I'm guessing that if all the waves were the same shape, it wouldn't make a difference.
Start putting a different shaped wave or one of a different period on each phase and then it's a different ballgame.
mike
I'm guessing that if all the waves were the same shape, it wouldn't make a difference.
Start putting a different shaped wave or one of a different period on each phase and then it's a different ballgame.
mike
I'd like put that thought on hold for a bit. I just had a horrible vision of being attacked by mutant, square shaped things. They were mocking me.
mike
The classic set-the-office-partition-on-fire situation is to have a y-connected 3-phase system, with a common neutral, and run a bunch of PCs off each phase. The PCs pull current at the peak of the AC line, at six different times each cycle, so even if the three load currents are equal and have the same waveshape, they don't cancel in the neutral.
John
From three different directions?
John
PCs? Oh..yeah..I hear there's a new Commodore Vic 20 available now. It has colour, sound, UPPER *and* lower case Fonts..wow.
Actually they did change the rule concerning derating a few years back, due to what you mention. Before, pretty much only that portion of the total building load comprising the lighting could NOT be derated. (and the first 200 amps of non-lighting load)**. The neutral was generally smaller than hots. Now, it's going in the other direction.
Lighting Ballasts were a big offender, with electronic ones even worse.
All the newfangled stuff seems to cause harmonics, which are additive in the neural conductor. That could make the Neutral current greater than the line current.
You inspired to me to find out how bad this stuff is. The following PDF file has some rather interesting tables.
mike
Rectifiers generate harmonics (no surprise).
The "triplen" harmonics - 3rd, 6th, 9th, ... - add instead of canceling on a 3-phase wye neutral.
-- bud--
I don't think it is the rectifiers as much as the chopper in the switch mode power supply banging that toroid transformer. If they just converted the AC to DC and used it there would not be a harmonic problem.
It's the interaction between the rectifiers and the storage capacitor. The current draw only happens for a short period near the peaks of the mains waveform, as the mains voltage rises above the capacitor voltage, and the capacitor is topped up to the peak mains voltage again. (The width/height of this pulse depends how much the capacitor discharges between each peak, which it its ripple - large capacitor with low ripple gives a shorter larger pulse.)
You can see this in the last example (Switched Mode Power Supply) on
Of course, if you have a modern power factor corrected PSU, then it will draw a load all through the mains cycle, so that it looks like a resistive load (as near as possible) with a power factor near 1.
With their harmonicas.
Ed
Have something to add? Share your thoughts — no account required.
Ask the community — no account required