Grant Erwin wrote in news: snipped-for-privacy@corp.supernews.com:
Grant,
I had the same experience. One of our physics profs bought 5
120v/2KW variable voltage transformere from MPJA. They were to be used to control heat tapes wrapped around a vacuum chamber. He complained that they popped 20A breakers at turn-on about 90% of the time. Only one transformer per breaker. I went through all the possible senarios that have been mentioned. They would trip the breaker loaded, no-load, wiper in any position form zero to full. Wiring was correct. Called MPJA and was told that we needed higher current breakers. :( Not happy with that blunt answer! Since the transformers were "Made in China" and labeled "Variac", but didnt look up to what I come to expect from VARIAC, I contacted "VARIAC". The person I talked to there said the same thing...bigger breaker. He just said that high current autotransformers...even theirs...have a very high initial current draw.When I look at the windings, there aren't that many...and of about 12Ga wire, primary and secondary being the same. I suppose that the inductive reactence at 60Hz is relatively low compared to the very low resistance of the windings...not limiting the inital current at turn-on...and depending where in the voltage cycle that occured.
Also emailed VARIAC about the name, since the labeling on these Chinese knock-offs were an obvious trademake violation.
Not an engineer...just a tech...passing on information...I won't argue the theory.
Ken