MV Distribution w/Floating Neutral?

Hello, all. I was in Cedar Rapids, IA recently (I don't reside there) traveling along Rt. 100 (Collins Rd) in northeast of downtown. I noticed utility poles with a single cross arm accommodating 4 medium voltage (MV) line wires. This clearly wasn't the usual 3-phase MV distribution with 3 wires on the cross arm with the neutral attached to the pole below the cross arm. I later examined Google satellite images along this part of Collins Rd and it appears one of the 4 wires may be the neutral (not the same insulator as the other 3 wires but on some poles they were the same) but no indication if it's earthed at regular intervals. If any of you folks have further info it would be appreciated and instructive. Just never saw this arrangement before. Sincerely,

Reply to
J.B. Wood
Loading thread data ...

I happened to get lucky when I took a look.

formatting link
(Google Street View) On the pole to the right there are three lines at the top and a neutral at the pole's midpoint, the usual arrangement. To the right there are 4 lines on top. The neutral rises from midpoint to the top over the span.

I have seen this before on older setups, including up the road from me.

Reply to
Michael Moroney

Hello, and aha! I missed that one! Thanks for taking the time. I have seen in a number of instances in other locales utility poles with two cross arms. The upper cross arm has 4 wires and the lower one has 2 wires. In this case I think it's two sets of 3-phase MV distributions. I have also seen (mostly in dry desert regions of the U.S.) utility poles with one cross arm hosting 3 wires and the obvious lack of a neutral. These runs usually cover many miles between loads with the primaries of MV-LV distribution transformers at the load locations connected line-to-line rather than the usual line-to-neutral. If for some reason a neutral is required at some location(s), grounding transformers can be employed. These areas are wide-open and dry most of the time. MV line faults to ground are probably rare. Thanks again for taking the time.

Reply to
J.B. Wood

I believe that is correct, two circuits. Especially when often one circuit heads off in one direction and the other in another direction.

In the northeast US, many older rural areas have the MV distribution voltage wired as delta, transformer primaries connected line-line. Often these use a lower MV voltage, such as 4800V line-line.

Often the electrical company will upgrade the lines in stages. The portion closest to the substation is upgraded first, almost always Y connected with a neutral. At the end of the upgraded section there is a transformer bank, connected Y-delta if the older section is delta. I've noticed one section upgraded 3 times over a decade. The first Y-Delta transformer bank was just south of an intersection, later it was just north of the intersection (because they upgraded the lines on the crossing road fed at the intersection) and now a smaller bank is several miles north.

Reply to
Michael Moroney

Hello, and my thanks again for providing further comment. Just wondering whether delta-delta connected autotransformers are used for the above purpose for interconnecting two 4-wire (Y) MV lines having different voltage ratings. In this case the neutral wire is pass-through. I've seen overhead devices on MV lines that at initial glance appear to be MV-LV pole-mounted distribution transformers but on further examination have a total of 6 bushings on the MV side and no LV bushings or obvious connections to LV subscribers. These units also don't have the footprint of "classic" MV voltage regulators. So I figure they're either autotransformer voltage boosters/reducers or ... Never saw them as off-the-shelf offerings in old GE, Westinghouse or ABB transformer catalogs. VTY,

Reply to
J.B. Wood

A quick look at the last transformer bank I mentioned looks like it may be connected delta-delta, not Y-delta as I said. I will have to take a closer look. Downstream of it is definitely connected delta, I am quite sure upstream is connected Y with neutral.

How many transformers in that group? 2 or 3? Sometimes they can use 2 when wired delta (open delta) with a derating.

If you know an approximate address, Google Street View may show it.

