Why are 12v battery chargers to unreliable

I own a large amount of equipment, and some of it, such as my home generator, is supported by battery maintainers.

Overall, reliability of those has been pitiful. They are sold by "features", "microprocessors", "smart charge modes", have numerous LED status lights, etc.

The reality is that most of them fail in a year, often in moderately cold weather or for no reason at all. Some stop working, some display blinking lights and do not do their job, some drain batteries when they fail etc.

I am personally not even asking for much, just a weatherproof device that keeps the battery mostly charged and not overcharged. Unfortunately, I have not been able to locate anything useful that could survive being out in the weather.

The one item that I had a lot of success with, is a solar battery charger that I use on my rough terrain crane, that one seems to be a champ and the crane is always charged. But the 110v devices are abysmal.

Would anyone recommend some weatherproof charger, the "dumber" and less sophisticated, the better. Thanks

Reply to
Ignoramus30995
Loading thread data ...

Have you used a genuine "battery tender" ?

Have not hrard of any issues with them - a lot of friends using them for years on their "toys" - and they won't boil batteries. Might have to put them in an enclosure of some sort - other than possibly marine chargers they ALL need protection, or they WILL fail.

Generalky "the dumber the better"

Reply to
Clare Snyder

Because far too many people want more power, quicker charging, AND cheaper pricing. Mfgrs overload power transistors, use the cheapest suppliers for everything, and have hacks design the circuits. Then these same people fail to hold the manufacturers to any warranty claims. "It was cheap and I tossed it; lesson learned." But they didn't learn it since they let the mfgr off without any angry feedback.

Yeah, isn't that fun?

Build one into a Penguin case with weatherproof leads?

Why not stick with what works? A portable solar panel is fairly cheap to put in the truck fulltime, then deploy it on the roof when it sits.

I'm still using my dad's old 5A un-weatherproof louvered metal box.

Reply to
Larry Jaques

I meant to add Schumacher Sure Fire 300, 3A, 6/12V from the '60s. Original clamps, cord, analog meter, and everything.

Reply to
Larry Jaques

Put your favourite one under an upturned mortar trough for outdoor use.

Reply to
Volker Borchert

Deltran Battery Tender? ? I have. Exactly the problems that ig described. All of them. Trash.

Reply to
Víðópnir

I've had good luck with the little 800 mA potted Deltran, 1 outside on a rock. I have 3 in service, 1 failure in 5 years. I don't live in snow country.

Pete Keillor

Reply to
Pete Keillor

On Nov 10, 2017, Ignoramus30995 wrote (in article):

What you want does exist in the marine world. When boats are in storage (on a cradle in a boatyard or back years), people often use trickle chargers to keep the batires charged (and thus freeze-proof). These chargers are almost always used outdoors, and are powered by 115 Vac.

Ask around your local boatyards for the best brands. And for the avoid-at-all-costs brands.

Joe Gwinn

Reply to
Joseph Gwinn

"Ignoramus30995" wrote in message news:WoednTsagZda-5vHnZ2dnUU7-I snipped-for-privacy@giganews.com...

I bought the Harbor Freight 99857 to install in my truck and was satisfied that it worked as intended, although I decided to use solar power instead so I can't tell you if it lasts outdoors.

formatting link

I personally like having voltmeters on batteries or easily connected to them so I can tell when they need attention. Cigarette lighter outlets and a meter like this work well.

formatting link

Charging everything on a schedule like the start of each month reduces the time power cords are out to trip on or damage. Old batteries need more frequent topping off to keep them from falling into the high resistance condition called sulfation.

They also need an ammeter to show if they aren't accepting a charge despite apparently correct charger output voltage, which might be your real problem. A solar panel charger forces current at whatever voltage is necessary. The danger is their open circuit voltage >20V which could damage electronics if the battery refuses to accept charge current.

I solve it by increasing the charge voltage above 15V from home-made adjustable linear regulator chargers with these meters.

formatting link

"Lab" or "bench" adjustable power supplies will work if the user knows how.

formatting link

My 2x100W Grape Solar panels arrived and are producing 140W right now,

9AM EST, equal to or slightly more than the APC1400, this laptop, its 19" external monitor and the fridge consume on average, according to charge and discharge wattmeters. They are already at their rated MPP current with the sun only 15 degrees up.

