expanation of 3 phaze power

Can somone post a link to a description of how 3 phaze power works. My brother is looking at buying a Felder combination woodworking machine
with 3 4kw motors in 3 phaze and while we both worked for an electrician as kids we never worked with 3 phaze. If he buys it he's planing on buying a converter as he can't get 3 phaze power at his place. He worked in a shop with converter while in college but has never had to set one up. Thanks Karl
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Hi Karl
Try searching for Three Phase Power in Wikipedia.
Bob Swinney (of this group) can tell you how Rotary Converters work if you want to make your own 3 phase from a single phase source.
Jerry
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Will do. Didn't think of that. I asked my brother if he was going to make a converter but he's looking at buying an electronic one. Thanks Karl
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Hi Karl
I support your brother's decission to buy an "electronic one". I suspect it will be a device that starts the 3 phase motor spinning then allows the motor to run on single phase. A 3 phase motor will supply nearly full power when running on single phase, but it will stall much more easily than when it has 3 phase power. If all 3 of your 4 KW motors are spinning at the same time from the same power connection, you will have made your own 3 phase power within the unit's wiring anyway.
Jerry
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Jerry wrote:

I see a slight contradiction in this statement.

And you only have to feed in 1/3 of the wattage. Quick, quick! To the patent-office! :-)
Nick
--
The lowcost-DRO:
<http://www.yadro.de>
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Hi Nick
I recognize that you are a smart guy, so there is a misunderstanding. I say that a 3 phase motor can deliver nearly its full name plate rated power to the load when it is running from a single phase power source. I suspect that you agree. I say that a 3 phase motor will stall more easily when running from a single phase power source than when running from a 3 phase power source. You certainly agree with that.
I considered that when one of the three motors is spinning, it becomes a "rotary converter" for the other motors. My thought was (is) when the system of 3 motors are included in one machine, not all will be loaded simultaneously. That assumption could easily be an error.
I am open to learn. Where is my thinking wrong?
Jerry
Jerry
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

the unloaded RPC motor acts as an LC network and creates the needed phase shift.
the RPC motor is not being used as it was originally intended as a LOAD its being used to pass power through it and apply a phase shift rather than to transform the power into mechanical energy.
The rpc will not generate the third leg properly until it is spinning at speed. once it is spinning at speed it will take a tiny amount of power to keep it spinning at speed but that will be insignificant compared to the load
the 3 motors in the machine are running as loads and are taking power out of the system rather than generating extra power on the third leg. and should be treated as loads that remove power
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Hi Brent
It isnt clear that the OP is considering a Rotary phase converter. A converter is often a capacitor that is temporarily connected to the 'not connected leg' of the 3 phase motor. Once the 3 phase motor is spinning, it will run well with single phase input power while the third leg of the motor disconnected.
3 phase motors run well when fed single phase, once they have "spun up" to near their synchronous speed. A 3 phase motor running from single phase will delliver very nearly its name plate reted power to a load.
Once one 3 phase motor is spinning, any additional motors connected in parallel with them will see the "spun up" motor as its being a Rotary phase converter with single phase power applied to their input.
Bob Swinney wrote a good article describing most of the theoritical aspects of Rotary Converters.
Jerry
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
    [ ... ]

    [ ... ]

    What he is planning to use, then, is the equivalent of a capacitor temporarily connected to to the "not connected" leg of the motor. This gets it spinning in the right direction and then disconnects.
    The sure indicator here is the range of horsepowers (instead of "up to X horsepower). This is because the capacitor needs to be sized to the horsepower of the motor which it is being used with. Too large a motor or too small a motor will not start properly. (Of course, the word "Static" in the name is another clue.
    You can perhaps get nearly full horsepower from the motor with this, but at the cost of running one winding at a much higher current than it was designed for. It would be more likely to burn out if run at this level for quite a while, though you can get away with it for short spurts.
    And this is not what *I* would call an "electronic converter".
    If you want to do it right, the better way to go (other than making a rotary converter) is to get a VFD (Variable Frequency Drive), a truly electronic device which converts the incoming power (single phase or three phase) to a high DC voltage, and then converts that to true three phase -- with the added boon of generating the three phase at a frequency of your choice, so you can run the motor significantly slower or significantly faster.
    When running significantly slower (say about 25% of full speed or so) you do have the problem that the internal fan in the motor won't keep it cool enough, but if you wish to run it at such slow speeds for long periods, you can add an external fan to keep it cool enough. Just mount it to blow into one end (in the same direction that the internal fan blows) and you are fine.
    I forget what kind of machine tool this was to be used with, but quite a few benefit from the ability to tune the speed to the task at hand. For example metal lathes can produce variations in finish quality as you face from outside towards center or vice versa. The reason for this is that at certain surface speeds you get buildup of metal on the cutting tool which will eventually break clear and give good finish for a short while before building up again. If you can turn the spindle speed up as you face in towards the center, or down as you face out from the center to the outside, you can tune away from the speeds which give the problem. And this is something which you can't do with a step pulley, since stopping to change belt steps would change the finish at the point of the stop. (Though if you have a variable speed pulley, you can do quite well with this.)
    I personally would not use a "Static" phase converter, and would choose either a rotary converter (home shop made) or a VFD (commercially made). Since I have three VFDs and no Static phase converters, you can see that I live by that.
    Enjoy,         DoN.
--
Email: < snipped-for-privacy@d-and-d.com> | Voice (all times): (703) 938-4564
(too) near Washington D.C. | http://www.d-and-d.com/dnichols/DoN.html
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
| Voice (all times): (703) 938-4564

