I recently lost the neutral between the pole pig and my meter. I had 67VAC on one side and over 160VAC on the other. I heard loud frying sounds as multiple surge supressors died, along with circuit breakers tripping. The break has. Been repaired, but I only have a couple working circuits. I lost my A/C and I only have a few working lights. I need to replace the service. I plan to move it underground. No Internet, phone or TV for almost a month now. The open neutral damage the CATV line when the neutral current was shunted through it. I have very poor cell service here. I hope that this gets posted. It was 98 degrees in my bedroom the other night. No sleeping in that. I had to take a nap in my truck with the engine running so that I could use its A/C.
=========================
You have my sympathy. That's both damaging and difficult to recognize in time.
In my case the resistance to the meter grounding stake and buried water pipe was low enough to keep the 'phases' balanced most of the time. I first noticed a fluorescent light buzzing when the refrigerator started. Voltage measurements showed a solid 240V across the phases and only small fluctuations in the 120V.
I don't have two outlets on opposite phases close enough together to compare their voltages with multimeters so I built a box with two analog AC voltmeters (from Variacs) and power cords long enough to reach between rooms whose outlets were on opposite phases (which I had mapped). It plainly showed the simultaneous dip in one phase and rise in the other, to as much as 180V momentarily when the fridge compressor drew starting current from the other phase. Digital voltmeters may not respond fast enough to catch starting surges.
formatting link
The evidence that convinced the power company to replace the outside drop and meter box was a clamp-on ammeter reading of 30A flowing through a water pipe. They cleaned the neutral lug coming into the meter box, and when that didn't cure it they replaced the weatherhead and meter box.
My long term monitoring solution is this meter that I boxed and wired to a GFI-equipped outlet strip to display the load on my solar system inverter. When not on solar power it shows the voltage and current of the appliances I operate on the stove, like the coffee pot or slow cooker. It can check for degraded wiring connections by plugging it into one side of a duplex outlet and the 1000 Watt coffee pot into the other.
formatting link
jsw