'Yes 5000 watts MAX... the closer you get to the 5k the sooner the generator will crap. A generator has a finate amount of power. Not infinate like the power company. Simple example. Let the wife turn on the washer and have it go into spin cycle. You just hit 18 amps. =A0 18X
6 X 120 =3D 12960 watts on one leg. The 6x is the short starting current motors require. In a washer loaded with clothes it will last several seconds until the load is going. The watts will drop as the load starts spining. Your 5k is only a 20 amp 240v generator. It will be maxed out with general lighting and a refergerator.
14 is way to small. You really need to check the local regs. Back feeding is against the law and dangerous to line men. Your performance will vary.'
ME: I called Coleman and the Tech dept. told me that there are two feeds off of the Generators Motor : one for the two 120 v receptacles and one for the one 240 v receptacle. They said the same as you did..that, the 240 v. is good for 20 amps. Arent i correct in assuming , that, if i tied the two feeds off the motor together, that i would end up with 40 amps capability ??? If so, thats what i want...and ill fuse it at 40 amps also. Ill be careful not to push the Generator to its limit.
Im fully aware of the dangers to backfeeding and will prevent that from ever occuring .
Thanks, dave