Hi Don
Why do you write that a static converter with more capacity will have difficulty starting a smaller motor? I refer to your statement -

Jerry
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

    [ ... ]

    [ ... ]

    Because the phase shift from the capacitor is a function of the motor horsepower (and related inductance) the capacitance, and the frequency. Since the frequency is fixed at either 60 Hz (here) or 50 Hz (UK) we have the motor inductance/horsepower and the capacitance. Too small a capacitor will not produce enough phase shift to get the motor started quickly enough to avoid blowing the capacitor, and too large a capacitor will generate too much phase shift, again resulting in very slow motor starting and likely failure.
    Note that the static converter was spec'd for a range of horsepower (in the part of the article now trimmed), not "up to such-and-so horsepower".
    This is a common limitation for a static converter -- at least of the capacitor and relay style. So -- if the machine tool has three motors -- one 4 HP, one 2 HP and one 1/2 HP (say for perhaps spindle, feed, and coolant pump), then while it may start the 4HP motor nicely, it will fail to start the 1/2 HP coolant pump if that is needed first. Obviously (in spite of what Nick thinks) once you have the spindle motor running, it can start the others, but if you need the smallest to start first (say it also pumps lubricant around to the bearings before you start moving things) you may have problems. For this, really, an external rotary converter would be a better bet. Let the static converter start the rotary, and it can start all of the load motors with no problems.
    Obviously -- if it is a homebuilt static converter, or if the owner is competent to open it up and replace the capacitor with the appropriate size for the other motor, then this can be overcome.
    Also -- if he is not careful to wire it so the real 240 VAC comes in to the terminals which feed the control circuitry, he may not be able to get the spindle motor to start with the static converter alone.
    Enjoy,         DoN.
--
Email: < snipped-for-privacy@d-and-d.com> | Voice (all times): (703) 938-4564
(too) near Washington D.C. | http://www.d-and-d.com/dnichols/DoN.html
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
| Voice (all times): (703) 938-4564

Hi Don
I have fallen short on my study in this 3 phase stuff. When I was doing the testing with my litle dyno on 3 phase motors, I recognized that the bigger the capacitor I used to spin up even the fractional HP 3 phase motors, the quicker the motors spun up. I suspect I never approached the "too much" capacity. At one time I thought the static converter was a partially useful method of running 3 phase machines at home, on single phase. But, the more I learn about them, the more I recognize that they are an excellant device for most home users for running 3 phase machines. The only literature I have read related to static converters ghas been sales brochures. I am a little sceptical of what is written in those sales papers.
I accumulated some data while dyno testing the effects of 3 phase motors and rotary convertyers. I saw that a very much smaller idler could spin up a larger tool motor when the tool motor is spun up while very lightly loaded. But, as you would expect, the little idler helps little or nothing to the tool motor's ability to deliver power.
Where can a guy find some good tech info on static converter design?
Thanks for the "heads up" on excess capacity for spinning the 3 phase motor.
Jerry
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

    [ ... ]

    [ ... ]

    [ ... ]

    You may not have even reached the level of "right value". :-) You were perhaps using oil-filled AC capacitors, instead of the electrolytic motor starting capacitors which are more common in motor applications -- because they are smaller and they cost a lot less.
    Oil-filled AC capacitors are a lot more tolerant of long start times.

