I'm trying to wire 3-way switches on either side of a ceiling lamp. The power initiates at one of the switches. I've got the wiring scheme figured out but I have a problem.
Prior to installing the lamp fixture I decided to check the switch functions (at the ceiling lamp) with this simple $ 1.00 neon tester. With the switch on the neon tester gives full brightness, with switch off it still lights up, but very dim.
Disconnected all of the wires everywhere and come up with the following:
At 3-way switch I have a ground, black, red & white wire (only the ground and the white have been connected to others). I'll call the black and red wire "shuttle wires". These same wires are dangling, unconnected, at the ceiling. Nothing is hooked up. Ground to power is 118.5v. White to power is 118.5v. Ground to white is 0v. IF I connect the "shuttle" black to power (as if the switch would also do) I get 30± volts on the totally disconnected (both ends) red "shuttle" wire. An ohm reading between the unconnected "shuttle" wires reads open (my ohm meter only goes to 20 megohms).
Is the only answer that somewhere in the wall the black and red "shuttle" wires have slightly shorted, giving me 30± volts? These are brand new walls in finished space and I'd hate to tear out the sheetrock and wires. Note that all of the above is with the 3-way switches in my pockets, i.e., totally out of the equation.
BTW, if I ignore all of the above, I get 60±volts at the ceiling in the switch off position. Turning either switch to the on position gives me my
118.5v. The 60 volts is not enough to light a bulb, so, I am tempted to ignore it. Is this dangerous?
All advice greatly appreciated.
Ivan Vegvary
Didn't find your answer? Ask the community — no account required.
R
Richard Ferguson
The voltages that you are seeing are probably caused by capacitive coupling in the switches or wiring. In addition to the normal DC and AC connectivity of a switch in the closed position, there is some AC coupling in a switch across the open terminals, and AC coupling between wires in a bundle. A neon test light probably draws very little current, so it may be lighting due to this capacitive coupling. In other words, it may be that nothing is wrong.
The voltages you are reading with a voltmeter are even less surprising, even though the switches were in your pocket. Most modern voltmeters are very high impedence, and find all kinds of voltages that have virtually no current or power associated with them, even when the probes are just lying around, touching nothing. The test lights are somewhat lower impedence, so usually are more helpful. The capacitive coupling is probably occuring from one wire to the other. These wires are probably in the same bundle, so one wire capacitively couples a little voltage to the other.
Hook up the light the way that you think that it should be hooked up, screw in a light bulb, and try the switches. If the light works the way you expect it to, forget it.
If you want to check for wires shorting in the wall, do it this way: Disconnect all wires in the bundle at both ends. Use an ohmmeter to check the wires for DC conductivity. They should all be open (very high resistance, probably relative to each other. If the readings seem flaky or indicate a problem, kill all the AC power in the house and repeat the ohmeter readings. I would be surprised if you had a short, but it is possible that a nail ran through the wire bundle, or something else strange happened.
This is another case of a little knowledge and test equipment being a dangerous thing. The more you check, the more confused you get, because you are seeing very marginal effects, and then assuming that you have some sophisticated problem. Don't take it personally, electricity is simple at first glance, but gets more complex the closer you study it. Electricians just wire it up, and are happy if everything lights up, and probably only pull out the voltmeter if there is a problem.
Richard
Ivan Vegvary wrote:
snip
R
rick
Ivan:
Though there may be other reasons for getting the measurements you see, I would propose the following:
You are probably measuring the voltage with a high impedance voltmeter, which doesn't put much load on the circuit under test. With a decently long run of wires running parallel, they act much like a transformer, which means that you will put an actual 117 (or so) volts on the hot wire, and induction will cause the floating wire to have a voltage induced on it. However, the amount of current available on the floating wire is extremely low. So low, in fact that it won't be able to cause a problem.
