| Like the man says...if individual neutral at the neutral bus | is not connected well that neutral as you say will have | current flow available to it as defined by ohms law and the | resistance if the connected 'upstream' load..and it is | dangerous. | | IF the individual neutral is well connected BUT the neutral | back to the transform is not well connected you have the same | problem. | | AND if there is an unbalanced load from from Line 1, 2 or 3 | that flows into the neutral then that neutral will read | *current flow to its ground which as you know will be | dangerous. | | So why doesnt the NEC require the neutrals to be protected? | Because it is not practically possible in these scenario's... | the flows are too variable. and protecting individual | neutrals would be entirely redundant. | | So what does one do? He can choose to not put his tongue | onto the neutral while standing in a puddle of water... that | would work.
Or he can choose to use appliances that don't have a need to have a neutral connected, which allows not running the neutral to the load at all. Loads that have a NEMA 6-XX plug are like that. No reason we can't have more of them.
It might be helpful to have some NEMA 6-15R and 6-20R GFCI receptacles.
| When you figure out how neutrals can be wired to always be in | balance with multi phase feeds, or how to protect users from | current in the neutrals as it varies let the NEC folks know | you could get rich.
A neutral that isn't there ensures the two hots are in balance. People don't get rich by showing the obvious.
| Currently thier practice though is to size the neutrals to the | transformers sufficiently large to carry any possible | imbalance or bolted dead short at full amperage long enough to | trip the over current devices at the transformer or main | breaker panel at the user end... but not to protect the user | from current if he touches the neutral. | | after all, there is no protection provide to the user if he | touches one of the hot lines either... those breakers are | there ONLY to protect the wiring to prevent a fire... its is | totally insufficient to protect from most electrocutions that | occur over a much longer time frame and lower amperage than | the over current device rating. | | Its the GFI that protects users... and those are available on | the line side as you know... your question then is why not on | the neutral?
Yes, that is the question. But keep in mind that GFCI receptacles actually do disconnect the neutral. That is certainly an extra cost, and manufacturers don't tend to add extras they can't use as a marketable advantage (they sure aren't marketing such a feature) so why are they doing this?
| I think that could be done actually...you would put a GFI on | the neutral wired appropriately with a good bond to | ground..have it operate a magnetic contactor in the service | feed, and kill the main feeds if the there was a fault from | the grounded neutral to ground.
The neutral wire already flows theough the current sensor with the hot wires. Just add the ability to disconnect it, and do it in compliance with NEC (ensure that the hots disconnect not later than the neutral).
| Why dont they do that? Because electricity takes the path of | least resistance and if the neutral is already bonded, you | touching it even as it carries current will not take the | entire potential to ground through your body because your body | has more resistance that direct ground only a fraction of the | potential, lets say 2% as a wild guess in most cases, will go | through you.
But they do disconnect the neutral, as I described earlier.
Futher, 20 milliamps of current is not going to damage a 14 AWG wire, but it can kill some humans.
| If the flow through neutral is 40 amps, thats 2 amps... enough | to fry your eyeballs if you touch your tongue to the neutral | while standing in water.
The human won't get the 2 amps. But they can easily get several milliamps, or tens to hundreds if the neutral is open upstream.
| So the lesson then is obvious. Neutrals are hazardous, just | not real hazardous unless one does something stupid.
Or if something breaks, like water getting into an appliance.
Why do we need GFCI in a bathroom? Why not just not do a stupid like dipping the hair dryer in the basin? Well, accidents happen that people have no control over.
Why GFCI in a kitchen? Water related accidents.
Why GFCI in the laundry room? Water related accidents.
Why GFCI in and around a Jacuzzi? Water related accidents.
| the NEC is not intended to protect from that problem as much | as it is to prevent fires believe it or not...the NEC is part | of the fire code...
If that is so, then why does it have all these GFCI requirements?
A great many of the NEC requirements have nothing to do with fire hazards. It's a fire AND SAFETY code.
My intentions is to gather evidence and build arguments to recommend that the NEC be revised in a future edition to require that all circuits in what are considered wet areas, or subject to water in a reasonable distance, be fully GFCI protected regardless of voltage or amperage. And by fully I mean disconnect the neutral in all cases.