Help with Car lift problem needed - Long!

OK a bit off topic , but worth a try.
A good friend is trying to start a small garage service going to service and restore old cars.
He picked up a 2500 Kg two poster car lift from the adds and installed it. At the same time the Electric supply company was approached and survey and price sought to supply 3 phase to the garage to deal with the various things he would need.
The price that came back to him was over 9,000 plus VAT. Now whilst that may not seem a lot to some people, it is a bloody great deal when starting and needs a lot of through put before that sort of price can be justified. It seems there is a general problem in the area, of the transformer being under rated for the surrounding houses and farms and the price included part charge for new transformer of larger capacity!
So I though I would let him use my static converter 240 in 415 out at up to 4 HP
It crippled the mains when we tried to start up the 4 HP motor on the ramp even without a car in place.
The mains input dropped to around 180 Volts to the static inverter. Larger cable is going to be fitted to help minimise the volts drop taken from the household supply, but the fears are that even this will not solve the issue.
I have been thinking of reducing the ramp motor from 4 HP at three phase to 2 HP and going to Single phase supply, The start-up currents would be reduced and hopefully less chance of taking the supply down.
Now as it stands the 4 HP motor is 3 phase, runs at 1415 rpm uses pulleys to reduce speed 70 cm and 230 cm so around 1/3 reduction in speed and the lift screws are 5 TPI.
So my basic working out gives me 1415 * 70/230 = 430 rpm screw speed
430 rpm / 5 TPI = 86 Inch lift a minute or around 7 foot lift in a minute which I guess is about right.
Now going down to a 2 HP motor would I need to need to reduce the lift speed by 2 by changing the motor reduction by 6 to 1 instead of the 3 to 1 now in use. Assuming same rpm motor.
Or would I in fact have to go even higher in reduction due to using a single phase motor that has lower starting torque then a 3 phase 2 HP motor.
say to 7:1 reduction from the 3:1 reduction now in use.
Any advice from those in the know is very much appreciated especially from anyone else that has done a similar change.
-- Cheers Adrian.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

I find it hard to believe that a 4hp motor is enough to cripple any electricity supply unless there's something fundamentally wrong with the wiring. 4hp is 3kw which is sod all really. About the same as an immersion heater or a couple of electric fires.
I run a 3 phase mill, lathe and big bench grinder in my garage off a 5hp Transwave converter. The garage is wired as a spur from the house about 30ft away with 5mm round cable (that's 5mm o/d of the plastic sheath so the wire can't be more than 3mm I reckon). That powers 10 flourescent lights plus umpteen single phase sockets and the Transwave is plugged into one of those. I can run every machine simultaneously without any trouble at all. I'm guessing the lathe and mill are about 1.5hp to 2hp each, the motor for the power feed to the mill table maybe another 0.5 and the bench grinder about 1hp or a bit less. There's a compressor in there too (single phase) so with all the lights on and every bit of machinery running there must be about 7 or 8hp (5 to 6kw) at least. The wiring isn't an issue and the converter doesn't even break a sweat. I leave it on setting 3 out of 6 for one motor and position 4 if everything is on.
Now let's look at your lift in power terms. 1hp is 33,000 ft lbs per minute. So that would lift a 3000 lb vehicle about 11 feet in a minute. Even with 50% mechanical efficiency (which I totally doubt or the heat losses into the screws would be huge) you'd lift 5.5ft in a minute. At full weight plus say 500kg for the machine itself you're lifting 3000kg or 6,600 lbs through 7 feet in a minute. That's under 1.5hp of actual work done. A 2 to 3 hp motor ought to breeze through that. Well greased screws ought to be 90% efficient I would guess.
Your problems might be that the converter is a bit small or the start up current on the motor is very high. That could well be the case if there's no clutch and the motor goes directly from off to on and lifting straight away. Far better if the motor spins up and then lift engages once the motor's going. I know my converter doesn't like starting my lathe on very high speed until the motor is warm. I have to turn it up a notch if I want to use 900 rpm or more, especially when it's cold in there like now. As soon as the lathe motor is warm the converter starts to hum so I turn it back down a notch. I'd try a bigger converter or just fit a single phase motor to the lift. If the wiring can't cope with that then how does the guy cook his dinner?
You might try asking in rec.crafts.metalworking too as lots of the guys in there use converters and know more about them than I do.
Dave Baker - Puma Race Engines (www.pumaracing.co.uk) I'm not at all sure why women like men. We're argumentative, childish, unsociable and extremely unappealing naked. I'm quite grateful they do though.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

