Circuit amperage question

I'd argue that you are making a LOT of mistaken assumptions!

Wire size: pry open an old ceiling fixture with fuzzy cloth covered rubber wire and nothing left of the wire color in poor light and it's very easy to misjudge the wire size. And the 'finger bend test' doesn't always work if the wire was work hardened.

Breakers are there to protect the building wiring, NOT people, NOT equipment. If you want to protect people use a GFI, ground circuits, etc. If you want to protect equipment use equipment specific fuses, surge protectors, etc.

11 amp continuous draw on a 15 amp circuit is a 73% continuous load. NEC wants to see no more than 80% anything more than a 100 watt bulb on the 15 amp circuit puts you over the limit. Net: 15 amp circuit is fine, but NOTHING else.

Assuming a Navy electrician would do it right is not an assumption I would make. Someone trained for a different environment with a different set of rules may not translate well. Worse than that, they may think "they know how" and do it non code.

The OP has a 50 year old house, who knows who and what has been done to the wiring since it was installed? From her other posts, I suspect the OP lives well out in the country, many of those houses had either no inspection or very loose inspection. Wiring done with salvage materials can be scary.

And the fact that someone has a journeyman or master electrician license does not necessarily mean competance. I got a call from a friend after her electrican with a master license pulled a 4 device entry way switch box completely apart, could not get it back together again, and walked off the jobsite. Left all the wires hanging out of the box. It took hours to trace every wire down, reengineer the various circuits (including a Carter circuit!! ACK!!!!), and reassemble.

My first run in's with the NEC made me feel like they were being anal jerks about some of the rules. After a few run in's with old houses, then rereading relevant sections of the NEC, I now have a lot of respect for the fine points in the code.

GatherNoMoss wrote:

Reply to
RoyJ
Loading thread data ...

If Jenny opens a ceiling box and finds ANY Rubber wire, it's time to check a lot closer. That rubber insulation is long-lasting but it was never meant to go forever, you need an honest assessment of the condition in all the junction boxes.

It may be in good condition in the conduits, but if it's been cooked brittle in the light boxes and crackles when you bend it, that's the time to schedule a rewire BEFORE you have a fire or a failure. If it checks good now, check it again every 10 years or so.

And if it's a 20A circuit there's enough excess capacity you can safely put a few table lamps or other small fixtures on that line with the window air conditioner - but not the coffeepot or toaster. This is the time to get a P-Touch or Dymo Labeler and identify all the circuit numbers on the wall plates, and add up the fixed loads.

And definitely not two space heaters, like I found at a rental house one time. (Worked when they were both set to Low, but kick one heater to High and *trip*.) One 18A continuous load to a circuit, not two.

In any house with Rubber or TW Vinyl (first generation 1950's-60's) a Green wire is probably NOT a ground, but a hot. I get the occasional call of "I added/extended a circuit and turned the power back on, and now there's a hard short" - they grounded the Green wire like they thought they should...

And if the house is still Knob & Tube wiring it's Way Overdue for a rewire. That's a fire waiting to happen, especially considering that the insulation has probably fallen off all the wire. You don't even go up in the attic without turning off the power to the house.

-->--

Reply to
Bruce L. Bergman

I take these comments as solid arguments, based on facts, Roy.

For those of us that have seen what's done when someone is too cheap, a bad worker, in over their head, in a hurry, thinks they are smarter than the NFPA/NEC, or otherwise unqualified, even the smallest assumptions will result in potentially hazardous conditions.

The obvious solution to the original question would be to run a new circuit with only one receptacle on it, period. I'd go with 12ga and a 15A breaker, and a 20A rated receptacle (for durability/reliability). This would probably be about a $35 DIY-done-right project (DIY-DR), not for everyone, though. Doing it properly is the only way to know absolutely. The results are a safe place to sleep.

Old receptacles are generally crap.. made well, but worn out (the friction that's felt when plugging/unplugging a 3-wire plug is usually the ground pin, not the other two). New generic receptacles are crap, so buy the better grade, always (without exception for motor and other significant loads).

If the manufacturer recommends a 15A circuit, I don't see where a 20A circuit is good enough (this is merely the "it'll get it to run" philosophy). My last window unit (about 12k BTU) stated a separate 15A circuit. Subjecting the compressor motor to momentary delayed overcurrent conditions is going to be hard on that motor, maybe even lead to failure. One example would be a brief power failure while the compressor is running/cooling cycle, and when the power returns, there is an overload condition for the compressor motor. Most consumer units won't have any overload protection devices, as they would raise the cost of manufacturing the units. If a 20A breaker "waits" briefly, for a 20A overload, bad juju.

The Navy electrician story may be factual, or just an anecdotal seller's comment. Was he honorably discharged, or bad attitude, BCD/DD for negligence resulting in a major loss? Just because he may have gotten the tattoos doesn't mean squat. Nothin' wrong with squids though, in general.

WB ......... metalworking projects

formatting link

Reply to
Wild_Bill

That violates the NEC. A 15A circuit requires 15A receps. A 20A circuit may feed 15A or 20A receptacles.

Reply to
Ned Simmons

I trust that you're correct, Ned, and it sounds reasonable. I should've recommended quality heavy duty receptacles. I'd be very concerned (alarmed) if it were a 20A receptacle on a 14ga circuit.

Marking the receptacle coverplate as 15A maximum would me my SOP.

BTW, aside from the suggested separate circuit issue, many receptacles aren't rated for the same feedthrough capacity that they can pass individually (as in a separate circuit). The pass-thru capacity may be lower, and marked on receptacles' strap (in small print).

