| If the MV neutral is the only MV ground link, then downstream of the break, | the MV system is floating unless grounded at that point so that the return | will be in the ground or any parallel wires going back to the source | neutral/ground. The current will be small compared to unbalance currents in | the LV neutral. It should not be a big deal. If the MV neutral is floating, | then there is the problem of an induced voltage in this neutral with respect | to ground or the LV neutral. Is this safer? Not really. Upstream of the | break, I assume that there may be other customers where the MV neutral is | also connected to ground so normal conditions occur. If an MV neutral breaks | and is anywhere near people, I would prefer that it is multigrounded. | How do you get proper grounding of both the MV and LV neutrals? | Running two parallel multigrounded wires gains only from having two wires in | parallel. Having both MV and LV grounded at the source and nowhere else is | not desirable and having the MV multigrounded and the LV grounded at only | one point (the source) presents its own set of problems. Multigrounded LV | and singly grounded MV also presents problems.
I'm assuming the MV neutral is grounded at many places along the way, as well as at the transformer that steps down to LV. The more such grounds there are, the less the problem will be on the LV service drop as that helps divide up the return voltage.
If there are no such grounds, that's certainly a very different case. But would there still be a crossover connection between MV neutral and LV neutral?
But there are wires on the MV circuit that are not grounded; the up to three line wires are not grounded. And they have some voltage.
I don't have a problem with there being a multigrounded neutral. What I have a problem with is connecting the LV circuit to it. If there is not way to make the MV distribution different to where I would not have this LV to MV connection issue, then what I need to do is isolate the LV from the MV more effectively.
|> Maybe what I might do is have the utility land the service drop to the |> first of three wooden poles. After the meter and disconnect, I'll take |> the 240 volts over to the next pole and energize an ungrounded polepig |> in reverse. Then take the MV from that over to the third pole with a |> second polepig taking it back down to 120/240. Crazy idea? Sure. You |> have a better one? | -------- | Yes, why bother?- effort spent on good grounding and maintenance will be | better.
And how does that prevent/eliminate any possible MV currents coming over?
|> You might not share my motivation to be doing this. But I think I have |> made it clear what I want to do. I'm still open to other technical ideas |> on how to do this. But I'm not really open to debating why. So this is |> the last of trying to explain that. | ------- | I still will rest my case- why bother?- The only reasonable "why" is that | there is redundancy in the grounding system if LV and MV neutrals are both | grounded as often as reasonable and effectively are in parallel. No matter | how you go about it, there can be found situations which can be used as | counter arguments. These arguments were around and settled before you and I | were born ('31 in my case).
If they were settled, there sure isn't a solution being deployed. This problem persists and is observable by the dairy industry, for example. If by "settled" you mean "dismissed as a non-problem", then that is not at all settled".
Maybe this is why Amish milk tastes better, even if you pasteurize it
So, anyway, you don't share my motivation and you don't have a solution.