electricity
is 3kw

of
30ft
wire
those. I

guessing
feed to

less.
and
sweat.
everything is

minute. So

screws
for
no
away.
going.
until the

more,
warm
bigger
can't
though.
A few more points Dave in no special order here.
I would not have expected the start-up to cripple the mains but it did.
Going from the household supply 240 Volts from a dedicated spur in the house with around 40 foot of armoured cable 40 amp rated, what's that about 2.5 to 3.0 mm, no idea at this end.
We used my 4 HP static converter 240 to 415 volt and measured the volts at both the spur from the meter and across the input to the converter. On trying to start up the ramp the volts dropped to 215 volts at the meter and 180 volts at the static inverter.
So two things were apparent to me, yes a large volt drop across his extension wiring but also a large drop across the mains supply. As I said there is an issue with the mains in the area, but there seems to be a reticence to upgrade the supplies to the houses by the supply company although this is being fought.
The Static converter switchable 1.5 2.5 and 4HP by Motorun of Teddington, it works well in my own garage and can drive my own mill quite happily. My own mill is 2HP and is very quickly up to speed, the difference is here that the lift is starting up under load which is not the case with a mill or a lathe.
The motor on the lift at 415 Volts 3 phase is 3.45 KW so OK just over the 4HP but it is probably 4HP output and takes a bit more from the supply. I think it was 4.8 amps per phase on the plate.
If the static converter was 100% efficient then I would see 13.8 Amps drawn from the 240 volt mains supply, expect around 70% so would draw around 20 Amps from 240 Volts single phase. The issue is in trying to start the motor.
When used in my own Garage on the 2 HP mill the converter draws 10 amps, it takes 30 amps surge on start possibly a bit higher but the meter I use is not fast enough. In it works in the same ratio then I would see in excess of 60 amps start-up surge on the 4 HP motor, and the volts drop that happens at this point is enough to drop the voltage so the converter has no chance.
From my college work a screw lift is somewhere around 40% efficient which is crap to say the least, but they are safe. The issue must be in the start-up current through the converter as the motor is trying to drive the lift at start-up.
Back to the main point of why I am asking about a single phase 240 volt 2 HP motor, it would reduce the start up current and running current, have no losses due to a 240 to 415 volt converter.
Just that as before the motor would have to drive the lift under load from start up, and HP may not be an issue but torque may be.
Gas is the answer to the cooking problem with Oil Central heating etc.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Fri, 26 Sep 2003 23:51:28 +0100, "Adrian Hodgson"

I'm normally a strong supporter of simple capacitor static phase converters but not when large starting torque is needed. Capacitor values can be tweaked to give acceptable 3 phase balance between light load and full load but it is impossible for this type of converter to deliver balanced 3 phase into a stalled rotor at startup. To achieve both correct phase angle and phase voltage at start up, the capacitor needs to be fed from a voltage higher than the supply voltage and this is not normally available. With typical static conversion you will be lucky to achieve even half the normal 3 phase peak starting torque.
A large capacitor start single phase motor could solve your problem but, even so, it's a pretty unkind load for a single phase motor and you would need to be careful that frequent starts did not overheat the starting winding.
A simpler and probably cheaper alternative is to add an idler motor preferably as large or larger than the lift motor. Once this motor is up and running it can supply much larger balanced starting power than the parent static converter.
You can get a pretty good idea of whether this is feasible by simply mechanically disconnecting the lift motor which should then start quite happily at no load from your existing converter. Peak starting currents will still be quite high so the voltage drop on your long 240v supply lead will still be significant so it would be better site the converter at the 240v supply end and run 415v thru the long lead.
I'm not sure where your 2HP mill is located but if it is reasonably close you could use this as a temporary idler - it's a bit small but should be man enough to start the lift on fairly light load and give you a good idea of the size of idler motor needed. Large 3phase motors are readily available from scrap dealers. The idling motor puts little dissipative load on the static converter and this can be left at its 4hp setting running the idler motor ready to supply the lift motor when needed. Hope this helps
jim
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Hi Jim; we did try to use an idler motor, only a 3HP one granted, that is the normal situation I use at home on my own 2 HP mill.
So the whole lot was taken with us to the new "Garage" and tried, Idle motor started first no problem then put the 4 HP motor across the output and it stopped the idle motor in its tracks.
We are loosing to many volts across the feed cable at 240 Volts and this will be changed to 6 mm soon.
Another poster has successfully fitted a 2 HP single phase motor and put in an idle shaft to give further reduction. I think that something along these lines will end up being the final solution in the longer term even if the static converter manages to cope.
I have even considered the idea of a hydraulic pump and motor running the pump from a single phase motor and then using a hydraulic motor to turn the screws, but suspect costs of these units are not cheap to obtain.
-- Cheers Adrian.
http://www.aphtrading.co.uk/pages/apage1.htm Weekend Workshop http://www.aphtrading.co.uk/pages/apage2.htm Home made propane Foundry http://www.aphtrading.co.uk/pages/apage3.htm Learning CNC on a Vertical Mill
wrote:

