Can't find a manual off hand but what are you stuck with, used to fit
these some years ago and may be able to remember settings.
John S.
John,
it`s not for me.It`s a mate down south who has bought a mill with one
on.He`s fitted a reversing switch between the inverter and motor.It
was running ok but stopped with a red flashing led.I`ve never used
inverters but it sticks in my mind that you should not interupt the
wiring between the inverter and the motor but should reverse them via
the control wiring.Is that correct?
Mark.
Mark
According to IMO literature, the VC150 is 1986 vintage and the VCD
series are from 1989. Definitely "old".
I share John's thought. "Oops" may be a little tame.
Yes. Modern VFD units are Started, Stopped and Reversed via the
control wiring and the 3-phase motor must remain "permanently
connected" whilst the unit is powered.
The red flashing LED may just be an overload or overvoltage warning
that can be reset. On the other hand, it may be a cat-as-trophy and
it's telling you, "I'm dead".
Best of luck to your friend.
Andy