When wiring two devices for instance a transformer to over current protection device of say 300A, I relaize would require 350kcmil THHW or 300kcmil THHN. Somewhere I thought I remember reading that you have to size wire with the ampacity of the LOWEST temp rated device in the circuit. That is if a panel board is rated at 75 degrees than you must use the 75 degree column in table 310.16 even if you are using THHN wire. Is this correct, and aren't most panel boards and breakers rated at 75 degrees unless specifically designed for 90 degrees? Thanks for the help.