A friend of mine has an arc-welder and keeps the generator portion in his shop and runs a 300 foot cable to his forge where he can do his welding in relative quiet.
Somewhere the cable has developed a break.
Initially I thought just following the cable with a compass might help find the break, but as luck would have it the cable is on an almost true N/S line.
I also read that you could trouble shoot the buried wires for early "invisible fences" for pets by just using a small transistor radio, but I can't find the exact info...
Any other worthy thoughts out there?
Thanks in advance,
Chet
Didn't find your answer? Ask the community — no account required.
S
Sunworshiper
LOL , or the earthworms flying out of the ground , or the smoke and steam , or night vision for the hot spot. I would have put it in a 2"+ PVC pipe so you could just pull it out .
L
Leo Lichtman
keith bowers wrote: (clip)Any other worthy thoughts out there? ^^^^^^^^^^^^^ If you end up having to dig to find the break, the most efficient system is to dig at the half-way point. Once you know which half of the cable has the break, dig again in the middle of that half--and so on. You will have to dig about six holes to narrow it down to about 5 feet, and then I would just trench that last part. Lot of work, but it beats digging another 300 foot trench.
J
Jack Smith
If it's paired cable so that the physical spacing between the wires is constant, and the failure is an open, you can measure the capacitance with an inexpensive capacitance meter. Many digital multi-meters include capacitance measurement ability.
Measure the capacitance between the wires at both ends and the ratio of capacitance will tell you the proportional breakpoint. You should be able to hit the break distance within a percent or so if the cable is uniform.
If the cable is just two individual wires separated by random distances, then you need a different approach. The normal way to trace a buried cable is to apply a low frequency signal to one conductor against ground, in the range of a few tens of kHz and use a tuned receiver fed by a detector loop to detect where the signal stops. You may be able to rent one of these devices, or perhaps you have a friend that works for a contractor or utility company that can bring one home for a "government job."
Jack
T
Tom Kendrick
Both cables are probably lying in the same trench. Probably the easiest method is to use the successive bisection method. There COULD be more than one break, though it is unlikely.
- Disconnect both welding cables at both ends, marking which one is an open circuit.
- Connect a low-voltage power source to one end of the open circuit (a
24-volt doorbell or furnace transformer would work).
- Dig a hole into the trench 150 feet from either end. Connect a voltmeter to the low-voltage transformer and to a pin which is inserted through the insulation of each cable (do not know which conductor is which in the trench). If 24-volts is detected, the break is in the other half of the trench.
- If 24-volts is NOT detected, put the power source on the other end of the dead cable and check again before digging more holes. If
24-volts is STILL not detected, there may be more than one break.
- Repeat the above processing the half of the remaining length which does NOT show 24-volts.
- By the time 6-7 holes have been tested, the cable length to be physically examined will be in the 2-4 foot range.
P
PrecisionMachinisT
You * Could* call the power or phone company up and ask for a locate because you are "thinking about some project like a gate or excavation or somesuch.........
Then, when they get out there, have them do the locate in the "proposed" area.......Then see if you can "sweet talk" the guy into checking the welder leads as a favor......
Kinda like " Hey ya know what???......I got these broken welder leads in the ground over here", "I wonder if that unit could be used to find the break real easy"..........
=========
Btw: Ive had good success with the power co in certain areas, whenever I wanted to do quickie electrical work between the transformer and the first mains panel......
Ask if they can come out and disconnect, so you can check and tighten your mains terminals.......I had everything ready to go, so they had no problem having a cup of coffee, waiting while I " tightened the mains"........
In actuality, I replaced the entire 400 A mains fuse / disconnect panel because it was ~ 50+ years old *very* badly corroded........The guys came on down in the basement and actually handed me tools while I did the job.......
Having sworn to discretion regarding the situation, cannot reveal the location where I lived at that time
T
Ted Edwards
It's called a binary search and is *very* efficient. :-)
Ted
M
mike
And as a side benefit, you get lots of little holes to leak water into the cable.
OK, I'll ask the obvious question. How does one break a BIG ole buried welding cable without leaving some evidence on the surface? mike
G
Glenn Ashmore
B
Bill Janssen
You can measure the capacitance between the wires or to ground. Do this at each end and the ratio of capacitance readings gives the ratio of distance to the break.
Bill K7NOM
D
Dan Thomas
Borrow/rent/steal a line finder from an electrician. This doodad has a signal generator that puts a tone into one end of the line, and a portable detector that you pass over the ground. A speaker in the detector will guide you along the cable, and at the break the strength will drop off sharply. Used one several times to find breaks in our airport runway light system, which has about 8000 feet of cable.
Dan
J
jim rozen
The trouble with all the capacitance approaches is, there may well be a break in the cable that prevents it from passing the 500 amp welding current. But there is probably enough of a conduction so that any simple capacitance meter will read the entire line, either line-ground or line-line. IMO.
Jim
================================================== please reply to: JRR(zero) at yktvmv (dot) vnet (dot) ibm (dot) com ==================================================
A
ATP
Faults in primary cables are located by sending short high voltage bursts down the line. Biddle makes the equipment, most mechanics call it "biddling" the cable. The cable shorts from the center to the outside concentric neutral. It doesn't blow a hole in the earth, but it makes a small thump that you can usually hear or feel as you walk the length of the line.
T
Terry Thorne
i bought a circuit/cable tester from Lowes a month or so ago for
60+ bucks, you clip the transmitter on the line and follow with a receiver, got hooked on using one tracking down a broken control circuit on a HVAC system, found it with one(borrowed from a radio engineer, had to have one!
Good luck!
tt
G
Greg O
Gophers are quite efficient at this. If the cable is aluminum all it takes is a nick in the insulation, and time. It will eventually corrode itself in two. Greg
N
NoSheeples
Call any local TV repair shop, and ask if they have a Sencore Z meter. I owned one of these. They will find a short in a cable within 5 inches, but you must have the specs on the wire. The would charge you a service call, but would be that much. If the guy has no clue what your talking about don't ever take your TV there. ;o)
formatting link
"Democracy is two wolves and a lamb voting on what is for lunch. Liberty is a well armed lamb protesting the vote."
E
Eastburn
Far faster in the binary method. Use it in standard searches all of the time.
Might try measuring - say a 12 volt battery - and a cable and a connection to the cable.
Then walk the line - binary ? - probing with a metal probe on the cable. Measure current. Might be small at first - feeble - then grows then lowers... So back up.
If you have the cables in a tube - all of this is a bit mute. But before you draw it out, Tie a nylon line to the end pulling through. Always leave a cord inside - pull a wire and a cord back through leaving a line.
My Dad had run a 220 line through a black water pipe - those in large rolls - he had some left over and thought - perfect for the old barn - run a line from the house... :-)
Well it worked just fine - however - lighting hit a pine tree that had roots near the black plastic line. It burned through and 'grounded' the line.
Needless to say, the line was retired and Dad patched a large loop around that tree.
Martin
C
Chet & Audrey Roberts
Thanks to all who offered a variety of solutions to the problem. Much appreciated!
I'll post the method used to discover and repair the break.
Chet Roberts
I
Ian Stirling
Unfortunately, probably not. These rely on the cable being consistent, with the conductors a specified distance from each other, and insulation around the pair greatly helps too, as it reduces the effect of varying ground.
Two welding cables laid in a trench probably won't qualify.
If the spacing varies, the propagation speed along the pair varies, and it becomes not that much better than guesswork.
T
Ted Edwards
Right answer but wrong reason. The propagation speed won't change much but the characteristic impedance will.
Ted