Reply to
Michael Moroney

Here's something not far from my residence: https://www.google.com/maps/@38.8784824,-77.1223311,3a,15y,328.87h,108.47t/data=!3m6!1e1!3m4!1sihLOkGP6jV8Ahnmq9m3eFg!2e0!7i13312!8i6656

What do you make of it? VTY,

Reply to
J.B. Wood

Looks like a boost transformer setup to me. Note the isolating insulators on each side of them and windings going to each side of the isolation. That is wye distribution IMHO based on the transformer connection down the street that is feeding the triplex. Going the other way there looks to be a 3p 208 wye that is abandoned for some reason by that parking lot. I never saw much 3p delta vee (red leg) up there when I was in the computer biz. Everything was 208 wye. It does seem pretty popular in SW Florida. The transformers look like this.

formatting link
That will be 2 transformers, one larger than the other. The big one feeds 120/240 loads and the smaller provides the 3d leg of a 240v delta. You see it in light industrial bays, usually, where they have a small 3p load and larger 120/240 loads.

Reply to
gfretwell

Hello, and thanks for the reply. I was focused on what pole-mounted devices might be used for MV-to-MV voltage boosting and not involving any LV interconnections. A 3-phase (delta) autotransformer (would have a total of six MV terminals) would seem appropriate (think of an equilateral trangle with another inscribed equilateral triangle as representative of the MV-MV connection.) I just haven't come across any MV distribution hardware online to accomplish this. Electromechanical MV voltage regulators (with their long tanks) can be used as well. I did come across a MV voltage regulator that has the footprint of a distribution transformer (Cooper Power Systems model S225-20-1 and available for up to 19.9/34.4 kV MV systems). IOW, it doesn't look like a traditional long-tank MV voltage regulator at first glance. Sincerely,

Reply to
J.B. Wood

I agree it is a wye connected MV-MV stepdown configuration, despite having

3 bushings/can rather than two + neutral. It appears to be fed from the commercial area in the direction away from the residential area. It is fed from the top of a 2 circuit setup, the top circuit has different/larger insulators so it probably is at a higher voltage than the bottom one.

I have seen similar configurations for converting 13.8kV to lower, wye to wye. Some appear to have a metering current transformer on the neutral legs, going to meters on the pole.

BTW across the road from the abandoned setup there appears to be a red leg delta configuration on a pole. Two transformers of different sizes fed from 2 of the 3 MV phases.

Reply to
Michael Moroney

Here are a pair of open delta connected regulators.

formatting link
I believe they operate at 4800V line-line.

Next pole(s) up the road have a wye-delta transformer bank supplying them.

Reply to
Michael Moroney

That photo is representative of the usual footprint regulators that I previously referred to and even when viewed at a distance you know what it is. Sincerely,

Reply to
J.B. Wood

I mentioned them since your earlier reply indicated that you thought delta connected regulators didn't exist or you didn't know of any. Perhaps I have misinterpreted your reply.

Reply to
Michael Moroney

Hello, and I failed to make the distinction between a fixed (with or without manual tap changers) MV booster transformer and a device specfically designed to provide MV voltage regulation. I haven't come across any off-the-shelf pole-mount equipment (except perhaps that Cooper unit) that was specifically designed to interconnect two 3-phase distribution systems having different voltages. Such a device would be useful when incrementally upgrading/creating MV branch circuits to higher potentials, e.g. upgrading a 7200/12470 distribution branch to one that operates with higher potentials (e.g. 7970/13800 or

14400/24940). Eventually the entire MV infrastructure back to the HV substation becomes operational at the new potentials. Sincerely,
Reply to
J.B. Wood

"J.B. Wood" wrote in news:q6tj5d$1dt0$ snipped-for-privacy@gioia.aioe.org:

Delta as opposed to Wye?

Reply to
DecadentLinuxUserNumeroUno

I see those often. Two poles upstream of the regulators I posted is a large Y-Delta transformer bank, and must be the reason for the regulators.

formatting link

Just up the road they upgraded a short stretch from 2400 Y to (I think)

7970/13800, to allow for a solar farm. Both before and after there was a transformer bank and a set of regulators a few poles downstream.
Reply to
Michael Moroney