> > Hi > > > > I recently had my solar hot water system replaced. The old one had a 1.8kw > > heater and the new one has a 2.4kw. The installers used the old heater > > wiring. Since then the 10amp switch for the heater failed. It obviously got > > hot and fell apart. My concern is that the wiring may also be under rated. > > I'm in Australia so it has to carry 10A at 240V. My thought is that 10A > > wiring would have been good for the old heater and probably that's what was > > installed. Comments please. > > > > Secondly, how would I approach a contractor for an opinion without giving > > them an open invitation to replace the lot ? > > > > Gordon > > my address needs gj in front > > > > > At 240 volts, the 1.8Kw water heater would draw 7.5 Amps, and the 2.4Kw > heater would draw 10 Amps. To an appliance like this, a #12 guage wire > would be the least that would be installed, although theoretically, a #14 > guage wire would be sufficient. > >JB wrote: > > Presuming the installer knew what he was doing I'd say you had nothing more >serious than loose connection in the switch, try a new one but check it for >temperature when the heater is running

Thanks guys, I'll check the gauge and the temperature. My concern, after the switch failed, was that the installer was a plumber and not an electrician and may not have taken note of the different heater sizes.

Thanks again.

Gordon