nec load analysis question

I am currently studying for the journeyman exam using "Stallcup's Journeyman Electrician's study guide". I am currently in chapter 10: Commercial calculations. Whenever my answer differed from the books I re-read the nec and I would find my error. However now I can't see why my answers are wrong. I have two questions:

1) in a commercial building ( say 120/240 V single phase three wire ) where the service load calculations for the neutral is greater that 200 A shouldn't article 220.61(B)(2) apply?

2) in the book there are examples of the following:

store building: 277/480 V 3 phase

  1. office area is 277 V lighting
  2. warehouse area is 277 V lighting

various 480 V loads

  1. various 120 V lighting loads ( track lighting, outside lighting, show window lighting, etc)
  2. various 120 V receptacle loads ( multioutlet assemblies, continuous and non continuous receptacle loads, etc )

For the neutral, the book adds the VA of 1,2, and 3. It then divides this by

480*sqrt(3). Why didn't they add the load of 4 as well? The examples do not mention any type of transformer and I am at a loss as to why they would include the 120 V lighting but not the 120 V receptacle load in the neutral calculations?

Thank you for your time.

Note: If the book happens to be in error does anyone know where I can find the corrections posted? ( I have searched but found nothing ).

Reply to
jh
Loading thread data ...

James Stallcup will be the first to tell you that no book is without errors.

Reply to
electrician

. . . .

I am only trying to find the correct way to do the calculations. It's more than likely that I am the one in error and I wish to know why.

thank you