If you were to connect two light bulbs to the "shuttle wires" you'll find that when you apply 117 to the red wire, the bulb connected between the red and white wires will illuminate, and the voltage on the black wire will be zero. If you apply 117V to the black wire, the bulb connected between the Black and White wires will illuminate and the voltage on the red wire will be zero.
Given a high impedance meter (or neon bulb) you can get odd indications, particularly if the run of wires is long, which increases the efficiency of the "single turn transformer" that is being created.
Now, the above explanation assumes that when you made your measurements, you verified that the "Shuttle Wire" cabling doesn't go anywhere else than between the two switch locations and the light.
From your description, it sounds like things were actually wired correctly (using a multi-color, 4-wire cable) instead of the slipshod stuff I've run across over the years.
What I would expect to see is a 3-wire (Ground, Black, White) cable coming into your "hot" swichbox from the breaker panel, and another cable with 4-wires (Ground, Black, Red, White) going to the lamp fixture box in the ceiling. From the Ceiling box there will be another 4-wire cable (Ground, Black, Red, White) going to the remote switchbox. At the hot switchbox, the Ground and White wires are connected to the Ground and White wires of the 4-Wire Cable and the ground wire should be connected to the box and/or ground terminal of the switch. The Black wire of the 3-wire cable goes to the common point of the 3-way switch, and the black and red wires of the 4-way cable go to the alternating contacts of the
3-way switch. At the ceiling box, the ground, black, and white wires are each connected to the corresponding colored wires of the remote switch cable, with the two white wires (one from each cable) connected to the lamp fixture. The white wire from the remote switch cable should have a wrap of colored or black tape on it to indicate it is the "hot" wire from the remote switch. At the remote switch box, the ground wire should be connected to the box and/or ground terminal of the switch. The black and red wires go to the alternating contacts of the 3-way switch, and the white wire, (which should have a wrap of colored or black tape on it to indicate it is the "hot" wire from this switch) is connections to the 4-wire cables, everything should work properly.
If this doesn't make sense, or you have any confusion at all, you should have a qualified electrician come in and check everything out. It's better to be safe and spend a few extra bucks than be dead or to cause an electrical fire because you wired something wrong. Also, in some areas, it may be illegal for you to do even the smallest electrical addition or change unless you are a licensed electrician. Always be safe and follow all applicable laws and regulations in your area.
Disclaimer: Don't do this at home. Always have a professional perform any electrical or plumbing work. I'm not licensed to perform electrical work in your location, so the above is for educational purposes only and not to suggest you can actually do your own electrical or plumbing work. If you do ignore this warning and do it yourself, don't bother to sue me because I don't have anything to get anyway, unless you would like to take over my bills... 8-)
--Rick
Ivan Vegvary wrote:
L
Leo Lichtman
Jeff Wisnia wrote: Don't sweat it Ivan ^^^^^^^^^^^^ I am sure Jeff and Richard are correct. If you want to verify that the voltage has no power behind it (high output impedance) place a fairly high resistance(thousands of ohms) across your meter leads or your neon tester, and you will see the voltage disappear. In order to be dangerous, a circuit has to be capable of delivering power into a load.
T
Tim Williams
And if it does work, I pull out the 'scope ;)
But then again, I'm testing things a bit more complex than a light switch. :)
Speaking of scope... my Tek 475 sounds like HV arcing, and smells like ozone. I'm guessing the 2nd anode on the CRT is dirty, tried opening the scope but can't find any way to get at the CRT. Display and functions appear unaffected. Ideas?
Tim
-- In the immortal words of Ned Flanders: "No foot longs!" Website @
formatting link
I
Ivan Vegvary
Thanks everybody!!!
I guess it was capacitance coupling. The wires are part of a bundle. This four wire bundle is also twisted along its full length (about 15 feet) as opposed to 2 (+ground) romex which is coiled flat. I don't know if this makes a difference.
Anyway, the wires do not appear shorted when I test them with a volt meter. The lightbulb does not light when placed accross this 30 volts, therefore no amperage as stated in the replies. If I grab this 30 volt wire with a wet fingers and the ground with the other fingers (same hand, of course) I feel nothing. Guess there is no current.
