I'm getting a ton of conflicting info on what size phase convertor I will need. The machine is a Mazak 250 MSY and is 56 KVA. If anyone is successfully running one on a convertor, what HP size is required? I've got

200 amp single phase input, but could go higher if needed. Dixon
Reply to
Dixon
Loading thread data ...

56 kva at 230vac works out to ~243.478 amps.

HTH

Reply to
over a barrel

Umm, 240 V x 200 A is 48 KVA. Sounds like you have a problem. Gee, a 56 KVA phase converter is going to draw a HUGE amount of lagging VARS, even before you turn on the Mazak. This can be compensated to some extent with a capacitor bank. This sounds like the kind of machine that REALLY wants to run off 480 and REAL 3-phase. To work right, you'd need something like a 150 Hp motor in the converter. The starting surge of that motor on single phase would likely be in the 1000A range. You can possibly reduce that with a soft-start circuit, but the idling current is still going to be very high. Doing a little net research, it appears to have a 30 Hp/30 min rating on the spindle, so I think the 56 KVA might be a bit high. Maybe that includes the starting surge of the spindle VFD.

Jon