house
to
at
and
said
it
own
the
lathe.
I
drawn
it
excess
happens
chance.
is
motor
HP
from
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Sat, 27 Sep 2003 17:16:30 +0100, "Adrian Hodgson"

You've clearly already done the right things and it's strange that there's been no useful result. I begin to wonder whether the 4HP motor is faulty or whether the mechanics have deteriorated to the point of requiring a higher starting torque than the motor was intended to deliver. Has the hoist been shown to work correctly from a normal 3 phase supply?.
If you're considering fitting a single phase motor the present motor will have to be removed and it will be immediately possible to check both the motor and the mechanics. Without ANY doubt an OK 4HP motor removed from the rig should start and run smoothly from the idler motor setup that you have described. It's a pretty improbable scenario but one open circuit winding or a single missing phase connection would exactly duplicate your problem!
Motor starting torque is proportional to the SQUARE of the supply voltage so, whichever system you finish up with, low voltage drop across the feed cable is pretty important.
Good luck jim
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Thanks Jim;
The 4 HP motor will start without any load on the static converter and although not a true test it shows the motor will start and turn.
From another post there are some things to check on the lift, it could be possible that the mechanics are failing, If I get chance I will try fitting some form of torque driver to see what it needs to turn the screws.
-- Cheers Adrian.

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Adrian, I had the same problem which I solved by exchanging the 3phase motor for a 3HP single from Northern Tools (about 85) and made a reduction arrangement using a large pulley from an old drum washing machine. The car lift was the only item I have been unable to run using the original 3ph motor from single phase (plus capacitors etc). I don't know what the final reduction was but the large pulley is about 10" dia and the pulley on the motor is about 1.5" dia ,the second reduction is via the original motor pulley and the lift pulley. Its probably a bit slow but it happily lifts as it should. I hear that RS are now selling a new inverter that is reasonably priced, I think the stock number is 431-9184.
John
--
Outgoing mail is certified Virus Free.
Checked by AVG anti-virus system (http://www.grisoft.com ).
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

arrangement
the
single
1.5"
Thanks John;
So it must be do able then as you have done it, is the single phase motor you use a cap start and cap run, I believe they are the best for starting under load. Your reduction seems to be around 6.6:1 plus the original belt reduction, in this case that would be just over a ft per minute lift is that what you have.
-- Cheers Adrian.
http://www.aphtrading.co.uk/pages/apage1.htm Weekend Workshop http://www.aphtrading.co.uk/pages/apage2.htm Home made propane Foundry http://www.aphtrading.co.uk/pages/apage3.htm Learning CNC on a Vertical Mill
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

