Upgrading 100A to 200A?

That's the part I hate about working day shift, it's hard to find an electric supply that's open while I'm not at work. Any recommended online electrical suppliers?

RogerN

Reply to
RogerN
Loading thread data ...

You might have to take an afternoon off or do some calling around. Personally I would replace the existing panel with a new larger one, and then if you need a subpanel in the shop for example run a 60A circuit to a small subpanel out there. Depends on the details of your existing installation though.

Reply to
James Sweet

Try Grainger

formatting link

Reply to
bilz2765

I went to the best stocked "Rural King" store I've ever been to today. They had 200A outdoor meter bases with a panel of 8/16 breaker spaces underneath. This seems like what I need, 200A in and feed the house with 100A breaker and feed my add-on panel from another 100A breaker. I think the panel was $110 or so, seemed reasonable. Does that sound like about the best solution?

RogerN

Reply to
RogerN

It sounds like a reasonable way to go. You still need to change the service entrance 3 wire to a 4 wire feeder and separate the ground and neutral in the house.

Reply to
gfretwell

See if your inspector will let you build the new service up to the service point, inspect it, give you an OK for temporary power and have the PoCo switch it over. Be sure to add a GFCI outlet outside next to the new panel. Then you will have temporary power while you are changing over the house panel. It also makes this one trip for the PoCo.. This will at least keep your fridge going and give you some lights with extension cords. If you have planned this all out well and have the parts on hand the switch over could happen fairly fast. The hardest part may be reworking the main to a separate neutral bus if this has had a lot of work done in it over the years. Be sure to buy some extra ground busses. I would bond them all together with 4 ga wire and not depend on the screw to the can although that is legal. Be sure to remove the bonding screw to the neutral bus in your old panel. Put one in your new panel.

Reply to
gfretwell

If I have all the wiring ready for the 200A upgrade, would the power company switch me over, then I just have to run the wire from the existing meter base to the breaker in the new meter base and switch on the power. I'm thinking if I have everything ready I can do my part in less than an hour.

RogerN

Reply to
RogerN

In my neck of the woods you could wire all you want but until you went in and sat down with the Utility Engineering department you would be in the dark, without power, forever. They may want upgrades or changes to the location or whatever. There may be outstanding items held against your service waiting for you to make your move.

The Inspector has no say in it other than it is safe or not and sends the info to the utility. No Engineering OK = nobody will come.

If I have all the wiring ready for the 200A upgrade, would the power company switch me over, then I just have to run the wire from the existing meter base to the breaker in the new meter base and switch on the power. I'm thinking if I have everything ready I can do my part in less than an hour.

RogerN

Reply to
Josepi

If you are on a residential branch, each of the pole transformers (or underground) can only handle a couple or few residences each. You may have to pay for a bigger pole pig installation as well, not just to hook it up.

This sounds also like the ideal drop location would be to the garage and then to the house via whatever means. I do not know what the access levels are for the buildings from the street though.

Reply to
SoothSayer

This can best be answered locally but when I did mine, FPL just swung over the drop to my new panel and they were done. It was a completely new service entrance, mast and the new panel. I did the wiring between the new panel and old after they left and called for my final.

Reply to
gfretwell

Snip

James Your making the same mistake many of us here make in assuming that what is true there is true elsewhere. In many localities underground service conduit is built at the customers expense by there electrical contractor or by themselves if they are doing there own work. The only part the utility then actually does is to pull in the conductors into the meter enclosure and terminate them to the meter socket. The conduit and ground work must be done to utility specification. Schedule eighty conduit is often required. Some utilities require that the back fill be free of stone and that the conduit be bedded in and covered with six inches of gravel dust. As long as the states Public Utilities Regulator has not established state wide rules the utility can require anything they want to see.

-- Tom Horne

Reply to
Tom Horne

Roger You cannot use the wire that runs from your existing meter base as a feeder to a panel that is not the Service Equipment. The existing cable is three wire. You will need to run a four conductor cable or four wires in raceway. One is the newly required Equipment Grounding Conductor (EGC) to which your newly separated equipment grounding conductors in the existing panel will be attached. The second is the neutral conductor and the other two are the two ungrounded current carrying conductors. It is common practice to use four wire service entry cable for this type of feeder. You end up with an EGC that is over sized but over sizing the EGC will not cause any problem nor upset anyone. You may need to buy an accessory lug for your EGC buss bar in order to properly terminate the over sized EGC but it is not an expensive item. Any circuit that originates at a breaker in your service equipment must have a separate EGC and Grounded Current Carrying Conductor (Neutral) if the equipment to be served needs a neutral connection.

-- Tom Horne

Reply to
Tom Horne

/ /Roger /You cannot use the wire that runs from your existing meter base as a /feeder to a panel that is not the Service Equipment. The existing /cable is three wire. You will need to run a four conductor cable or /four wires in raceway. One is the newly required Equipment Grounding /Conductor (EGC) to which your newly separated equipment grounding /conductors in the existing panel will be attached. The second is the /neutral conductor and the other two are the two ungrounded current /carrying conductors. It is common practice to use four wire service /entry cable for this type of feeder. You end up with an EGC that is /over sized but over sizing the EGC will not cause any problem nor /upset anyone. You may need to buy an accessory lug for your EGC buss /bar in order to properly terminate the over sized EGC but it is not an /expensive item. Any circuit that originates at a breaker in your /service equipment must have a separate EGC and Grounded Current /Carrying Conductor (Neutral) if the equipment to be served needs a /neutral connection. /-- /Tom Horne

So if I'm understanding this correctly, ground and neutral are connected at the 200A box and I need to separate the ground and neutral going to the sub panels? I know I have to have a ground rod, would this be connected to the neutral at the 200A box or would they be separate? I'm not sure if the power company grounds their neutral at the pole or it's done at my main panel.

