Use different size wire in electro clutch?

Or FSF (Furlong Stone Fortnight).

Reply to
krw
Loading thread data ...

Metric magnet wire (enameled copper wire to you) is usually specced in diameter, rather than cross sectional area.

Reply to
Fred Abse

"About 12 gauge" is hardly an engineering statement. Didn't they use a micrometer?

Possibly 2mm diameter.

(maybe slightly

#12 wire is 2.053mm dia. #10 is 2.588.

Best practice would be to wind for the same number of amp-turns as before.

From wire tables, changing from #12 to #10 wire,the resistance of the same number of turns will decrease by a factor of approximately 0.6. The current will correspondingly increase by a factor of approximately 1.6, hence so will the amp-turns, assuming the supply voltage stays constant. How much the strength of the magnet will increase depends upon the magnetic properties of the magnet iron. If the magnet was originally operated close to saturation, the increase in pulling strength may not be very much.

The power dissipated in the copper is proportional to current squared, hence 1.6 for the same voltage. The coil will run hotter.

There's also the issue of supply regulation. Will the transformer supply the increased current without significant voltage drop?

Why did they rewind it using #10? Didn't they have any #12? I'm surprised they didn't have metric sizes, there are a lot of Japanese and European motors around.

Reply to
Fred Abse

Long ago I reclassified all my enamelled copper wire into potrzebie units for simplicity

Reply to
Ron

Now you're just teasing the donkey, who can only count to four that way...

Reply to
Michael A. Terrell

You're wayyyy off base...

Reply to
Michael A. Terrell

No, my position is pretty safe.

Reply to
krw

Otherwise agreed. Any world wide "Standard"agreement is an extended version of what is going on in Copenhagen- politicians and special interests drag it out indefinitely as it is important to get ones first class travel to expensive places -preferrably in a warm place with cheap booze.

Reply to
<dhky

All your base are belong to us

Reply to
Ron

The USA is 'supposed' to be metricated. hy you choose to be so backward never fails to amaze me. Any given wire gauge covers a wide range of cross-sectional areas. At least you know what you're getting with mm2.

Graham

-- due to the hugely increased level of spam please make the obvious adjustment to my email address

Reply to
Eeyore

It is indeed. AWG does not specify an explicit conductor CSA.

TOTALLY universal except for the USA, Liberia and Burma / Myanmar, both somewhat backward countries you have chosen to retain compatability with. Some might say the USA is rather backward too. The high level of belief in religion is one pointer to that.

Conversion is a waste of time and a source of errors. There is only ONE system of units I need for engineering.

And what did you get from going to the Moon ?

Furthermore we have ESA

formatting link
Galileo
formatting link
It knocks spots off GPS.

Graham

-- due to the hugely increased level of spam please make the obvious adjustment to my email address

Reply to
Eeyore

Oh dear ! Is that how it was specified ? At what temperature btw ?

Graham

due to the hugely increased level of spam please make the obvious adjustment to my email address

Reply to
Eeyore

What an absurd comment. Do you have 12 fingers so you can count in inches to the foot ?

Graham

-- due to the hugely increased level of spam please make the obvious adjustment to my email address

Reply to
Eeyore

LOL ! Give me a thou over a 'mil' anyday. Only the Americans could confuse a metric prefix with an old unit.

Not to mention that if you use the word 'mil' in the UK it means a millimetre.

Graham

-- due to the hugely increased level of spam please make the obvious adjustment to my email address

Reply to
Eeyore

I didn't go bonkers at all. I just picked an easy target to stir you up.

We can convert too, you know. Thankfully only an issue for you lot.

Why don't you use it ?

Graham

-- due to the hugely increased level of spam please make the obvious adjustment to my email address

Reply to
Eeyore

I don't see cubits mentioned there.

Graham

due to the hugely increased level of spam please make the obvious adjustment to my email address

Reply to
Eeyore

What's the matter, challenging for you?

Reply to
Jamie

I will try to remove the bad taste with a swig of Coffee/rooibos.............. Nah, that failed.

Reply to
Sjouke Burry

Yes, we use the binary way!

Reply to
Jamie

The way I see it, you're not able to comprehend the vast complexity of the intellectually enhanced American!

Did that just about sum it up?

Reply to
Jamie

PolyTech Forum website is not affiliated with any of the manufacturers or service providers discussed here. All logos and trade names are the property of their respective owners.