a
but
I
that
The motor I got from Northern Tools was 2 pole cap start cap run and thus runs at nearly 2500 rpm, the motor pulley is about 1.75" driving a 11" pulley, then to a 2.5" and finally the 8" pulley on the lift. The lift is used to keep a 'Stag' belonging to my daughter off its tyres when not being used, She is also afraid of mice getting into it so likes it high off the ground. The important point that I forgot is that there is not enough starting torque to start lifting the car higher once the full weight is on the lift ( its wheels off the ground). Its fine from starting from ground level (no load on the lift), we found this out after raising it up to work on the brakes and then wanting to raise it higher to check the brake pipes. We had to put the wheels back on, lower the car to the ground and back up again. I see from that Machine Mart sell 4 pole motors (1500rpm) that look identical and I guess this would be better but give a slower lift, maybe a higher starting torque as well. The chap who gave me the lift also gave me a large tub of black grease and said take the covers off and give the screw a good smear before use, probably helps. I put an indicator lamp (neon) across the start cap so that when it goes out I know the motor is up to speed.
Hope this is helpful
John
--
Outgoing mail is certified Virus Free.
Checked by AVG anti-virus system (http://www.grisoft.com ).
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Thanks for that John
-- Cheers Adrian.
http://www.aphtrading.co.uk/pages/apage1.htm Weekend Workshop http://www.aphtrading.co.uk/pages/apage2.htm Home made propane Foundry http://www.aphtrading.co.uk/pages/apage3.htm Learning CNC on a Vertical Mill

for
was
lift
priced,
motor
starting
belt
Foundry
Vertical
being
had
out
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Fri, 26 Sep 2003 21:07:07 +0100, "Adrian Hodgson"

I know nothing about car ramps, but a couple of suggestions:-
Why are you planning only 2hp single phase? 3hp single phase motors are readily available, and in some situations will start/run OK via a standard 13A socket. The particular configuration of single phase motor is significant when trying to start under load - I'm no expert here, others can probably advise (eg Capacitor start/induction run, capacitor start/capacitor run etc...)
If you're trying to start a 3-phase motor under load via a converter, you stand a much better chance of success if you start up an idler motor first, preferably a bigger one than the one you want to start, though you may need to play about with the sizes of balancing capacitors if the converter is specifically for 4hp.
Bear in mind that the starting surge current for a 4hp single phase motor would be (IIRC) something over 100A, and probably won't be much different starting a 3-phase motor via a converter. This means that any significant cable runs must be sized accordingly to avoid too much voltage drop during that surge.
What about using, say, a 3hp 3-phase motor via an inverter, you could adjust the pulley sizes as you suggest, but then get back some of the speed loss by overspeeding the motor if the car isn't too heavy? I don't know what a 3hp single to 3-phase inverter would cost, but might be worth investigating, and the soft starting should ease your voltage drop problems.
Cheers Tim
I'd suggest at least a dedicated 30Amp circuit for your 4hp converter . Tim Leech Dutton Dry-Dock
Traditional & Modern canal craft repairs
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
3 phase motor draws at least 2.5 times Full Load Current with a direct on line starter. current is also greater with low power factor ie 0.7 power factor requires 1.42 ties more current as voltage is out of phase with current. A wound motor is an inductor in which current leads voltage and adding a power factor correction capacitor can make a significant difference to starting current and thus cable size. The full load current will be marked on the motor nameplate. Small motors are not very efficent and losses in transmission belts gearboxes etc are very significant and screws are notoriously inefficent so any calculations need to include realistic practical allowances for each item in the drive chain. Remember these factors are multiplied not added. I have no experience of the effect of introducing 3 phase converters into the equation but a friendly competent electrical technician or engineer, given all the relevant detail, would be able to provide the answer very easily.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

