An oxygen lance will slice through concrete and rebar with no trouble, my brother has done this with reinforced poured concrete. You need full leather protection, it's like standing next to a volcano and anything combustible nearby will catch fire but it will CUT!! Committees of Correspondence Web page:- tinyurl.com/y7th2c

Reply to
Nick Hull

On Tue, 6 Mar 2007 00:49:45 -0800, with neither quill nor qualm, "Roger Shoaf" quickly quoth:

While you have your locksmith cap on, Roger, how do you feel about fiberglass entry (not basement) doors? I've heard that steel doors fall apart in about ten years.

Reply to
Larry Jaques

I really have little comment on fiberglass vs. wood vs. steel for entry doors. The failures on entry doors seem to be related to abuse. If you live in a real cold climate the insulation value might be a big factor.

On wood doors, how much weather and the up keep seem to be a big factor. If you do opt for a wood entry door, get at least a coat of primer on the top and bottom of the end grain to seal it.

I have notices that steel doors will dent so to fix them you have to get out the bondo. Most of the problems with steel doors that I have seen are the industrial ones. When these get banged around a lot the spot welds start to break and then it is down hill. I used to resurrect them buy drilling and installing lots of pop rivets.

Reply to
Roger Shoaf

A few other things:

Check with an architect before you start cutting the wall, have him look at the loading on the wall above and around the door. You may have to reinforce the wall above the door to spread the loads - make a new cast in place header beam, or sandwich two sections of C-channel or heavy wall rectangular tubing on each side with drilled through clamp bolts to reinforce the header externally.

Go look at some commercial 'tip-up slab' buildings where they have cut in a doorway later, they usually have the added-on reinforcement headers over the doors. You can box them in and stucco over them to make it look decorative.

And if you do it, make the hole and the doors as big as the space will allow. If you only do a 60" set, the next piece of gear will need the full 72"...

If this is being used as the emergency exit door from shop space, ignore the looks and put on "crash bars". Shop work means welding, power tools, chemicals, flammable solvents, etc. and you may need to get out of there in a big hurry.

"Remember folks, I'm a trained professional. I know all about the hazards of the work I'm doing. If you see me running and hollering "Get out!" don't stop to think about why - just try and keep up." ;-)

And while we're on the subject, consider adding fire sprinklers and full 5/8" or double 1/2" sheetrock ceiling to the basement, there are

2-Hour standards that can be easily followed. And make sure the basement stairs door is 2-Hour rated.

If the furnace ducts are down there, consider fire dampers at the penetrations. Etc. Bad enough to lose the shop, you might want to keep the house above it.

-->--

Reply to
Bruce L. Bergman

Moreover, if you live in an area with building codes, building inspectors and building permits you are going to need to go talk to the local building inspector about your plan. What you propose involves structural modification to the building. There are very specific and well established engineering requirements for the header members over door openings in order to safely support the building above. Not to imply that your plan is not doable, only that it must be done safely, for your protection and the protection of others that occupy the building now or in the future. If you do live in such an area, failure to comply may subject you to legal penalties including tearout and redo of the work. Incidentally, I found affordable copies of the local building code for sale in the bookstore of a local community college.

David Merrill

Reply to
David Merrill

That's why I am trying to get a steel door frame.

This house cost $180,000 17 years ago. What you are talking about will easily exceed that! We'd have to have new water service put in, too!

Jon

Reply to
Jon Elson

OK, that's the end of the whole plan, then. We're talking $25,000 to install a machine I can buy for $2500. Just no way!

Thanks for keeping me from making a big mistake.

Jon

Reply to
Jon Elson

Seriously, Jon, this is why people rent commercial building space. You could lease the space you need for a year for the cost to safely modify you home.

Paul

Reply to
co_farmer

Reply to
Tom Wait

DARWIN AWARD: Forklift Safety Video Confirmed True by Darwin

March 2000, Australia | It just stands to reason, one should follow safe practices while filming a safety video. But the

52-year-old owner of a machinery and equipment training school violated that rule of common sense while filming a forklift safety demonstration.

With the cameras rolling, he was thrown from the forklift cabin, and crushed. Subsequent investigation fingered the culprits responsible for the fatality: driver error and high speed over varied terrain, coupled with an unused seat belt.

His final safety demonstration was the most convincing of his career.

References:

formatting link

Reply to
Roger Shoaf

Maybe. Another look at it shows only about 8" of concrete above the door. Right above the area where the wider door opening is wanted is a 3-bay casement window. That doesn't allow much roof load to be transferred through the wall in that area, anyway. Maybe that's WHY the door is in that exact spot. I'm thinking that the heavy steel doorframe is all the support needed there. But, I probably don't want to widen the door opening any more than I need, so a 5' door would be better than a 6' door.

Anyway, I have a friend who is a major rehab and renovation contractor coming over to look at the job and give me an estimate. He does this sort of work all the time.

Jon

Reply to
Jon Elson

The door frame is not a structural member - but it does have to be made for use as a set with the doors to keep the fire ratings valid.

You need a header over the door. The existing wall had extra rebar placed in a big hoop around the jamb area when it was poured, and you are going to cut that rebar on one or both sides.

Unless you want to see a six foot section of the house start collapsing into the basement wall over the doorway, you need to replace that header function and the wall strength. It might require vertical steel posts on the inside surface of the wall, from the steel header beam down to the footing, to act as new king studs.

