We have an MCC that we are having problems with a number of relay coils failing - eight failures in the last week. The relays that are failing are the 4 Pole 3 Amp 14 Pin plug in relays. Coil voltages of the failing relays are 110 VAC and 24 VDC. The coils are showing no signs of overheating, they are going open circuit. The setup, the 110 VAC relays are MCC control circuits. These are supplied from a control circuit transformer 415V/110VAC, the transformer is common to all the MCC cubicles. The 24 VDC relays are interface relays for a PLC. The 24 VDC is supplied from a 240VAC/24VDC power supply. The 240 VAC is from 1 phase of the same 415 V system and neutral. I have tested the voltages and found to be correct, my assumption is that whatever is causing the relays to fail is common to both the 110 VAC control supply and the 24 VDC supply. The only item I can think of that is common to all is the automatic power factor correction panel. This switches capacitors on/off to correct power factor, and is connected to the MCC busbars. The power factor panel does not seem to be working correctly, and I did notice a leading power factor at very low loads. I have since switched off the pf panel for a week's trial. Anyone else experienced a problem like this, or can offer any advice on what may cause this type of problem. Also, what effect would a leading pf have on these small relay coils? I may be barking up the wrong tree here, but cant see what else could be causing this type of fault. Appreciate any advice. TIA