Why the electrical generators are always connected in delta?
Generators!!
Mar 27, 2007
8 Replies
ohh sorry... i mean to say NOT CONNECTED IN DELTA?
Who says they aren't?
Perhaps because for a given load, the currents are higher in delta, and copper is expensive and heavy?
Whether connected delta or wye, the same amount of copper (in principle) is required for a given kVA rating. Insulation thickness and other factors may have a second order effect on how efficiently the copper can be used.
Bill
-- Fermez le Bush--about two years to go.
--------------------------------------- They aren't. Probably more are connected Y.
Capacitive impedances between conductor and ground are relatively high so ground faults in a delta machine can result in appreciable current at the fault point- chewing holes in the iron and the conductor but low enough not to be easily detected. If you do have a fault it is better to be able to detect it quickly and clear it quickly. In addition there is some actual cost advantage to a Y connection- particularly at higher voltages.
All in all, the choice is made on the basis of actual experience.
| On Mar 27, 11:30 pm, "Ali" wrote: |> Why the electrical generators are always connected in delta? | | ohh sorry... i mean to say NOT CONNECTED IN DELTA?
Why would they need to be? You could have the generator wired in Star/Wye and the load wired in Delta.