I replied before, but the post got eaten apparently. Look at the three phase power as three legs 120 degrees apart, That is what they are. Period. Now,...... The nuetral could be anywhere...
Let us try the geometric example to visualise this. The three legs forn an equilateral triangle. You could get those three legs from three transformers, say arranged in the triangle. That would be Delta power. Draw the triangle. Do it. This has gone on way too long... The neutral could be balanced in the center of the triangle, but it doesn't have to be. If you were in charge of the world, you call one of the legs neutral if you wanted to. But don't do that. If you had three transformers in the delta (triangle) configuration, you could take the center tap of one of thos transfomers as the neutral. Draw it out.... Now, each transformer has 240 volts output. So from any leg to any other leg, is a 240 volt transformer, and sure enough you measure 240 volts from any leg to any other leg. Now put the neutral in center tap of one of those transformers. Sure enough, either of those two legs now measure 120 volt to neutral. They better, they are on either side of the center tap, and the center tap has been to be nuetral. They are 180 degrees out of phase with each other, and provide 120 volts to neutral, and 240 volts across each other. They are also 120 degrees form the center of the triangle, but that is where neutral is connected in this type of system. But the other leg is now a "wild leg" it is 208 volts from nuetral to the "wild leg" Draw it out, it is now simple trig to see this is so, and why. This sytem is called a corner grounded Delta system. It is handy when you have a bunch of 120 volt loads, and some three phase loads. If a motor connects to the three legs, and does not connect any of it's windings to the "neutral" it will never know or care where the neutral is in relationship to the normal or wild leg. So, you get 120 volts, when you need it, and three phase for motors or transformers when you need it. All of the 120 single phase loads are connected to the same phase input. This is also neat that you can get by with only two transformers on the pole. A big one for the phase that provides 120/240 volts, and smaller one for the "wild leg" just for the three phase loads. Did you draw the triangle? erase one of the transformers that feed the 'wild leg" See how it all still works? In rural areas, many times there are only two of the three phases on the poles, to save money, and many miles of wire for the third wire. Most of that equipment will have a 240 volt to 120 transfomer in it, so you never connect the "wild leg to a 120 volt via "neutral". The input of the transformer always sees 240 volts even if it is connected to the wild leg.
The RPC basicaly provides corner grounded delta, or close enough to it. The first two legs are single phase, and come from the single phase power panel. The third phase is generated locally and not as stable as the single phase input.
SO WITH AN RPC, MAKE SURE THAT NO SINGLE PHASE LOADS, TRANSFORMERS ETC, HAVE ANY CONECTION TO THE WILD LEG. GET THE SCHEMATICS AND MAKE SURE! THE GENERATED WILD LEG IS ONLY THERE FOR THE THREE PHASE LOADS. THESE LOAD DO NOT USE THE NEUTRAL, SO DO NOT CARE WHERE THE NEUTRAL IS REFERENCED TO.
Is this assertive anough for you now?
Another system in common use is the WYE system, Draw the triangle again. this time all the transformers feeding have 120 volt outputs, and connect in a center point. The "neutral" in this system is really balanced in the center, and all legs read 120 volts to neutral, However, the leg to leg voltage is 208 volts. Now any leg can provide
120 volts for a load, It is possible to balance the 120 volt loads across all the three phases. You need all three transformers, and all three wires out in the country.
Three phase 480 volts has a WYE connection, and the transfomers are 277 volt output. Any leg is 277 volts to neutral, and 480 volts leg to leg.
Draw it out!!!!!
All these same questions over and over, waste the time of those who are trying to help. Once you draw it out, it is much easier to understand.
There are a lot's of other possible systems, but the principles are the same.
Pete