Refrigerent substitution

I was wondering if anyone knows the basis for the 80% ROT, when upgrading an R12 refrigerent system to use R134?

What property necessitates the use of less charge?

JW

Reply to
jw
Loading thread data ...

IIRC, R134A is both somewhat less dense than R-12, and it boils at a higher temperature per a certain pressure.

In a CCOT system, that would normally only require reducing the size of the oriface tube, and _maybe_ reducing the charge so as not to cause a hydrostatic block on the liquid side. In a thermostatic expansion valve system, you might not have to do anything.

In a capillary tube system, it would require reducing the charge both to avoid hydro-lock, and to establish a lower pressure on the evaporator side.

LLoyd

Reply to
Lloyd E. Sponenburgh