I have a 100 amp sub panel in my attached garage that is 2 feet from my main panel and was put there due to spaces in the main panel running out. ANyway, from this sub panel I was going to run another subpanel in a detached garage I just built.

Upon inspection, the sub panel in the attaached garage that is 2 feet away from my main panel is Essex 4-3 NMB cable. Is this by code able to carry 100 amps? I bought 3 # 3's and a # 6 ground for my run to the detached garage.

Do I need to replace that wire with # 3 also? When I installed that first sub panel 7 years ago that is the wire the wire supply house told me to use.

Reply to
stryped
Loading thread data ...

#4 THHN is only rated for 95 amps, not 100. #3 THHN is rated for 110 amps. It is unlikely that you will ever reach a 95 amp draw in the panel making the #4s okay. But in my opinion, since you're in there and you're buying some #3 anyway...I'd replace the attached garage sub-panel #4 feeders with #3 ones and call it a job done well and done correctly.

Reply to
Rich.

Unlikely a problem, but does code allow that? In theory you *could* overload the cable.

If in doubt, go up a size. It'll reduce the drop when large loads are used. A motor that draws 10A running can draw close to 100A for a brief surge. Friend of mine had an air compressor in his workshop that despite being on a 15A circuit, would take a couple seconds to come up to speed. I measured and found the voltage at the receptacle would drop to around

85V when the motor first switched on. We rewired it for 240V and ran a new circuit with #12 and it starts instantly now.
Reply to
James Sweet

Isn't it really time you learned a little basic electrical installation practice? The infinitely patient people in this group have done an enormous amount of work for you, and I don't recall seeing many expressions of thanks.

John

Reply to
John Nice

With all of the questions he's asked, I think he now falls into the category of having learned a little basic electrical installation. One of the reasons some of us are even here is to help people like him that don't have all the answers or don't know exactly what to do. I'd rather answer 100 questions instead of learning someone died because they didn't ask even one. Yes it's nice to hear a thank you once in a while, but at the same time it can get old and meaningless after so many times. To me, helping is it's own reward, I don't need anything beyond that.

Reply to
Rich.

I do appreciate everyone's help and through asking these questions have learned alot. That is one reason when I looked at that wire and it said 4-3 I knew that something might not be right.

Reply to
stryped

PolyTech Forum website is not affiliated with any of the manufacturers or service providers discussed here. All logos and trade names are the property of their respective owners.