2.5 x full load current 4.8 Amps I think it was, is 12 Amps, is that per phase. If so then the input at 415 would be 415 x 12 x (root 3) comes to around 8.6 Kw, translate that to a 240 volt circuit and this gives around 36 Amps, add to this losses in the converter and it is no wonder the mains dips as it does. I think a screw thread is around 40% could be worse not sure.
Thanks for the advice/help, I might even suggest he buys a 3 phase generator and runs that when required. -- Cheers Adrian.
http://www.aphtrading.co.uk/pages/apage1.htm Weekend Workshop http://www.aphtrading.co.uk/pages/apage2.htm Home made propane Foundry http://www.aphtrading.co.uk/pages/apage3.htm Learning CNC on a Vertical Mill
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Adrian
First problem - you have the wrong type of ramp (not a lot of help I know). In single phase locations the one to go for is a hydraulic - either the traditional four post or a newer two post. Bradbury have made these in single phase for many years the only difference to the three phase being a smaller motor which does slow down operation somewhat. The softer start associated with the pump presumably lends this type better to single phase useage. You don't say what make / model of ramp you have, if you post the details I will try to get you more info. I have a client who is a main Toyota dealer who runs the whole workshop on single phase, he has four hydraulic ramps with single phase motors and two three phase tecalamit screw ramps running on a converter using a constantly running ballast motor which looks to be about 3 HP. I have never seen a single phase screw ramp and assume this is due to the high starting currents generated by the high mechanical resistance of the screws and drive chain (I assume yours is a single motor model). I would think that your best solution would be to introduce a lay shaft and subsequent gear reduction between the motor and screw shaft, the result will be a much slower lift but this won't be a problem in a small workshop. Alternatively can you make some sort of clutch arrangement between the motor and screw so you can start the motor before applying the load? You need to check the lifing nut wear on these ramps on a regular basis - if you post details of the model I will let you know how to check them.
Gaspode

and
things
part
to
Larger
issue.
to
to
lift
speed
in
single
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

know).
constantly
currents
(I
solution
the
won't
Ramp is not mine but have been back to friends garage this morning and believe it was a Bradbury, It has a single motor with a 3 belted pulley on top of one shaft gears and chain as you suggested at the bottom of the screw's to the second ramp. I have been told this morning that there was a mod kit years ago that included motor and gearbox to take it to 240 Volts single phase but costs approached that of a modern ramp.
Just measured the starting current at 50 plus Amps, that fact that the mains is dropping to 180 Volts at the starter means it could be higher current.
The main issue is cable size, I think to the garage for this level of current. So the friend is going to up grade to 6 mm csa. run is about 22 metres.
I think after that the best way will be to go for a single phase motor and lay-shaft as you suggest, this has been done by another poster.
OK on the hydraulic style of ramp, I can see would be a benefit, but things are down to cost while the business starts up and the ramps are second hand and in very good mechanical condition. I will be looking out on ebay for any 2 HP motors with 90 degree gearboxes I think.
-- Cheers Adrian.
http://www.aphtrading.co.uk/pages/apage1.htm Weekend Workshop http://www.aphtrading.co.uk/pages/apage2.htm Home made propane Foundry http://www.aphtrading.co.uk/pages/apage3.htm Learning CNC on a Vertical Mill
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Adrian
Just a note of warning, most of the older Bradbury 2 post screw ramps are VERY susceptible to lifting nut wear and you need to check this carefully and regularly. If your ramp has the sheet metal covers at the rear of the posts secured by four push & twist fasteners then you have one of those which wear quickly. You should see two square bronze nuts seperated by about 25 - 30mm when the covers are removed. The original gap between these nuts is often marked on the top nut and you need to renew them if this measurement decreases by 1.5mm. Beware though, the original dimension marked on the nut is not always accurate! Best to lever the nuts apart and measure max and min. dimensions then use 1.5mm difference as a renewal criteria. The good news is that excess wear on these nuts is nearly always caused by lack of lubrication and a few shots of grease into the top nut once a week will ensure that you don't need to renew them frequently, (cut a 50mm hole in the sheet metal covers so you can get a grease gun in without removing them). Also ensure that the safety cable (3mm wire rope passing from one set of nuts to the other) is in good nick and properly adjusted.
Gaspode

a
phase
the
on
two
chain
of
motor
you
a
mains
things
hand
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Adrian,
Going on from what Gaspode has just said - is it at all possible that a set of new lift nuts might solve all your difficulties?
Mike
--
Mike Whittome

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Can but look and see. -- Cheers Adrian.
http://www.aphtrading.co.uk/pages/apage1.htm Weekend Workshop http://www.aphtrading.co.uk/pages/apage2.htm Home made propane Foundry http://www.aphtrading.co.uk/pages/apage3.htm Learning CNC on a Vertical Mill

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Your information is now printed out and will be handed over to Andy the guy with the garage.
Words of warning regards equipment are always appreciated.
-- Cheers Adrian.