Yeah, right, suuure. Pull my other leg, I'm walking lopsided. ;-)

Not necessarily - the residential sprinklers have improved a LOT, they have some with thermostatic heads that shut-off, and most of them have a smaller orifice and K-Rating than the commercial heads. We had the water main replaced and I bumped it up from 3/4" Gal to 1-1/4" Copper figuring on eventually installing fire sprinklers. Then I was told 1" would have been plenty.

Hell, I'd have already done them, but I haven't found anyplace to get the special orange CPVC piping and the heads. I'd do it all in copper, but that's megabucks.

-->--

Reply to
Bruce L. Bergman

It doesn't have to be the end of the plans, but the job has to be done right - even if you don't go through all the permits and inspections, you have to think it through as if you did.

And a lot of that stuff can be done on the cheap if you don't have to pay for the expensive special equipment.

The bare minimum you need to do is to reinforce the wall over the old door NOW, before you cut the new doorway and remove the existing cast-in-place header beam. Scab a chunk of heavy 2X8 C-channel on each side, drill through the wall and huck-bolt it together with a dozen

1/2" - 3/4" bolts or chunks of threaded rod. Two sections of smaller channel down to the floor on the inside, and a small baseplate sitting on the footing with a few Redhead anchors to make sure it won't move.

Then you cut out the wall, pop in the new door frame, square it up, grout behind the frame, place the threshhold and hang the doors. Trim out door hardware, Finito. And it's not going to cost $25,000.

You're operating a surface mount pick-and-place machine - that means you need a wave solder machine, and that's going to involve a large heat source and will need outside ventilation.

(The concrete cutting guys will need to pop a few more holes in the basement wall for vent intake and exhaust grilles, unless you go up through a bedroom closet or convenient void space to the roof for the exhaust.)

And there are solder resist masking screen printers and other stuff, also working with chemicals and solvents... Flammable Solvents and the furnace and water-heater pilot lights do NOT mix, and the intermittent ignition on the clothes dryer is almost as bad. You will have to wall off the utility areas and provide them with separate outside ventilation.

Basic fireproofing would be 5/8" sheetrock on the ceiling and any exposed wood partition walls. Taped and mudded - paint optional but suggested so it can be cleaned.

-->--

Reply to
Bruce L. Bergman

I'll guesstimate $4K. Let us know how it works out.

Reply to
Gary Brady

would drilling a series of holes and then using feathers and wedges to split it work? Worls super on rocks but I don't know about crete

Reply to
jjbell

I don't think there is a fire rating required for an exterior door.

I looked specifically for a steel joist or rebar, and I absolutely can't find any sign of iron in the wall.

There is a large window directly over the door (both existing, and the proposed wider one). So, the roof load really is not coming down above the door. The contractor who looked it over wants to rip out ALL the concrete above the door, as the height from the top of the doorframe to the footer of the wall above is so thin, 6 - 8". He wants to put 4 2x12's across the top of the doorframe to support the footer. I haven't figured out exactly how he is going to cut the concrete so the ends of these 2x12's will be bearing on the concrete, but I think that must be part of the plan.

Umm, there is NO basement stairs door! The basement stairs are in an open area off the entryway, part of the main hall of the house, and open to the hall by the bedrooms and the living room. It would take MAJOR modification of the entire interior layout to wall off the stairs. I think it would end up looking really HOKEY to do it that way. The main shop room does have a door, and most of it is isolated from the rest of the basement space by a concrete wall, so upgrading that wall and door might not be too tough.

I do have pressurized air over water 5 Gal extinguishers scattered around the place. They are timed-out commercial extinguishers. I have only used one once on a fire in the oven caused by a buildup of turkey grease. It sure worked on that one, but leaving the door closed and turning the heat off probably would have worked, too.

Fire sprinklers? Having a professional fire sprinkler system installed, at least to industrial standards, is REAL expensive.

I haven't seen a residential-grade fire sprinkler installation. I have a partially-built homemade fire alarm/suppression system, but was thinking about a dry pipe water system for the garage. The rest of the house would get a CO2 system. I don't know if I will ever get around to finishing this system.

Jon

Reply to
Jon Elson

There IS NO header beam. This place was built CHEAP! it is a panelized construction house. The pre-made panels are tilted up and nailed together at the site. The central beams are lowered into place and then the roof panels are set on them. I am positive there's no beam over that doorway. There might be some rebar in the very center of the wall that I can't detect with a magnet, but I am positive that I could have detected any sort of steel beam in there.

Nope, no wave solder, but IR reflow. If the boards are small, this doesn't have to be a huge machine. Most commercial setups are for doing 12" square panels, that's why they are so big. I do have a setup for ventilation.

I've already done this. I put a 3" hole through for may paint spray booth/fume hood.

No, the solder paste has very little solvent in it, we won't use masking, and the cleaning can be done in the fume hood.

Jon

Reply to
Jon Elson

Ughhh! That's a lot of money for a door! I hope my guy comes through cheaper than that. I do live in an area where costs are lower (St. Louis, MO).

Jon

Reply to
Jon Elson

Oh, it would work fine, alright. You might not get the break where you want it, because this concrete is full of gemstone-hard jasper. I will be interested to see how a diamond blade cuts that stuff, it just laughs at carbide drill bits. Any, having half a ton of concrete come crashing down on you when it lets go might not be much fun, either.