TIG high frequency trips GFIs in shop... WHY!!???

Okay you geniuses out there...
I have a Miller Syncrowave 250 TIG machine. I normally use the high
frequency start when welding, but 90% of the time, it trips a GFI
outlet.
This GFI is on a different circuit (obviously) than the hard-wired TIG
machine and the GFI breaker for another circuit in the box never
trips.
I used to work at another artist's studio where the same damn thing
happened but with his GFI breakers in the breaker box.
Someone suggested the work table wasn't grounded enough, so I tried
running a set up jumper cables from it to the copper grounding wire
for the building with no luck.
What's going on here?
I just want to listen to the radio when I'm working.
Thanks,
James Kelsey
formatting link

Reply to
RainLover
Loading thread data ...
The GFI will be less likely to nusance trip if each outlet has it's own GFI.
Reply to
R. Duncan
Battery powered radio don't need GFI.
Reply to
R. Duncan
Is there a need for a GFI on that particular circuit or that particular outlet location? If the outlet is not out-of-doors or in a wet area, I am curious why one would have so many GFI outlets (i.e., no non-GFIs where a radio could draw power)? Ciao, David Todtman
Reply to
David Todtman
James,
Obviously electrical interference from the high-freq start is getting into the GFI device. GFI's have toroid coils in them with the two wires (hot and neutral) passing through them. If all of the current that goes out the hot doesn't come back on the neutral it senses this imbalance which can be as small as 0.005A, amplifies it and fires the trip circuitry within a few milliseconds.
You can see it wouldn't take too much interference to upset this device. Obviously removing the GFI would cure the problem but first check to see if the supply wire for the welder runs near the wires for that particular circuit; if so, move them apart if you can. Also, look inside the panel if you feel comfortable doing so and once again see if the welder's wires (both hot and neutral and perhaps even the safety ground) runs close to that circuit. If say the breakers for the circuits are close together consider relocating one of them in the panel. If this doesn't work and a GFI is needed on that circuit, I would try a different one; it may be less sensitive to extraneous electrical noise.
Wires that run parallel to each other can have considerable coupling for high-frequencies.
Hope this helps,
Billh
Reply to
billh
It sounds from your description that the GFI breaker is in the breaker box near the breaker for the welder. I would try replacing the GFI in the breaker box with a standard breaker and install one of those outlet combined with GFI at the first outlet served by that circuit. The outlet combined wih GFI can be wired so that all the outlets after it are also GFI protected. A combined outlet and GFI breaker will only cost about $7 or $8.
Dan
Reply to
Dan Caster