-jsw

Reply to
Jim Wilkins

This is the accepted reason why batteries fail:

formatting link

The symptom is increasing intenal resistance that eventually won't let the battery accept charging current at the usual float voltage. Increasing the voltage to 16 - 17V may force enough current in to begin slow recovery. The charger needs to limit the current which may otherwise rise quite high at 15V or above when the battery recovers. Pulse reconditioners automatically apply high enough voltage at limited current, though I'd rather watch the progress with a metered DC supply and adjust the charging current to a few percent of the Amp-hour rating of the battery

I've made neighbors' "dead" batteries last for several more years that way, but they needed annoyingly frequent attention. Since I don't like trickle charger power cords lying around I check and top them off on a schedule.

When old batteries reach that condition the trickle charger voltage doesn't tell you enough. I bought the HF carbon pile tester to measure how much starting current is really available. A cheaper fixed resistance load tester is nearly as good.

-jsw

Reply to
Jim Wilkins

Sadly, Shumacher has done like everyone else and gone to high feature low quality Chinese-built crap.

Reply to
Clare Snyder

I had a Guest charger and it failed in a few years. This is what I am trying to replace right now./

Reply to
Ignoramus15309

Also "smart" chargers, "genius" chargers, etc

Reply to
Ignoramus15309

This is what I will do, I will go with the Pulsetech solar charger.

By the way, Pulsetech's 110v chargers get the same kinds of bad reviews like "failed in a year".

i

Reply to
Ignoramus15309

I've got an old Canadian Tire charger I've had for decades, as well as a Shumaker smart charger I've had for at least 10years. It is a bit overly picky and accuses some good batteries of having a shorted cell when I know from there performance they definitely do not.

I also have a Sears DieHard charger given to me by a friend when he accidently left it in the "boost" mode too long and totally fried the ammeter. I ordered a new one from a charger repair depot for something like $17 and now it is as good as new.

I also have an assortment of 24 and 36 volt chargers floating around. The old ones seam to live forever, while the newer ones have a ways to go - - - -

Reply to
Clare Snyder

Not quite everyone. Ig, maybe look for one of these?

formatting link

4 left in the US.
Reply to
Larry Jaques

An ad on Amazon shows that they build for the US Army. What size do you have? They seem to make $72 2 watter, 5w, 6w, and a $730 25 watter! =:0 Hmm, 24v desulphators, too. (Watch Jim cringe.)

Can you wire it in and just unplug the charger and solar panel whenever? That would be ideal, at least to me. It would also make it usable on multiple vehicles or pieces of equipment.

Suckage.

Reply to
Larry Jaques

Congrats! They sound efficient at that angle.

I bent up some replacement brackets (decided to raise the bottom 3" to get the proper tilt, so had to lengthen the top 6 with no metal stretcher at hand) for the solar panels yesterday and then spent far too long removing the scale from the damned things. Now to clean and cold-galv spray them. It's going to rain here all week, so get ready downstream, guys.

Reply to
Larry Jaques

I lost some batteries to a Guest. Now my onboard charger is a Minn-Kota. 10A on 3 channels. It's worked well for about 6 years now, just replaced the start battery last year.

Reply to
Pete Keillor

I'm impressed with how well they perform on a PWM controller, compared to the maximum 32W I got from an HF "45W" kit.

I couldn't resist $1/Watt with free home delivery. Now I have more solar panels than good places to permanently mount them. Folding plastic sawhorses worked well enough for temporary use.

At noon the wattmeter on the controller input peaked at 180W. It totaled 0.958 KWH from 8AM to 2PM when I stopped because the battery voltage was climbing into the gassing range. In another 1/2 hour they would have been shadowed by a tree anyway.

My Windy Nation P20L PWM controller allows a higher equalizing voltage for 2 hours before limiting at 13.8V (or whatever you program) . For wet cells it goes to 14.6V, too much for indoors.

I will retest with the battery type set to Gel which drops the 2 hour voltage limit to 14.2V where my batteries don't gas as much. A published threshold for concern is 14.3V. It's easy to see if they are or aren't fizzing or bubbling but difficult to measure the rate. At the APC1400's 13.6V default float setting there is virtually no bubbling, but the recharging rate is too low for daily cycling.

-jsw