Existing wiring for electric range

I had to replace the 3 prong receptacle for my electric range. I noticed that the wiring consisted of 1 black insulated wire, 1 white insulated wire and 1 bare wire. I took a peek in the circuit breaker box and found that the black and white wire are the hot leads and the bare is the nuetral. Is this normal? I would have thought that all three wires should have been insulated. Also, the bare wire is not as thick as the insulated wires. I'm a bit concerned and any information would be appreciated.

Reply to
StefanoN
Loading thread data ...

Absolutely correct for that type of configuration. The NEC does not have a wiring code except for a couple of situations that you do not need to be concerned with, in the residential arena. Using a white wire as a hot is very common especially with 3 wire cable, for 240 volts. It is common for the ground to be smaller than the conductors in your situation.

Make sure everything is tight and be at peace with the world.

At least about this, humor

Reply to
SQLit

Not "absolutely" correct. The NEC requires an insulated ground in this case since it will be carrying the neutral current from the control and pilot light circuit which operates at 120 volts. Also it is only going to work if it is landed in the service panel and not a sub-panel, since the neutral and ground would be separate in a sub panel. A correct configuration therefore, would likely be a black, red, and a white for a 3 wire plug. Current code requires a 4 wire plug with separate ground and neutral, which would be a Black, Red, White, and a bare ground. If your plug was installed prior to this requirement, it is likely to be "Grandfathered" in, depending on local code.

Reply to
Long Ranger

P.S. , The white wire is required to be colored by paint or other indelible means, (not tape) , if it is landed on a breaker. A white wire is a neutral, according to the NEC.

Reply to
Long Ranger

Don't they now use a 4 wire cable? Black and Red for power, White for return and a bare ground.

Reply to
Rich256

Yep. It was earlier on when they used that config. Once upon a time you didn't have to ground switches or recepticles either.

Reply to