The existing box should be a 4"x4" square box with a single gang plaster (p)-ring. Acquire a 4"x4" double gang p-ring. After (turning off the power) and removing the existing receptacle, center the double gang p-ring over the the opening and pencil around the perimeter of the…

Read the full reply

If there's a better forum for residential and commercial electrical supply wiring questions, please forgive and inform.



I want to expand a single duplex outlet to dual duplex outlets. If this were a romex type wire job, it would be a no-brainer. But this is a small office building with metal conduit entering and leaving the box, so besides it being nailed to the framing member behind sheet rock, the conduit makes it pretty hard to remove the box and install another.



How can I do this? I thought of adding another box to the side of the existing one with a close nipple between and just routing the wires to the new box. Cover the old box with a blank plate and put the duplex outlets in the new box.



That's my current plan. Any suggestions to the contrary?



Thanks,


The existing box should be a 4"x4" square box with a single gang plaster (p)-ring. Acquire a 4"x4" double gang p-ring. After (turning off the power) and removing the existing receptacle, center the double gang p-ring over the the opening and pencil around the perimeter of the p-ring. Take a razor knife and cut out the drywall on the pencil marks. There will be two screws in the corners of the box catty-cornered from each other.....you'll have to dig the drywall out from around them. Remove the screws and the single gang p-ring, then install the double gang p-ring and mud around it. If you are careful a regular size double duplex receptacle cover plate will hide everything, if not use an oversized one. Be careful..........if you see more than one circuit in the box, be sure to de-energize those circuits also before working with the neutral.

Yes, this would be the way to go, but if the object is to have more places to plug in lightweight office equipment, then the cube would be a lot less troublesome and less expensive, and be more effective and provide more outlets, as long as there was no intent to plug in window air-conditioners, and other heavy duty appliances. The cube would provide 3 outlets to the one, and in the case of a duplex outlet, would provide 6 places to plug into. The cube can be purchased at your local hardware or Home Depot store.

ever consider one of the outlet expanders. I bought one that plugs into both parts of the recpt and gives me 6 places to plug in equipment. One of them even has a surge arrestor in it.

>

On Mon, 29 Sep 2003 5:12:46 -0700, Zathera wrote (in message ):

Seeing how it was the local fire inspector who was attracted to our use of our extensive use of extension cords and power strips, I don't think he'd be amenable to this solution.

He said to provide more outlets for direct plug-in of equipment.

On Mon, 29 Sep 2003 0:56:44 -0700, volts500 wrote (in message ):

Thanks, V500. I never thought that the box would already be a 4-square.

Adding another box alongside the original should be fine and meet Code.

--- sam | Sci.Electronics.Repair FAQ Home Page:

formatting link
Repair | Main Table of Contents:
formatting link

+Lasers | Sam's Laser FAQ:
formatting link
| Mirror Site Info:
formatting link
Important: The email address in this message header may no longer work. To contact me, please use the Feedback Form at repairfaq.org. Thanks.

Well, theoretically yes, but practically no. Fire inspectors don't like lots of extension cords. They can heat up, short out, get kicked, all sorts of abuse that cannot happen to wall wiring, regardless of the overall circuit load.

That is exactly what this device does. It provides more outlets. Less hassle and less money

formatting link
If indeed you created a rats nest of wires, then I doubt that even this device will help as you have stated that you are to install a new receptacle NEXT to the existing one. You might need more circuits/outlets in different locations. Have you considered wiremold or Plug mold.
formatting link
This is what I use for my office.

Once upon a time in Prescott AZ there was a fireman who ran an electric space heater on an extension cord across his daughters bed. The cord caught the bedding on fire and he was heralded as a hero because he installed a smoke detector in the bedroom. I heard about it on the news and called the fire department and suggested that the guy get sent to electrical 101 training again. Since he was supposed to be trained not to do these things.

It is not my intention to be condescending. I am trying to help and sometimes my thoughts and my text are not the best of fellows. Sorry if I have offended.

Just a side note: Be aware that electrical code prohibits "hidden or concealed junction boxes", therefore if you add a double box and then want to cover the original single one with sheetrock/paneling (instead of just making it wider) then that violates code.

On Tue, 30 Sep 2003 16:00:51 -0700, Pac-Fan wrote (in message ):

Yes, I was aware of this. While having the boxes side-by-side is a little more difficult to find covers to fit, I wasn't going to hide the original.

Outlet expanders: Presuming this is in North America. Yes; usually only a few dollars (even the protected ones) and while the ground pin is common, even if the outlet is 'split' i.e. different 115 volt 'poles' on top and bottom of the existing outlet, the expander will (at least the ones I've got) give you three outlets from the top of the duplex and three from the bottom. But since the clutter of AC wires in the area of the outlet will be the same what's wrong, especially with 'normal' office loads, with with an outlet bar, possibly incorporating a small circuit breaker and/or voltage protection. Quick, cheap, an easy to do and portable solution.

Because of the problems of sistering up a box you are probably better off to put the second box a few inches away. Run a short piece of Type MC, AC or FMC between the boxes. If you make the MC several inches longer than it has to be and feed the boxes from the bottom you should be able to work through the hole you cut for box#2 to feed the original box and use an "old work" box so the hole is covered when you are done.

Zathera,

I have read a number of your posts offering advice to others connected with serious electrical safety issues. My suggestion is that you get off crack or whatever mind enhancing drugs you are using. If it is not drugs then you need to complete high school.

Regards,

John Phillips