Looking for 15hp 3ph motor

Hi all, it's been a long time since I visited but I see a few familiar names.

I'm looking to build a phase converter and need a 15 hp 3 phase 230v

1750 rpm motor. I'm in the Albany NY area. Get back to me here or the email listed will work with the obvious edit.

Thanks

Reply to
Andrew
Loading thread data ...

Sure you electric service can handle this? The line current will be in the neighborhood of 75 A idling, and way higher when it starts. Some power factor caps will help some with the running current.

Jon

Reply to
Jon Elson

I have a 25 total hp. phase converter. its on a 100 amp circuit breaker. A 10 hp starts and then several seconds later a 15 hp comes in. The first motor start dims the lights on the whole place. Second one doesn't do much. Now, when i start the Mazak M4 with the 20 hp. spindle you really see the lights dim.

Karl

Reply to
Karl Townsend

I have a 50 and a 30, similar setup except I manually start the smaller = unit on an as-needed basis...

I'm only using the 50 today but a quick check with a clamp-on shows = about 55 amps ( apparent power )--this is with a couple of machines on = line but not actually cutting.

Startup is a different issue though--yes my lights dim a bit even with a =

75kva single phase transformer and 13,500 volt primary.
Reply to
PrecisionmachinisT

He will likely see 180 starting amps.

i
Reply to
Ignoramus16222

on an as-needed basis...

Nothing dims for me, I have 800 amps of clean 3 phase supply

Reply to
Ignoramus16222

On 4/30/2012 5:34 PM, Ignoramus16222 wrote: ...

There ya' go. Just run a long cord to your float; no genset needed... :)

Reply to
dpb

smaller unit on an as-needed basis...

Sounds nice but since I also have tons of wildlife, a private firing = range and a total of about 3 neighbors living closer than a mile away, = I think I'm just going stay where I'm at for the time being.

Reply to
PrecisionmachinisT

I have an indoor firing range too. Just used it extensively last weekend.

i
Reply to
Ignoramus16222

What no one is mentioning here is that you don't need one 15 hp motor.... you can kluge any number of smaller hp motors together, which, I suspect, will wind up giving better regulation. I have 2's, 5's, 10's in a switchable bank, and rarely get past the 5's.

But no matter.... just separate your starting caps from your running caps (altho you can leave in partial start caps for the run mode, whatever brings the 3rd leg to a reasonable value), and try to base your running cap values on anticipated load, if using electronics. Or separate out the electronics so they don't rely on the generated leg.

You only need start caps for the first idler started, and then just sequentially bring in the other idlers as needed, and finalize with suitable run caps. I have a bunch of switchable caps so's I can fiddle with the 3rd leg voltage depending on load and idlers. Don't switch caps in/out while electronic loads are connected, tho.