I will sleep tonight thanks to this newsgroup.
Thanks again, Ivan Vegvary
B
Bruce L. Bergman
Before I develop a migraine reading through that again, are the switches a "Pilot light" design to light up when they are off? That would explain some current flow through the neon pilot lights.
The switches stamped "ILLUMINATED" on the back would be a big clue.
-->--
K
Kenneth W. Sterling
Methinks you should develop better testing techniques - Unless, of course, you really don't want to be around much longer, or possibly are looking for a Darwin award..... Ken.
I
Ivan Vegvary
Hi Bruce, Yes, that was pretty bad reading (my post). Should have dropped the subject of switches and merely stated that I have voltage in a wire that is unconnected at either end. The switches are not ILLUMINATING.
Thanks aga>
L
Leo Lichtman
Bruce L. Bergman wrote: (clip) are theswitches a "Pilot light" design to light up when they are off? That would explain some current flow through the neon pilot lights (clip) ^^^^^^^^^^^^^ Those would have to be some very *special* switches, since they were in his pocket while all this was going on. :-)
J
Jeff Wisnia
Even though you're an electrician Bruce, I'll stick my neck out and ask, "Do they even *make* 3-way switches with pilot lamps in them?".
Not impossible, but it's take some fancy wiring to make those neon pilot lamps light up when the switches are "off", wouldn't it?
Jeff
T
Thompson Family
I have several of them the neon bulb is in series with the light bulb in the fixture when the switch is off
J
Jeff Wisnia
Sorry I'm being so obtuse about this, but could you post a diagram showing how this works on a "3-way" switch? I understand how a neon bulb (and it's dropping resistor) are wired inside a single pole illuminated switch and light when the switch is open,, but the best I can sketch out for 3-way switches needs at least two neon bulbs and two resistors inside each switch.
I wonder if the switch makers have figured out a way to do it with just one neon bulb in the switch.
And yes, I have learned something new tonight; Leviton does list an illuminated 3-way switch, so they obviously know how to do it.
formatting link
Jeff
J
Jeff Wisnia
Nah, I'm reminded of a british prof who tought our sophmore course titled "Rotating Machinery", circa '54. (That was just a fancy name for motors, generators and such.)
Lots of 208/3-phase all over the place, slate panels with big unguarded knife switches and exposed tapered pin and sleeve cable connectors.on them. OSHA would have crapped in their collective pants if they'd been around back then.
I'll never forget him telling us early on that we'd never "make it" as engineers until we learned to "take" a shock.
He also wisely tought us the "One arm behind your back" tactic to keep those shocks from running through our chests, which may explain why I'm still around to write this.
Jeff
J
jim rozen
But of course: o--------------------o / | H-----------------o O o-------------Lamp---N | / o--------------------o
They put the pilot light between the two poles of the switch. Interestingly the tiny bit of current that flows when the light is 'on' is due to the exact stray capacitence that started this thread!
Jim
================================================== please reply to: JRR(zero) at yktvmv (dot) vnet (dot) ibm (dot) com ==================================================
J
jim rozen
Well. That ascii art didn't work out at all. But the essence of the explaination is correct:
================================================== please reply to: JRR(zero) at yktvmv (dot) vnet (dot) ibm (dot) com ==================================================
N
Ned Simmons
Put the neon lamp and resistor in series between the NO and NC terminal of each 3-way switch. Won't that work?
How about a 4-way switch?
Ned Simmons
G
Gerald Miller
From the Leviton page, they are obviously using two neon lamps, one connected from each messenger wire to ground. Press the illuminated end of the toggle and the controlled light comes on or is extinguished and the other neon is powered. Gerry :-)} London, Canada
N
Ned Simmons
Looks OK here (but you beat me to it by 3 minutes).
Ned Simmons
T
Ted Edwards
OK here. Maybe you should give up thos stupid M$ fancy fonts.
Ted