US. U,V,W denote the conductors or conections supplying a load; R,S,T are supply conductors. The connection thru a 3-phase contactor would look like this:
Line Load R--||--U
S--||--V
T--||--W
Thanks, all, for the great information. I'm learning...... One of the main problems with working on this unit is that there is VERY LITTLE room in the control cabinet - it's nice and neat, but very tight and hard to see where everything goes. When the new contactor comes in, I'll just have to take a little time to "figger it out". Worse to worse - it'll still run on low speed..... which is way better than mixing a bunch of pizza dough by hand . (At least according to the boys in the shop that have been building up their muscles lately) Thanks again to all..... Ken.