Yes. In subpanels neutral and ground are not bonded. There is a link in the box that can be taken out to separate the two.

A ground rod for your sub? Is this in an out-building?

Its *ALWAYS* done in your entrance panel.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Sat, 31 Jul 2010 14:08:20 -0500, " snipped-for-privacy@att.bizzzzzzzzzzzz"

"The Company" grounds "their neutral" AT THE PIG, at the base of THAT POLE! Using a huge sheathed or unsheathed, solid copper wire of like #8 size into a 6' or 8' copper clad steel ground rod. That attachment node is very important!
The COMPANY REQUIRES the CUSTOMER to ground the neutral of "their service", which should be a direct feed from the aforementioned pole, ALWAYS at the entrance panel, directly to Earth or Ufer ground via various accepted methods. Usually a ground rod.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Think "equipotential" grounding.
Tie the earth, the house sits on, and all the equipment shells inside, to the same potential as the grounded neutral entering your house. No differences = no shocks.
in message "The Company" grounds "their neutral" AT THE PIG, at the base of THAT POLE! Using a huge sheathed or unsheathed, solid copper wire of like #8 size into a 6' or 8' copper clad steel ground rod. That attachment node is very important!
The COMPANY REQUIRES the CUSTOMER to ground the neutral of "their service", which should be a direct feed from the aforementioned pole, ALWAYS at the entrance panel, directly to Earth or Ufer ground via various accepted methods. Usually a ground rod.