tricky questions

Hi all, never been in this NG before, but I'm hoping someone would be kind enough to help me out. I am moving into an apartment that has only 2 prong outlets. My questions are.....

1) I can replace the plugs with 3 holed ones, and install ground wires to the radiators, which then lead at some point to the main water pipes, so it'll be grounded. Is there any fire danger associated with this?

2) I have heard of surge protectors that actually have fuses in them which will trip and break the connection once the influx of power gets to high. Do these work at all? Also, in this case, would i simply install the new outlets,m NOT install a ground wire, and let this type of surge protector handle the extra power in case of a spike or surge? Essentially, does this type of surge protector REPLACE the requirement for a ground wire?

All in all, I'm concerned about safety for both myself and my equipment. Any help would be greatly appreciated on this one, thanks all!

Tucker

Reply to
Tucker
Loading thread data ...

You can replace the two prong receptacles with GFCI receptacles. Adding a three prong receptacle with a wire to the radiator may or may not provide you with a safety ground, but that would mean you were altering the wiring in a building you don't own. I don't think you want to go there.

You can't establish "ideal" surge protection. That requires, at a minimum, installing a "whole house" surge protector at the entry panel, and you don't have the right to do that. You can get some protection with point of use surge suppressers, or you could use a UPS to power your equipment.

A surge protector NEVER replaces the requirement for a ground wire at the receptacle. The ground is there for your safety.

Reply to
ehsjr

Thanks for the reply.....in my research I found this page about GFCI receptacles at the plug

formatting link
you scroll to the bottom it says this... ".....If you're in the situation of wanting to install computer equipment on two wire groundless circuits take note:

Adding a GFCI outlet to the circuit makes the circuit safe for you. But it doesn't make it safe for your equipment - you need a ground to make surge suppressors or line filters effective...."

Now I'm more confused....if i simply replace the plugs and dont ground them, i can at least plug in my surge protector, but because it isnt grounded, its useless anyway, to my equipment.....I cant install something ideal at the panel level.....i can wire to the radiator without necessarily telling my landlord, which isnt great either BUT at least I could do that then test it for groundedness, and at least Id know if it was grounded or not...this is becoming quite a headache.

My very first thought was installing the ground wire in the three prong receptacle and connecting it to the inside of the small metal box encasing the entire affair, as I assume that must be grounded.

I hope I dont sound too dull in this matter...lol...its taken me days to even understand some of the basic terms i seem to keep seeing in my research.

Reply to
Tucker

Check the boxes for ground. You could use an ohm meter from the box to the water pipe for example. If you read very low then they are grounded/bonded together. Consult a electrician to be sure. Good grounding is the basis of a good electrical system. 40+ years ago when 2 wire was installed, there were very few if any electronics in the home.

If you really are worried about surges then you will need both a service protector and a point of use protector. The IEEE states that you have to have 2 out of the 3 protection areas to have protection. ( You do not need to worry about the distribution class, that is for the utilities protection, not you.

formatting link
web page has some good reading, look about to get the best deal. Lots of manufactures make this equipment. The circuit breaker protection is way to slow for surge/spikes. Yes they have a CB in the strip but that is for over load. Read the specs on the strip. Your looking for something less than 350v let through. Runs in my mind that mine are like 300v at my computer. The one I installed at the service is like 700v. Do not get sucked into a 100k warranty for any more money. You will never be able to prove what happened. So you will never get the cash. Secondly you can buy a UPS, expensive, if you get one with voltage and surge protection included. The cheapy plug in models will not have voltage/surge protection.

Reply to
SQLit

ok i'm just bored and very sleepy here so I'm going to post some nonsense which you can ignore if you want coz they probably waste your time :)

1) you don't want surges, etc.etc? use a generator which uses an inverter to output the voltage? Cleaner than mains, no surges, lightning etc.etc hehehehe.

2) If you want a good ground, connect to your house's metal water pipes coz that's a very good source to ground to.

3) don't ever ground to gas pipes, they are illegal in most places :)

Reply to
Brian Su

I agree that the first thing you should do is check the boxes for a ground, but not necessarily with an ohmmeter to a water pipe. For a duplex outlet, loosen the screw that holds the cover plate on. Using an AC voltmeter (or simple neon test lamp from a hardware store), you should measure approximately full line voltage (or the lamp will light) between one of the prongs of the plug and the center screw. In some cases the head of the center screw might be plastic or coated with paint. You need to get to the threaded metal part. If you can take the plate off, an alternative ground test point is the screw in either metal ear that holds the receptacle to the box.

If you do get this voltage, you can assume that the box is grounded. Unfortunately, this test doesn't tell you the quality of the ground, more elaborate testing is required for that. A lot of houses built in the 50's and early 60's have grounded boxes, but only two wire ungrounded receptacles. If this is the case for you, the easiest method is to get a 3 wire receptacle to 2 wire adaptor plug with a ground wire (or tab) which connects to the center screw.

