I need to know the proper aluminum wire size to hook up a 27.5 KW generator. The run of the wire will be approximately 115 feet.
Thank you
I need to know the proper aluminum wire size to hook up a 27.5 KW generator. The run of the wire will be approximately 115 feet.
Thank you
try this site,
You didn't say the voltage and phase but if this is 240 single phase that is about 115a. Minimum in the 75 column would be 1/0al but you will probably want 2/0 or 3/0 for voltage drop reasons.
I appreciate the link, but.... Determining wire size generally requires the solution to TWO equations. The Voltage Drop equation is one which limits the losses in the wire. The other solution iso the heat transfer equation which limits the temperature of the wire. This second equation is generally solved by using Tables, Table 310.16 of the NEC being the one most widely used. Therefore, voltage drop alone is not sufficient for determining the correct wire size.
The generator is a three wire single phase 120/240. Two hots and a 'return'
thanking everyone for their help
120v per hot
There was not enough information to do the calculations correctly so I thought I would put the guy on to a path that would be self enlighting.