    That depends. If you need to "plug reverse" a motor -- say do it to a lathe spindle motor when you are threading up to a shoulder to avoid a crash -- a static converter is useless.
    The static converter (one version) is something like this (view with a fixed pitch font such as Courier to avoid distortion of the drawing):
(1)--------+ +----------------------------------(A) | | +--> | +----------+ | | | I R | | | +----------+ | | o o | | (2)-------------------+-----------------------------(B) | | C1 +---|(------------------(C)
The block marked "I R" is a current sensing relay. When the motor is drawing the high current when it is switched onto power with no ability to start, it is sufficient current to close the contacts. One contact connects to either (1) or (2) of the 240 VAC input lines (neutral is ignored, so I did not draw it here). The capacitor (C1) applies phase-shifted current to the motor terminal (C).
    Once the motor spins up to perhaps half of its normal speed, the relay is no longer seeing enough current, and thus the contacts open, leaving terminal (C) on the motor totally disconnected.
    That's OK for most things, because the single-phase power applied between (A) and (B) is sufficient to keep the motor spinning at normal speed -- though if it is loaded to full horsepower rating, the current through the single winding will be higher than it was designed for, and the winding will overheat and eventually burn out if you are running it near its load rating for a long time.
    However -- if you want to reverse the motor quickly, you are out of luck. Normally, a three-phase motor is reversed by interchanging any two of the three power leads. At that point, the three-phase power will be trying to turn it the other way and it will reverse *quickly* (and with a lot of current for a very short period). But, remember that the (C) feed to the motor goes to nothing as long as the motor is not drawing a lot of power. And once the motor is spinning, it doesn't care which way it is going when fed by single phase.
    So -- it won't reverse until the relay contacts close, and that will require a lot of current, such as you get from a stalled motor. But since it is spinning at normal speed, you won't get that current and the relay will keep the connection to the (C) terminal open, so the motor will keep running in the original direction, and your lathe tool will crash into the shoulder.
    A VFD does not want switches between the VFD and the motor, so you have to ask it to reverse the motor, and that will require it to slow the motor down and then speed it up in the other direction. Not quite a fast as just reversing two leads on a real three phase, but usually quick enough.
    A rotary converter (which can be thought of as a static converter starting a motor (called the idler motor) which then acts to generate the third phase) can handle plug reversing -- as long as the idler motor is enough larger than the load motor. I have heard of attempts to plug reverse with too small an idler motor resulting in reversing the idler motor instead of the load motor. Plan on at least 1.5 time the load motor rating for the idler motor -- or two times is even better.

    Good!
    Not from the makers -- they don't want you to see how simple what they are selling you is, and how little it would cost for you to make your own.
BTW    That current relay is another reason for the minimum horsepower.     If the motor is two small, even with it stalled it won't draw     enough current to draw in the relay and engage the start     capacitor.
    Some may be built using voltage sensing relays, waiting for enough voltage to come back from terminal C instead of current sensing relays -- or perhaps even a timer which just assumes that the motor must have started by now and thus disengages the capacitor. All of this is doing just what the centrifugal switch in a motor built for single phase does.
    If you want to study circuits which do what a static converter does -- look at the home-brew plans for rotary converters -- they often use the "static converter" design to start the idler.
    And good rotary converter designs add oil-filled AC capacitors to tune the output of the rotary converter for better balanced three phase. You need to adjust the total capacitance according to the idler motor, and ideally with the load motor connected too, so you are tuning for best balance when under load.
    Now -- I have seen mention of static converters which use a tapped inductor to accomplish the phase shift instead of a capacitor. That might avoid the need to switch out the third phase as soon as the motor is spun up -- but it certainly increases the cost of construction. Basically -- if you have difficulty lifing a static converter, it is probably an inductor-based one, and may be better.
    But personally, I like the VFD for most home shop conversion, since it lets you tune the speed. The only place where I would consider the rotary converter better is when you have a lot of three phase motors on a single machine (which I believe is what started this). And of course real three phase from the power company is even better -- if you can get it.

