Generators!!

Why the electrical generators are always connected in delta?

Reply to
Ali
Loading thread data ...

ohh sorry... i mean to say NOT CONNECTED IN DELTA?

Reply to
Ali

Who says they aren't?

Reply to
contrex

Perhaps because for a given load, the currents are higher in delta, and copper is expensive and heavy?

Reply to
contrex

Whether connected delta or wye, the same amount of copper (in principle) is required for a given kVA rating. Insulation thickness and other factors may have a second order effect on how efficiently the copper can be used.

Bill

-- Fermez le Bush--about two years to go.

Reply to
Salmon Egg

--------------------------------------- They aren't. Probably more are connected Y.

Reply to
Don Kelly

Capacitive impedances between conductor and ground are relatively high so ground faults in a delta machine can result in appreciable current at the fault point- chewing holes in the iron and the conductor but low enough not to be easily detected. If you do have a fault it is better to be able to detect it quickly and clear it quickly. In addition there is some actual cost advantage to a Y connection- particularly at higher voltages.

All in all, the choice is made on the basis of actual experience.

Reply to
Don Kelly

Reply to
Long Ranger

| On Mar 27, 11:30 pm, "Ali" wrote: |> Why the electrical generators are always connected in delta? | | ohh sorry... i mean to say NOT CONNECTED IN DELTA?

Why would they need to be? You could have the generator wired in Star/Wye and the load wired in Delta.