Can a 50 Hz motor run on 60 Hz

Check this out (baldor.com long URL)
http://tinyurl.com/yr6xtj
This describes a single phase 2850 RPM motor. Can such a motor be run
from 60 Hz?
i
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Thu, 07 Jun 2007 09:03:31 -0500, Ignoramus27187

Yes, but it will run at 3420 RPM.
Thank You, Randy
Remove 333 from email address to reply.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Jun 7, 8:03 am, Ignoramus27187 <ignoramus27...@NOSPAM. 27187.invalid> wrote:

50 Hz on 60 Hz is not problem, it just runs faster. 60 Hz on 50 hz usually won't work, there's not enough iron in the guts and it would run slower anyway as well as overheating.
Stan
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Funny, we have around 400 60 Hz motors running on 50 Hz David

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

It will run, but might not produce the rated 1HP at 120V. Call Baldor for a better estimate.
Randy
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Randal O'Brian wrote:

Wrong. 50Hz motors can always be run at 60Hz. 50Hz motors cost a little more because they have to be wound with a little more copper. 60Hz motors can't always be run at 50Hz, but 50Hz motors can always be run at 60Hz.
GWE
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Grant Erwin wrote:

The OP might have meant torque rather than horsepower. If so, he would have been right.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
More things are at bay than just speed - and that is a natural.
Power is most important as well. Sometimes there won't be enough power designed in a core that is to large for the frequency provided.
A low frequency has a large core, high frequency uses lighter cores.
The core size - mass or volume determines the power ability.
It might be just fine. You might not ever need the full power either.
So you might have a ok dual frequency motor or just never need to push it the full extent.
Martin
Martin H. Eastburn @ home at Lions' Lair with our computer lionslair at consolidated dot net TSRA, Life; NRA LOH & Endowment Member, Golden Eagle, Patriot"s Medal. NRA Second Amendment Task Force Charter Founder IHMSA and NRA Metallic Silhouette maker & member. http://lufkinced.com /
Ignoramus27187 wrote:

-
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Yes. Almost any 50 Hz motor can be operated on 60 Hz, and visa versa. Voltage, RPM, and output power scale with the frequency. For this motor the factor is 60/50 or 1.2 so 2850 RPM goes to 3420 RPM, 110 V goes to 132 V, output power capability will go to 1.2 HP. Current will stay the same as 50 Hz. It will think it is running on low voltage, but because this motor has a service factor of 1.25 you should have no problem getting the full 1 HP, even if it runs a little hotter.
--