does 440 volt power exist?

Don't forget 565, 600, etc. Our Canadian (Quebec) friends may be offended.

As a side note, 208 seems to only exist in very old cities these days and sporadicaly here and there elsewhere.

Regards, Joe Agro, Jr. (800) 871-5022

01.908.542.0244 Automatic / Pneumatic Drills:
formatting link
Spindle Drills:
formatting link
V8013-R
Reply to
Joe AutoDrill
Loading thread data ...

208V is extremely common, as the 120/208V Y three phase service used in nearly every light commercial building in the US.
Reply to
Pete C.

Must be a regional thing. Here in Maine, in large industrial settings,

208/120 wye is very common for small loads and 480/277 wye for larger loads.

Since we're close to the Canadian border, and machinery seems to get shuffled back and forth, it's not unusual to run into 550-600 volts.

Reply to
Ned Simmons

Interesting. Especially the 550-600V stuff. I've only run into it in Canada and I think Turkey.

Only place I've run into 208 is old sections of NYC, Chicago and other "older" cities. maybe it's just that industrial areas were built with the

220 circuits because I basically only sell into heavy industrial areas...

As they say, learn something new every day. What they forget to tell you is that every new thing you learn seems to force out an old memory to forever be forgotten. :)

Reply to
Joe AutoDrill

120/208 Y is a very advantageous setup to have if your loads are not large and you also can benefit from having 3 phase. There is no wild leg to be concerned with and you only need one service panel. Sure, in some cases you may need to up your wire gage to account for the reduced voltage but this would be far less than the cost of a seperate panel for your 3 phase loads.

Shawn

Reply to
Shawn

I've seen house power stated as 110, 115, 117, and 120 volt. Ive seen three phase motors marked 440, 460 and 480 volt. However according to my Electric supplier, PPL Corp. (Allentown PA) Power is supplied at

120, 208, 240, 277, or 480 volt all of which are +/- 5%.

Where did all these other numbers come from, or in some parts of the US can you actually get 110V residential or 440Volt 3 phase power?

My shop is right at the +5% limit. 126, 251V (my meter is not true RMS)

Thank You, Randy

Remove 333 from email address to reply.

Reply to
Randy

The 120 and 240 are the nominal supplied single phase configurations. The 208, 277, and 480 volt figures are all various 3 phase configurations.

In the 'old days', the nominal line voltage was 110 volts, 220 volts, and 440 volts depending on the service. The power companies discovered they could get more power (watts) through the same wires with higher voltage. This has led to voltage creep over the last century or so. This is where you get your "110, 115, 117, and 120 volt" figures. Currently, my residential line comes in at a pretty consistent 123 or 124 volts.

During heavy load conditions (heat wave and air conditioner load), you will get voltage sag so your power co may deliver 126 volts in the early morning, 114 volts in the afternoon, and still be in tolerance. Some older systems may allow the sag to get below 110 volts, that starts to cause motor overheating.

The guys working 2nd shift in our weld shop doing fussy work on thin tubes during the summer would be constantly readjusting their machines as the voltage levels rose from the peak system load time of around 4 pm to light loading at midnight.

Randy wrote:

Reply to
RoyJ

So, I would guess this was an increase by the power co's at the primary voltage level and secondary voltages just went up accordingly. Back in the 80's I worked at AT&T in Allentown PA and at about 3:30 in the morning there was a big explosion on the lower floor. Turned out to be some type of suge arrestor. They changed out every one of them in the plant, when I checked them out (there was a dumpster full) they were marked 9800 volt max, the plant was fed with 12,470 volts. some time in the past the voltage was upped and nobody noticed the little details, took years to fail........

Thank You, Randy

Remove 333 from email address to reply.

Reply to
Randy

The small percentages are a voltage creep over the years. Your example is more like a major upgrade to the lines and someone forgot to make ALL the necessary changes.

In rural areas it was common to have the feeder lines running at 4100 volts, then to the step down transformer in the farm yard. These got bumped to the current 8KV that we usually see. A lot of transformers went to the scrap yard on that changeover.

