I would like to know what the maximum voltage rating of each bus in a single or three phase load center. Can anyone help?
- posted
18 years ago
I would like to know what the maximum voltage rating of each bus in a single or three phase load center. Can anyone help?
bus in a single
Depends on the voltage of the load center...you can buy whatever you need. from 240 vac to 600vac but not usually higher unless its very heavy industrial.
Most homes require 240 single phase (line 1 and Line 2 and a neutral.
most light commercial 240 3 phase some 480vac 3 phase. that adds line 3 to the mix.
Phil Scott
The OEM I used to work for, rated load centers at 300 volts. Panelboards could go up to 600 volts. I do not remember seeing a load center rated for
480 volts. Mostly because the breakers are a lot larger.Your question is a little vague. I do hope your definition and mine of a load center are the same.
Basically NO.
The circuit breakers you would buy in the USA for a load center rated at 120/240V would be rated only to break 120 volts per pole. For 240-volt loads, a 2-pole circuit breaker is used.
Most European circuit breakers I have seen are rated for
300 volts per pole and are larger as a result. Bill Kaszeta Photovoltaic Resources Int'l Tempe Arizona USA snipped-for-privacy@pvri-removethis.biz
If by "foreign" you mean Europe or the countries that follow the European 220-230 V. 50 Hz standard, be aware that the systems are very different as is the equipment that is designed for them.
The North American "Edison" system is typically 120/240 V. 60 Hz single phase with a center tapped neutral at the secondary of the service transformer. This transformer is typically pole or pad mounted.
The advantages of this system are as follows:
In England, for example, you have the "other" system where you have one hot wire running at 230 Volts or so, one neutral, and one ground wire. The panel boxes are designed differently to accommodate this type of configuration with one large hot buss instead of two.
If a typical 120/240 USA cb panel were used on the European system, for example, it would have to be fed by two (in phase hot wires). The neutral buss would carry double the current (instead of just the difference current) All the breakers would have to be rated for 240 and would have to be single pole- non ganged and operable safely on 50 Hz. Not sure that all these parts exist and if it would pass local codes. I don't think so.
Beachcomber
Bill how do you confuse "bus" with "circuit breakers"?!?
Basically NO.
The circuit breakers you would buy in the USA for a load center rated at 120/240V would be rated only to break 120 volts per pole. For 240-volt loads, a 2-pole circuit breaker is used.
Most European circuit breakers I have seen are rated for
300 volts per pole and are larger as a result. Bill Kaszeta Photovoltaic Resources Int'l Tempe Arizona USA snipped-for-privacy@pvri-removethis.bizPolyTech Forum website is not affiliated with any of the manufacturers or service providers discussed here. All logos and trade names are the property of their respective owners.