>>So, the welder "really" does not care what combination of neutral and phases
>>enter the box. The welder would not care if a 120 volt adapter was
>>connedted to black and red, red and white, or black and white. It is
>>equally happy with two phases and a neutral, three phases, two phases and
>>higher voltages on the phases?
>>
>
>
> Correct.
> I have had my Maxstar 200DX for 3 years and it has the same Autoline > circuit.
> I have run it off of pretty much anything.
> I standardized on a 14L20 connector for the machine, and just made upa
> pile of adapters for every other possible plug.
>
> I like 14L20 and 14L30 twistlocks because you can buy premade 25 foot
> extension cords from Yellow Jacket.
>
> They are intended for use with small generators.
> I have 3 of them, so I can go 75 feet from whatever power I find on a > jobsite.
> I have one female 14L20 plug with bare leads on it for hotwiring into a > power panel.
>
> BTW if you plug an inverter into 460 volt 3 phase it will make some
> really odd clicking chirping noises.
> Don't worry it is supposed to sound like that and will work fine. >
>
>
>
>>
>>>>>>
>>>
>>>>I am in the process of shopping for a welder. Based on what I have read
>>>>about their flexibility, an inverter looks like a good bet and I have not
>>>>read anything bad about the Dynasty, other than the price and its other
>>>>features may cancel that out. The machine will probably still be working
>>>>long after I quit.
>>>>
>>>>It appears the machine will work from virtually any ac outlet the plug >>
>>you
>>
>>>>install on the end of the cord will fit. I assume this includes either a
>>>>standard 120 volt outlet or a 240 volt dryer outlet. Not being an
>>>>electrician, how does this translate to the diagram in the downloaded
>>>>instruction manual which shows an L1, L2, and ground for single phase? >>
>>Is
>>
>>>>that ground, neutral and black, a 120 volt connection (red is shown as >>
>>not
>>
>>>>connected and taped off to the side)? The three phas diagram is shown as
>>>>ground, L1, L2, and L3. Is this ground, neutral, black, and red? It may >>
>>be
>>
>>>>the 3phase distinction that is confusing me. Does that connection cover
>>>>anything that is not 120 volts?
>>>>
>>>>Thanks for the help clearing up the confusion.
>>>>
>>>
>>>The white lead is neutral only on 120 VAC. Both the black and white
>>>are hot on 240 VAC single phase. On three phase, the phases are
>>>black, white, and red. Green is always ground.
>>>
>>>I deviated from the directions on mine by wiring all three phases to a
>>>three conductor plus ground twistlock. Currently, I'm running it on
>>>an adapter cord I made up to go to 120 VAC. I only used a three
>>>conductor adapter cord, and didn't wire the pole matching the red
>>>lead. When I run a 240 VAC circuit to the garage, I'll do the same,
>>>just avoid landing a wire on the terminal matching the red wire lug
>>>(and triple check it before plugging in). This is conveniently
>>>labelled (X) on the Hubbell plugs I'm using.
>>>
>>>This would allow me to use the rig with three phase without re-wiring
>>>the main cord, if I get lucky someday.
>>>
>>>Regards,
>>>
>>>Pete Keillor
>>
>>
I have my Dynasty 200DX wired into a 3-phase plug. The 3-phase "loose" socket - one of its pins - the L3 - is not connected to anything as a standard 3-core (wire) lead comes into it, from single phase mains. Could plug welder into 3-phase if it were available, therefore.
This is in the UK, with 240V 50Hz power (std 13A off a wall socket - typically 2 13A outlets in one wall fitting suggests something about 26A which I won't state (240x26 is a lot of power!) and the cooker is always on a 30A spur which has a plug - good place to plug in a welder)
Richard Smith