The fuses for these l> >

Reply to
RoyJ

Was 12,470 the line to line voltage on your 3-phase service? If so, the arrestors (always connected line to ground) were seeing 7200V.

Randal

Reply to
Randal O'Brian

I never realized there was a powder charge involved, or that the intention is to blow out the arc. It definitely makes sense. I've been there for a few "moments of truth" when the primary splice is put to the test...

Reply to
ATP*

Reply to
RoyJ

Can't say, That was the sticker on the side of the conduit and on the switchgear. The arestors were connected to ground, not phase to phase, so maybe is was just age, not overvoltage that caused one to fail. Never saw what was put in, just the dumpster full of old one's.

Thank You, Randy

Remove 333 from email address to reply.

Reply to
Randy

And it also gives them more of a cushion for voltage sag before they get into the 'damaging customer equipment' territory. I'd much rather have it come in a little hot than a little low.

Oh, and a "True RMS" DVM will read a bit higher than an old 6" panel meter at the substation that traces it's roots to a Simpson 260.

Depends on whether that switchgear belonged to the utility or to AT&T. The utilities are pretty good on noticing and correcting those little details, but some Pointy Haired Boss at AT&T might have deleted the line item for replacement arrestors figuring 'it's not critical.'

Amazing thing that Utilities noticed when usage grows, if you double the voltage you cut the current in half - or double the capacity on the same lead. And all you have to do is change out the insulators to handle the higher voltage and make sure you have sufficient clearance, the wire stays the same. Lots of distribution lines were bumped from

2,400V to 4,800V, 9,600V to 34,500V...

The replacement might have been prompted by fine print on the surge arrestor label that said something like "Mfg Date Apr-1952, Replace by Apr-1972" and this was 1988. Oops...

There are some high-voltage switches and circuit breakers that use SF6 gas (sulfur hexaflouride?) to blow out the internal arc. If the gas has leaked out over time it's not the arc that blows out, it's the whole breaker - and rather violently at that.

Moral: If it has a "freshness date", or even a production date, there's usually a reason.

-->--

Reply to
Bruce L. Bergman

The sulfur hexaflouride gas in SF6 breakers is pressurized to a few hundred psi. They all have a pressure sensor or switch that prevents opening the breaker unless a minimum pressure is present. In medium voltage breakers, the gas does not blow out the arc, it is merely present in the chamber where the contacts part. It is extremely resistant to ionization and has a high heat capacity, all of which help to suppress the arc formed between the contacts in a few cycles.

Randal

Reply to
Randal O'Brian

Tell that to Pacfic Greed and Extortion....

Lately Ive been unable to use the VFD on my Gorton MasterMill...single phase 220 coming into the property has been running at 245 volts. The vfd shows an over voltage condition and refuses to start up. A call to PG&Es office brought out a tech, who measured, shrugged and said that was "normal" in my area.

Im about ready to stick in a buck boost.... the bastards......

Gunner

Reply to
Gunner

That's beyond hot, that's high enough to start damaging things if you get spikes and surges on top of it - even cause surge arresters to flash over...

Call the Public Utilities Commission and tell them. PG&E can blow you off because you have no power over them, but when the CPUC calls the Utility and says "Fix It!" they listen.

Unless they've got a really good reason to run it that hot, there is a tap-changer at the transformer they can kick down a notch. Or they can damned well swap it out for a TX that has one.

-->--

Reply to
Bruce L. Bergman

With the nominal voltages now commonly stated to be 120/240 it seems that

245 is only about 2% high. Even for 110/220 it's only a bit more than 10% which is a common tolerance for line operated electronic equipment. What am I missing here?

Don Young

Reply to
Don Young

Most VFDs have a voltage sensing safety circuit that tops out at 240 volts. Most are rated for 230ish voltages.

Above 240 (single phase mind you)...they go into alarm and not start.

Gunner

Reply to
Gunner

I wonder if it might be feasible to tweak the sensing circuit a bit or if

240V is really a good limit and anything higher would be too likely to cause damage? Are current versions still limited to 240V?

Don Young

Reply to
Don Young