    You're welcome.
    Good Luck,         DoN.
--
Email: < snipped-for-privacy@d-and-d.com> | Voice (all times): (703) 938-4564
(too) near Washington D.C. | http://www.d-and-d.com/dnichols/DoN.html
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
| Voice (all times): (703) 938-4564

Hi Don
You have alot of information on Converters. I began a study a few years ago by building a dyno and using Excel to make charts of HP while running 3 phase motors from a single phase line. Don Foreman taught me lots and lots about all the stuff I built and tested. he is world class instructor. I have disassembled the dyno but keep the set of four 200 mic electrolytics in parallel that I can apply to the unfed motor lead thru a solid state switch. I use the capacitors to spin up 3 phase motors here at home. I wont be surprised if i sometime fail to spin up a small 3 phase motor due to the excess capacity. I have several VFDs in systems I work on. So, I do like them and have used alot for stuff I've built. I even repaired a 120 KW solid state converter last week. It is fixed frequency at 60 Hz in and 400 Hz out. The problem is 'I dont know what I did to make it work'. Thats not too satisfying, but the unit did get shipped after I disassembled part of it and then put it back together. But, the more I learn about "Static Converters", the more I respect their value to home use where space and budget is a factor.
Jerry
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

    [ ... ]

    [ ... ]

    Hmm ... that is enough to handle rather large horsepower motors.

    An interesting device -- and something which I would like to have -- except much smaller -- to run an old gyrocompass and an artificial horizon which want 115 VAC 400 Hz. Probably on the order of 20 W each.

    I'm not too sure about the budget matter. The price from vendors seems to be not too different from that for a VFD from eBay or one of the good dealers -- at least until you get into seriously high horsepower ratings.
    Enjoy,         DoN.
--
Email: < snipped-for-privacy@d-and-d.com> | Voice (all times): (703) 938-4564
(too) near Washington D.C. | http://www.d-and-d.com/dnichols/DoN.html
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
wrote:

I agree, Jerry; static converters get an undeserved bad rap. I have three machines (mill, lathe, surface grinder) that benefit from VFDs, but my vertical band saw, belt sander, and one bench grinder run happily on a static converter. (And, yes, turning one of those machines on will help start a motor that the converter would otherwise not start.)
I do have a large rotary converter, and can easily switch between the static and rotary, but rarely find it necessary to run the (noisy) rotary.

And yet it works. I ran a Bridgeport for many years on a static converter and regularly plug reversed when power tapping. A friend who has a commercial shop without access to 3-phase runs 4 BPs on static converters, and has for as long as I can remember. Plug reversing isn't a problem for him, either.
Here's what Phase-A-Matic has to say: ********************************************** Next, you must determine whether to use a Regular or Heavy Duty Converter. Keep in mind you can always use a Heavy Duty Converter in place of a Regular Duty model. However, there are some applications for which you should always recommend Heavy Duty Converters. They are:
1. Frequent starting or instant reversing (more than once a minute). 2. Unattended equipment, such as air compressors. 3. Long, heavy starting cycles, such as lathes without a clutch, flywheel driven equipment, etc. 4. If jogging is required. 5. If there is a chance of the motor being stalled during use (woodworking equipment, etc.)
********************************************
--
Ned Simmons

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Capacitors cant store enuf energy to be used to convert single phase
to 3 phase , you must use rotary machines to store the energy .
Its real simple , a motor is powered to store energy , which it delivers
to a phase wire on a 3 phase motor , you simply control the energy
applied to the single phase so it can deliver this energy , but delayed
to the 3 phase motor .
The more energy needed , the larger the rotating mass of the single phase
motor .
motors and transformers can be modeled as a magnetizing inductance in parallel
with a leakage induct'+resistive load .
At no load , all current flows thru magnetizing induct' .... bad P.F. ,
so you pay more to the electric company .
But as the current flows to the load , which is series to the leakage induct'
the P.F. improves to 85% ( cause the load is resistive , not induct' as the L-induct is ).
The stored energy is in the Leakage induct' , and it is effecient .
But it needs a large heavy rotor to deliver that energy to a 2nd motor .
It also needs a small air gap , to reduce the reluctance of the path from
stators to the rotor .
we need to move above 400 hz , to get higher power , but that means diameter
of motor also increases .
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Hi Werty
I find no fault in what you write here. But, there is a situation where 3 phase motors can be run nicely when connected to single phase. And, it requires only that a capacitor be temporily connected from one of the single phase lines to the "not connected" third wire from the 3 phase motor. That temporary connection of the capacitor gets the 3 phase motor spinning so it can then deliver appreciable power. The capacitor doesnt need to store power. It is quickly "bumped across" the two terminals of the motor wires. The major benefit from having a VFD or a Rotary Converter would be to get the tool motor to delive close to its name plate rated power to a load for extended times.
Jerry
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Thanks everybody. This should give him the info he needs to decide what to do. Karl