WB ......... metalworking projects

formatting link

Reply to
Wild_Bill

aaah guys - the receptacle is irrelevant - the circuit is protected by the breaker - you can put a 100 amp receptacle on a 14 gauge circuit and use a

15 amp breaker - it will be safe - it won't power a 100 amp device, but it will safely deliver the 15 amps via the 100 amp receptacle (now, why you want to do that might be a different question)

The code is designed to protect the plant, not the equipment

Reply to
William Noble

No violation - you can under-breaker a circuit if you want, if the wires and receptacle can handle 20A you can use a 15A breaker as equipment protection. It's silly on a short run, but legal - consider that people use a larger wire gauge than the breaker (sometimes several sizes larger) all the time for voltage drop on long wire runs.

But you can't put a 20A breaker on that circuit and over-protect it if the entire circuit can't safely carry that much current. I.E. there's a wire gauge change to 14-gauge in mid-run.

-->--

Reply to
Bruce L. Bergman

Larger wire is obviously OK, but *not* a 20A receptacle on a 15A circuit. I don't have the latest version of the NEC, but it's in table

210-24 in the 2002 edition.

20A receptacle means one with contacts like this ( | |- ) that'll accept a 20A plug with blades like this ( - | ).

Reply to
Ned Simmons

Yup, the $.59 receptacles are pretty sketchy. You only have to spend $2-$3 to get something pretty good. I have a stash of new hospital grade receps that I found cheap at a salvage place for use in places where they get especially heavy use.

Reply to
Ned Simmons

Not if you care to conform to the NEC. See my reply to Bruce and

formatting link
which says, in part:

************************************************** Q: Can a 15A receptacle be installed on a 20A branch circuit? A: Yes, per the 2005 NEC Article 210.21, a 15A receptacle can be installed on a 20A branch circuit so long as it is not the only receptacle on that circuit. A single receptacle on a 20A branch circuit must be 20A rated. Q: Can a 20A receptacle be installed on a 15A branch circuit? A: No. According to the 2005 NEC Article 210.23 "in no case shall the load exceed the branch-circuit ampere rating." **************************************************
Reply to
Ned Simmons

That is incorrect.

It is permissible to put a 15A breaker on a circuit that is wired with 12AWG copper conductors.

It is *not* permissible to put a 20A-rated receptacle on that circuit. The 15A breaker makes it a 15A circuit, for which the permissible receptacle rating is "not over 15". [2005 NEC, Table 210.21(B)(3)]

Reply to
Doug Miller

That IS the code - stupid as it is. It would make sense not to allow a

20 amp receptacle on a circuit WIRED as a 15 amp circuit, perhaps, but if a 20 amp circuit(wire and receptacle) is protected at 15 amps, what harm can be caused? No more than having multiple 15 amp receptacles on a 15 amp circuit, for sure.
Reply to
clare at snyder.on.ca

aaah, ned, the second quote does NOT say you cannot put a 20 or 100 amp plug on a circuit fused for 15 amps (or one amp for that matter), it says the "load" cannot exceed the rating. Not having the NEC handy, I can't look up the definition of load, but in normal usage, one would differentiate between the rating of a receptacle and that of the load.

think about it this way - I plug my cell phone charger into a 15 amp receptacle, but the load is only .01 watt - clearly that's permitted.

formatting link

Reply to
William Noble

Yep, that's great stuff, the hospital/institutional/medical grade hardware. I try to find and buy any of the better grade gear any time that I encounter it. Electrical, utility carts, door hardware, cabinetry and lighting, plumbing fixtures.

I'll generally buy Hubbell and better grade stuff for most anything, but the cost of those better grades are in the range of "more than one would normally want to pay for", not even being a particularly cheap buyer.

WB ......... metalworking projects

formatting link

Reply to
Wild_Bill

That's true -- but Article 210.21(B)(3) **does** say that. The page Ned cited gives the right answer, but for the wrong reason.

Article 210.21(B)(3) says "receptacle ratings shall conform to the values listed in Table 210.21(B)(3)" -- which says that the permissible receptacle rating for a 15A circuit is "not over 15".

Yes, but you're plugging that into a 15A receptacle, too. The point is that a

20A receptacle on a 15A circuit allows plugging in a single load that exceeds the capacity of the circuit and is therefore prohibited.
Reply to
Doug Miller

Sure it does, it says, "Can a 20A receptacle be installed on a 15A branch circuit?" And answers that qusetion, "No."

I agree the explanation is lacking, but it is just an FAQ, and the answer is correct. If you had the NEC handy you could read the applicable section.

This page paraphrases the NEC in more detail.

formatting link
***************************************************If a branch circuit supplies two or more receptacles:

The total cord-and-plug connected load must not exceed 80 percent of the receptacle rating [210.21(B)(2)].

Receptacles must have an ampere rating that complies with the values listed in Table 210.21(B)(3) (Figure210?44).

***************************************************

And here's the table:

************************************************** Table 210.21(B)(3) Receptacle Ratings Circuit Rating Receptacle Rating 15A 15A 20A 15 or 20A 30A 30A 40A 40 or 50A 50A 50A **************************************************
Reply to
Ned Simmons

Meanwhile the customer, Jenny3k, is long gone.

Why was knob and tubing brought up when she clearly said that the Navy guy used conduit ?

It's because people like to discuss...show off.

Hey, it's a chat room I know....but still humorous.