I have a new installation, consisting of an AutomationDirect DL450 and one of their "Ez-Touch" panels. Despite being grounded to hell and gone and hooked up '422 with proper terminations and expensive belden cable, I get intermittent but frequent "No Communication with PLC" problems. Not causing a particular problem, but puts a cosmetic dent in an otherwise perfect machine. The problem occurs whether the machine is running or just sitting there.
Power is +24.2v from a 150W supply, and the comm cable run is about 6 feet. AD support says "noise". S*it. What "noise"? Upsetting an RS422 whilst switching nothing?
Baud is 9600 N-8-1. FWIW It did this hooked up RS-232, which is why I went to '422. The PLC and touch panel are in two seperate cabinets. All cabinets tie back to a groungd busbar connected to the 480v ground. The control power transformer is grounded ("Neutral") side.
Anyone want to take a crack at it?