This would be easier than rewiring the outlet completely with a 3 prong receptacle. I wouldn't do this unless I owned the premises, could safely shut down the circuit when I was working on it, and knew a little bit about wiring. Do you fit into that category?

If the wiring is really old, you may not have a ground at all. Installing a GFCI - Ground Fault Circuit Interupter will give you a little added bit of safety, but it will not give you a true ground for you electronic devices.

Beachcomber

Reply to
Beachcomber

Grounding to a water pipe to dump electricity is unacceptable and dangerous. NEC discourages it so many obvious reasons. The only ground wire to water (or gas) pipes exists to remove electricity. Never ground to pipes to dump electricity in those pipes.

How clean is that generator (or UPS) output? Typically not cleaner than AC mains. But then, who cares? An appliance already contains internal protection that makes standard electric 'dirt' irrelevant. The dirt is called 'noise' - not a surge.

This UPS, for example, creates 120 VAC by outputting two 200 volt square waves, with an up to 270 volt spike between those square waves. That is called 'clean' inverter power? Yes, unfortunately, too many actually believe myths that a plug-in UPS or generator will always provide cleaner power. Cleanest power typically comes from utility. UPSes can output dirty power (in battery backup mode) because electronic appliances already contain resilient protection; must withstand dirty electricity without damage.

Appliances already include internal protection. In fact, if those UPS or power strip surge protector components were effective, then those $0.10 parts would already be inside that appliance. So where is the advantage of spending so much money on power strip and UPS protection? Its called a myth.

To keep so many ill informed, manufacturer must avoid all mention of important facts such as earth ground. Which kind of transient does that UPS claim to protect from? A type typically not destructive. So instead they forget, even in long pages of specifications (if you can find them), to mention common (longitudinal) and differential (normal) mode transients. They simply collect everything under the simple title of Surge. Therefore the naive will falsely assume all transients are same.

Did the manufacturer lie? Is it a lie to intentionally obscure the facts?

A destructive transient is a typically rare event - occurring about once every 8 years. Those plug-in (power strip and UPS) protectors quietly forget to mention that they are not effective for such transients. Better to not mention earthing to maintain sales.

For those who think a receptacle ground is earth ground; did you consider wire impedance? Take a 50 foot wire from receptacle to breaker box. Probably less than 0.2 ohms resistance. But same wire has maybe 130 ohms impedance from the perspective of a destructive transient. Let's assume a plug-in UPS or power strip surge protector is plugged into that receptacle. A 100 amp transient is connected by that surge protector from black hot wire to receptacle ground wire. Will that 100 amp transient transverse 130 ohms impedance to breaker box? Not likely. Surge protector and adjacent computer are now at something less than 13,000 volts relative to earth ground. Where will the transient go? Through computer and modem to earth ground via phone line. And so that adjacent plug-in protector has contributed to damage of computer modem - even when computer is powered off.

Therein lies the problem. Wire has impedance which is why a receptacle's safety ground is not earth ground. Which is why the effective protector connects a transient less than 10 feet to single point earth ground. Now add other factors that only make a plug-in protector worse. To properly earth a destructive transient, the wire cannot be spliced, no sharp bends, and not bundled with other non-ground wires. First two only increase wire impedance. The latter means that surge protector only induces transients on other wires - because transient is bundled with other wires. Again, more reasons why a plug-in protector is not effective and can even contribute to damage of the adjacent appliances.

Too many reasons all point to the plug-in protector - power strip or UPS - as ineffective against destructive transients. No wonder those components are not already inside the appliance - that already contains effective protection. Ineffective protectors are quickly identified - 1) no dedicated connection to earth ground AND 2) it avoids all mention of earthing. If they discussed earthing, then you might discover wire impedance, problems created by sharp bends and splices, and induced transients. Better to leave customers ignorant (not mention earthing) so that ill informed customers will recommend ineffective, overpriced, and typically undersized plug-in protectors.

Aga> ok i'm just bored and very sleepy here so I'm going to post some

Reply to
w_tom

No surge protector, UPS or line conditioner manufacture will honor their warranty on improperly installed equipment.

I'd bet a pizza those metal boxes are Not grounded, but it's something to hope for.

If you connect to a radiator, you are also connected to the water line. This sounds like a good approach, but there might be some drawbacks that I don't know about (I'm not an electrician). You will need a metal-to-metal connection.

There are adaptors which have a small external terminal for attaching a wire to the ground prong socket. Where the other end of the wire goes could be a radiator or a grounding rod outside.

Most surge supressors will have an LED signaling that the connection is proper. You'll need to check this often, else you could end up unprotected and not realize it.

Michael Whatever it takes.

Reply to
Michael A. Ball

This isn't a very reliable test at all.

Both a neon test light and a voltmeter will give an apparently good reading even with a very high resistance ground path. A 100W incandescent bulb would be a better test, as would the previously mentioned ohmmeter check to the plumbing.

