OT - Start capacitors

Our small concrete mixer blew the start cap so we have to spin it by hand to get it going. It is a 110 volt motor, probably 1/3 hp. It uses a 40 mfd, 400 volt cap. The closest Grainger has that I can find is a 43-50 mfd, 250 volt. Would that work, or do we need to get a 40 mfd? What about the voltage rating, is 250 ok since this is a 110 volt motor, or do I need to stick to a 400 volt rating?

-- Dennis

Reply to
DT
Loading thread data ...

The tolerances for start caps is uneven. Something like - 20 % plus

100%. I don't think you will have any problem with using the 43-50 mfd 250 volt. If you rewired the motor for 240 volt operation, it should still be okay. Typically the start winding is always used on 120 volts.

Dan

Reply to
dcaster

Thanks. I went down to Surplus Electronics near me and found a 40 mfd 250 v cap for. I also discovered the switch on the mixer had gone bad so I picked up a weatherproof 20 amp switch. Everything works fine again, only ten bucks spent.

-- Dennis

Reply to
DT

According to DT :

Make sure that it is *marked* as a start capacitor. 40 uf 250V sounds like a common DC rating, and a surplus electronics place is more likely to have DC caps than the AC rated ones needed for motor starting duty.

If it is DC rated -- you'll be lucky if it lasts a single start.

O.K. So you *did* get a motor starting cap, not a DC one. Good.

BTW I find it good practice to have a couple of spares on hand, since they tend to go out in the middle of a project just late enough into a weekend so you can't buy replacements until Monday. :-)

Enjoy, DoN.