RogerN

Reply to
RogerN

Yes. In subpanels neutral and ground are not bonded. There is a link in the box that can be taken out to separate the two.

A ground rod for your sub? Is this in an out-building?

Its *ALWAYS* done in your entrance panel.

Reply to
krw

"The Company" grounds "their neutral" AT THE PIG, at the base of THAT POLE! Using a huge sheathed or unsheathed, solid copper wire of like #8 size into a 6' or 8' copper clad steel ground rod. That attachment node is very important!

The COMPANY REQUIRES the CUSTOMER to ground the neutral of "their service", which should be a direct feed from the aforementioned pole, ALWAYS at the entrance panel, directly to Earth or Ufer ground via various accepted methods. Usually a ground rod.

Reply to
OutsideObserver

Think "equipotential" grounding.

Tie the earth, the house sits on, and all the equipment shells inside, to the same potential as the grounded neutral entering your house. No differences = no shocks.

"OutsideObserver" wrote in message news: snipped-for-privacy@4ax.com... "The Company" grounds "their neutral" AT THE PIG, at the base of THAT POLE! Using a huge sheathed or unsheathed, solid copper wire of like #8 size into a 6' or 8' copper clad steel ground rod. That attachment node is very important!

The COMPANY REQUIRES the CUSTOMER to ground the neutral of "their service", which should be a direct feed from the aforementioned pole, ALWAYS at the entrance panel, directly to Earth or Ufer ground via various accepted methods. Usually a ground rod.

Reply to
Josepi

You have to provide the power pole for the above ground service in Central Florida, or the conduit if underground. Have you ever set a pole, by hand? Or even better, moved a pole because it was a foot too far from a building? :)

Reply to
Michael A. Terrell

In one of my church's summer camps the power company had to set a pole by hand. They brought in a couple of retired outside wiremen to teach the younger troops how to do it. The use of pole carrying tongs, Peavey hooks, Pike poles, and other apparently hand forged antiques was very impressive. The reason that it was not done with heavy machinery was that it was in a marshy area that had a large colony of endangered flowers and habitat for an endangered animal.

-- Tom Horne

Reply to
Tom Horne

The only tools we used were a shovel and a level. We dug the hole to the depth we needed, then cut into the wall at a 45 degree angle, about half way down. Then my dad and I shoved it, till it was over the open hole. Some heavy lifting, and the end started down the angled part. When it was upright far enough, it dropped to the bottom of the hole. Then we started back filling the hole, while rocking the pole to compact the soil. The last part was shoveled in, then the shovel handle was used to tamp that dirt into place. Then he said that there was no way to remove the old ground rod so I hooked a chain to the clamp, and to the back of my Ranger pickup. It pulled right out. :)

Reply to
Michael A. Terrell

I remember a summer Job involving building a line. Only where the soil didn't allow the use of a mechanical drill, did we have to dig by hand-using a "spoon" and "crowbar" to dig the hole and then using pike poles to heave the pole into the hole- no 45 degree slant involved. Where a machine could dig the hole it could also drop the pole into the hole. In any case, as long as the pole was in the hole, the foreman had the job of setting the line and the crew used a peavey to turn the pole as desired and pikes to set it vertical. Once that was done , the pikes could be grounded and the crew split between shovellers and tampers (yes, we had tamping bars rather than shovel ends so tamping could start as soon as some soil was added to the hole so this eliminated rocking the pole. (Mind you- usually there were 4 or 5 people on the pikes) ) If a tamper got caught by too much backfill - that person bought beer for the crew that night. This was in the early 50's and we worked hard for under a dollar per hour. This crew's record was 66 poles set in one working day. A problem in swampy soil was that of bell bottomed holes- some of which seemed insatiable gobblers of fill. Overall a great incentive to get a "higher(sic) education"

I remember a summer Job involving building a line. Only where the soil didn't allow the use of a mechanical drill, did we have to dig by hand-using a "spoon" and "crowbar" to dig the hole and then using pike poles to heave the pole into the hole- no 45 degree slant involved. Where a machine could dig the hole it could also drop the pole into the hole. In any case, as long as the pole was in the hole, the foreman had the job of setting the line and the crew used a peavey to turn the pole as desired and pikes to set it vertical. Once that was done , the pikes could be grounded and the crew split between shovellers and tampers (yes, we had tamping bars rather than shovel ends so tamping could start as soon as some soil was added to the hole so this eliminated rocking the pole. (Mind you- usually there were 4 or 5 people on the pikes) ) If a tamper got caught by too much backfill - that person bought beer for the crew that night. This was in the early 50's and we worked hard for under a dollar per hour. This crew's record was 66 poles set in one working day. A problem in swampy soil was that of bell bottomed holes- some of which seemed insatiable gobblers of fill. Overall a great incentive to get a "higher(sic) education"

Reply to