To be useful, you need a solid, low resistance ground connection.

Bob Weiss N2IXK

Reply to
Bob Weiss

Have the superintendent replace them for you.

Reply to
Brian

Yes - it is a headache, but it need not be. GFCI comes first, for your safety, and has nothing to do with surge protection. Next comes a point of use surge protector or a UPS, because that's all your situation allows you to do.

That's it in a nutshell, but details are below if you care to read them.

1) There is a myth that computers MUST be protected from surges. Not true. Computers will work fine with or without surge protection. 2) There is a myth that surge protectors are "effective" where the word "effective" is misunderstood to mean something like "100% safe from damage". Not true. A surge can be powerful enough to overwhelm both whole house and point of use protectors,

Surge protectors are like "crash tested" bumpers on your car or air bags/seatbelts. Cars run just fine without them. PC's run just fine without surge protectors. But a car crash can be violent enough where the safety devices are overwhelmed. Same is true of surge protectors - a large enough surge can overwhelm them. A point of use surge protector, whether grounded or not, provides a little bit of protection - say roughly analogous to a "crash-tested" bumper that will withstand a 5 mph impact. A whole house protector provides much more protection - say roughly analogous to the air bags/seatbelts.

In your case, the GFCI will protect you. It has nothing to do with surge protection.

You cannot install whole house protection in your situation, so that is not an option for you. Any wiring you could do would also be out of the question, as you do not own the building.

A wire to the radiator connects you to the hot water pipes, which may or may not be bonded to the cold water pipes. The effectiveness of that "ground" is questionable, and becomes more dubious, in terms of surge protection, when you add in the impedance of the "add-on" wire and connection. You again have the restriction that you don't own the building.

What does that leave you? You can add a point of use surge suppresser or a UPS. If the receptacle into which they plug is grounded, so much the better, but whether it is or not, that appears to be your only options beyond installing a GFCI. Those devices provide some protection. Could you have a surge that would destroy them and the equipment that plugs into them? Yes. Are they better than nothing? Yes.

The three prong adapter mentioned in the thread is actually a bad idea. If the metal box is in fact grounded even though it has a two-prong receptacle, the adapter still relies on an uncertain mechanical connection to present a ground at its ground hole, and can create the false assumption that a ground is present. Aside from that, if the box is in fact grounded, it would be better to install a 3-prong receptacle than an adapter.

Installing a GFCI will bring a ground to the ground hole on the GFCI **if** the box is grounded and the GFCI is properly installed. Proper installation includes connecting a green or bare wire from the GFCI ground screw to the metal box. The GFCI will still protect you if the metal box is **not** grounded.

Reply to
ehsjr
1) Recommending a ground to water pipe is bad advise for multiple reasons as in previous post. 2) LED signaling does not report anything about proper connection. LEDs may report a missing safety ground or may report a failed surge protector. Neither can report a good condition. LEDs can only report a failure condition. And LED can never indicate the existence of earth ground. No earth ground means no effective protection. And effective protection means no damage from direct lightning strikes - even to the surge protector. 3) A plug-in surge protector adjacent to computer can even complete a destructive circuit through powered off computer. That's right. The surge protector can provide a destructive path from wire with surge to earth ground via computer and computer modem. A circuit that may not exist if the surge protector was not adjacent to computer. In the OP's case, two choices: a) Buy a 'whole house' protector for his landlord to install, or b) plug the largest joule surge protector into the receptacle (of same phase) closest to breaker box.

In b), at least the protector is closer to earth ground and farther from computer - to provide some protection. But if a receptacle does not even have a safety ground, then plug-in protector only makes damage to adjacent computer easier.

Safety ground is not a replacement for earth ground. No earth ground means no effective surge protection. Meanwhile 'whole house' protector is typically properly sized so that surge damage is irrelevant.

In the meantime, what protects that GFCI? Most certainly not a plug-in protector. Just another reason why the surge protector (even if using a plug-in type) must be as close to service entrance, breaker box, and earth ground as is physically possible.

Surge protecti> No surge protector, UPS or line conditioner manufacture will honor

Reply to
w_tom

Just do not merely replace two hole sockets with three hole ones if you cannot ground them. I found sockets like that at my son's home. It was the previous owners low cost electrical upgrade of the home. In a bathroom no less. Two wire romex was used, so there was no possibility of grounding until extra conductors were installed.

Upgrades like that are incredibly dangerous. The provide a false sense of security. It would be better to use GFCIs.

Bill

Reply to
Repeating Rifle

Neither of those suggestions will indicate whether a ground is good or bad. Both a voltmeter and a neon lamp will indicate almost full line voltage with a very high ground resistance, leading to the false conclusion that there is a "good" equipment ground path. The ohmmeter idea is not perfect, but far better than your suggestions, and it doesn't require the op to open a box and expose hazardous voltages.

Ben Miller